Excuse me that this is a little out of my normal realm of commercial construction. We are stringently required to exhaust our kitchens, gas HWT, and our HVAC systems 10' from an operable door or window in commercial and multi-family units. Does this apply to a SFR? I have become involved as a consultant on various issues of a log home, and the HVAC contractor does not seem to own a code book, or is at least reticent to produce one. I am concerned about the exhaust gas of a furnace and HWT exiting the house directly above a 5-0 x 6-8 door, and the possibility of CO and CO*2 being reintroduced into the living area.
|
|
|
|
|
|
#2 |
|
Pro
Trade: HVAC
Join Date: Mar 2009
Posts: 1,310
|
Re: Exhaust Gas Location?
Code requires it to be atleast 1' above a door or window. Thats all.
|
|
|
|
|
|
#3 |
|
Pro
Trade: Commercial Superintendent
Join Date: Mar 2009
Posts: 1,511
|
Re: Exhaust Gas Location?
Thanks Beenthere,
Certainly much less stringent standards than are applied to commercial work in Seattle |
|
|
|
|
|
#4 |
|
Pro
Trade: HVAC
Join Date: Mar 2009
Posts: 1,310
|
Re: Exhaust Gas Location?
I don't know why they are insisting on what you posted for commercial.
|
|
|
|
|
|
#5 |
|
Pro
Trade: Commercial Superintendent
Join Date: Mar 2009
Posts: 1,511
|
Re: Exhaust Gas Location?
I think you misunderstand. I saw this vent location, and I couldn't get the HVAC guy to show me his book, probably because he doesn't own one. I am very familiar with how commercial codes are interpreted in much of metropolitan Puget Sound, but not this application on a SFR.
Are you saying that the commonly enforced 10' in the Seattle area is out of line in your opinion? Never the less, this location is much better than the vent location of the original HVAC contractor, who dumped all the combustion gasses out inside the mud room |
|
|
|
|
|
#6 |
|
Pro
Trade: HVAC
Join Date: Mar 2009
Posts: 1,310
|
Re: Exhaust Gas Location?
Yep.
IFGC. 503.8 Section 2, A mechanical draft venting system excluding direct vent appliances, shall terminate at least 4' below, 4 ' horizontal from, or 1' above any door, operable window, or gravity air inlet onto the building(This actually applies to both commercial or residential). 503.8 Section 3, gives clearance based on BTU input. For direct vent appliances. 10,000 BTU or less, 6" Over 10,000 BTU but less then 50,000 BTU, 9" Over 50,000BTU input, needs a 12" Both the bottom of the intake and vent shall have at least 12" clearance above grade. Sorry, I didn't type it word for word, Its longer then section 3. |
|
|
|
|
|
#7 |
|
Pro
Trade: Commercial Superintendent
Join Date: Mar 2009
Posts: 1,511
|
Re: Exhaust Gas Location?
Wow, we are always fighting the 10' rule on commercial buildings. Here they commonly apply it to building air exhaust, furnace and HWT combustion gas, and commercial kitchen exhaust.
|
|
|
|
![]() |
| Thread Tools | Search this Thread |
| Display Modes | Rate This Thread |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "LifeBreath" HRV as exhaust fan for bathroom? | jarvis design | HVAC | 2 | 09-22-2009 06:02 AM |
| Exhaust Fan Hood System Help... | Remco Air | HVAC | 1 | 06-27-2009 11:24 AM |
| hottub access panel location in closet | 72chevy4x4 | Plumbing | 4 | 03-09-2009 11:15 PM |
| Need literature on power exhaust | Dr Heat | HVAC | 0 | 01-23-2009 09:47 PM |
| Codes for exhaust fan installations | jarvis design | Kitchens & Baths | 0 | 01-18-2009 11:48 AM |
| Go to Page... |