Go Back   Contractor Talk - Professional Construction and Remodeling Forum > Trade Talk > HVAC
Old 04-26-2009, 10:21 PM   #1
Trade: hvac contractor
compressor failure???
I went to a house saturday night for no cooling. Inside unit was running, outside unit running as well. Coil was not frozen, inside drybulb 78 degrees. Pressures on the Suction side: 100 PSI, pressure would rise to 108 then fall to 100, Liquid line 160 PSI. not a TXV coil. Compressor dosen't sound to good when running. This is a Carrier split system 3.5 Ton. Any suggestions?
hvactech140 is offline   Reply With Quote
Old 04-27-2009, 07:13 AM   #2
NICKTECH
NickTech's Avatar
Trade:
Send a message via AIM to NickTech Send a message via MSN to NickTech
what does it sound like when it shuts off? if it's a recipricating compressor then the low side reed valve may not be closing off allowing hi side to dump into the lowside. when it shuts down you can hear the hi side whoosh and hiss back through the valve.
NickTech is offline   Reply With Quote
Old 04-29-2009, 05:17 PM   #3
Trade: HVACR
need more input
Ambient temp was? What type of refrigerant? Heat pump or A/C ?
Rated amps and running amps ?
beecoolinc is offline   Reply With Quote
Old 05-09-2009, 08:31 AM   #4
Trade: hvac
service
Sounds like the compressor has internal problems and needs to be replaced. If it is a heat pump you might have reversing valve problems.
service is offline   Reply With Quote
Old 05-11-2009, 10:11 PM   #5
Trade: HVACR
More info. is needed to diagnose but from your description you might be right about the compressor beginning to fail, there's usually a reason why compressors fail. Find out why and go from there.
Remco Air is offline   Reply With Quote