Hello,
Today I am working on a Comfortmaker RPJ2 furnace. Initial problem was no heat with the 2 blinking lights indicating the pressure switch was closed. Upon inspection, the draft inducer housing had a crack, its motor bearings were also excessively noisy, and the vacuum hose to the pressure switch had a small crack. Ah.. an easy repair. Replaced all of the above; new draft inducer motor & housing, new pressure switch - following the new pressure switch's instructions to adjust the switch to .90 WC per the original pressure switch spec (original switch was set at the factory). One would think we're done! Heck no... The furnace cycled nicely about 2 or 3 cycles and then locked out with 2 blinking lights - "pressure switch closed" again.. just like before all of the new parts were installed!!! Upon disconnecting and reconnecting the power, the draft inducer starts as soon as power is connected and runs continuously (regardless of if the thermostat is calling for heat). Any ideas on this one?? Best regards, Tom Addition: I forgot to add that the vent is clear to the roof (no leaves, etc), the filters are new and clean, and thermostat seesm to be functioning normally. Last edited by tpope; 02-27-2007 at 12:21 AM. Reason: Forgot important content. |
Trade: hvac
Re: Comfortmaker RPJ2 Trouble
you say the inducer runs even when not calling for heat. disconnect W from the control board, this tells us if its thermostat or low voltage wireing malfunction. if problem still occurs replace control board
Trade: general
Coolmen, Team,
I followed the advice this evening, diconnected the white wire from the control box. With W disconnected, I switched the unit on and the inducer started up immediately. If I follow Coolmen's logic, this should mean that the thermostat was not allowed to call for heat (disconnected W) and the inducer still kicked on - so something is wrong with the control board. Correct? Now, here is a follow-on question. Upon fiddling with it today I had a better flashlight with me - and took a look inside the burners. Looking down the burners it was apparent that the metal blades down which the flame travels are a bit burned up - burning away at the tips with bits of metal bubbled up at the ends. Should I stop here and replace the furnace before I buy a control board? |
Thoroughbred Mopar Man
Trade: Railroad Conductor/ Ex Hvac Service manager
Hi tpope
The unit you are working on should be electronic ignition. This being the case it may have either a Fenwal control or a United Technolgy. If this is the case it sounds like your ignition control is bad, which also controls inducer. The other possible set up for this furnace is a Honeywell smart valve II. If this is the case, grab your bucket of vasoline and get ready. If it uses the smart valve set up the only way to fix it is replacing the gas valve. Whichever set up you have, for some reason the ignition control has failed, this is the reason for the nuessence problem. Good luck Rusty
Character is doing the right thing even when no one is looking. Intelligence is understanding and practicing the meaning of character. |
| Problems with Comfortmaker RPJ2 Furnace | BSC | HVAC | 18 | 12-11-2010 03:12 AM |
| mdshunk, try this: RPJ2 Gas Furnace similar ignitor prob | tpope | HVAC | 12 | 04-09-2007 01:25 AM |
| still trouble with flashing | Traditions | Painting & Finish Work | 20 | 01-31-2007 09:01 AM |
| Another Comfortmaker rpj2 problem | ramn1 | HVAC | 3 | 02-28-2005 06:46 PM |
| Comfortmaker RPJ2 will not ignite - fan induced motor not turning on. | rolandt | HVAC | 3 | 12-31-2004 05:23 PM |