Goodman Heat Pump
Old 01-06-2011, 06:57 PM   #1
C comfort's Avatar
Trade: hvac
Question
Goodman Heat Pump
I am working on a 3 ton 14 seer goodman heat pump that is six months old. The 410A pressures are 320 on head and 85 on suction, ambient temp is 45 degrees. The cap tubes, on the flowrator, feeding the outdoor coil are icing, and the bottom of the accumalator has a solid ring of ice an inch thick. The suction line back to the compressor is frosting. Would the flowrator have a restriction or is there not enough return air on the indoor coil.
C comfort is offline
Old 01-06-2011, 09:20 PM   #2
Azpipe's Avatar
Trade: ...
Re: Goodman Heat Pump
Interesting question. I would want to make sure the defrost is operating properly. Are you checking pressures in heating or cooling?
Azpipe is offline
Old 01-07-2011, 07:43 AM   #3
C comfort's Avatar
Trade: hvac
checking pressures in ther heating mode
Old 01-07-2011, 07:01 PM   #4
beenthere's Avatar
Trade: HVAC
Rewards Points: 1,078
Sounds low on charge.
beenthere is offline
Old 01-08-2011, 02:15 PM   #5
Azpipe's Avatar
Trade: ...
It does initially sound low on charge. That's usually the first thought. Without looking at a PT chart, I'd say your pressures seem okay.
What is your supply air temp.?
If your getting good discharge air temp after several minutes of running your probably charged okay. depending on how cold it is in your area (where are you) you should see 90's to 100 or so.
I find it harder to check pressures in heat. I would locate the wire on the defrost board that powers the outdoor fan motor and pull it off and run it in cooling. You can control the head pressure by just carefully putting it back on and off if you need to control the head pressure. It is much more accurate to check charge in cooling mode.
Is the defrost working, do you have good airflow.
Azpipe is offline
Old 01-08-2011, 02:23 PM   #6
Azpipe's Avatar
Trade: ...
I just read your question again and it does kind of make me want to look closer at air flow.
Is this a split system or package unit? Has anyone adjusted the charge on this 6 month old unit? If not and it was installed correctly, the charge is probably fine.
Make sure to check supply and return air flow. If someone has most of the supply air ducts closed or blocked that can do it too.
I'm glad I read it again.
Good luck brother, you'll get it just stick with it.
Azpipe is offline
Old 01-08-2011, 05:17 PM   #7
beenthere's Avatar
Trade: HVAC
R410A
320 PSIG equals 100įF sat temp.
85 PSIG equals 23.5 sat temp.
Pressures are not as good as they should be.
Old 01-08-2011, 05:32 PM   #8
beenthere's Avatar
Trade: HVAC
Goodman SSZ140361B specs at outdoor temp of 45. Head 292, vapor 102, indoor temp rise should be 23.7
Old 01-08-2011, 05:41 PM   #9
Carbon Dioxide Producer
DuMass's Avatar
Trade: EC
For some reason, when I hear 410A and 6-month old install, the first thing I think of is partial restriction in the filter/dryer. Not saying thatís the problem in this situation, but it does seem to be more common with R410A system installs these days.
DuMass is offline
Old 01-08-2011, 06:36 PM   #10
C comfort's Avatar
Trade: hvac
I recovered the refrigerant and checked the pistons for blockage. This unit has .65 piston at the condenser, and a .65 at the evaporator. Both were clear. I charged the system with 50 psi of nitrogen and checked for leaks. Vac. system down for an hour and scaled 7lbs. 12oz of R410a. Head pressure was 330, suction pressure was 105 with a 45 degree ambient temp. The unit checked out and ran fine. There was definetly something going on with the charge.