Boiler System No Heat
Old 11-13-2009, 05:01 PM   #1
rav1964's Avatar
Trade: general contractor
have boiler system in an apartment complex, it feeds 8 units. in one unit there is no heat. the plumber has drained the system and replaced the t-stat. when the system gets drained and filled back up there is heat for a while and then no heat. the system was repiped due to a fire, is it possible that the hot supply line that goes to the unit got plumbed back to the hot supply line and not the return. thanks
rav1964 is offline
Old 11-13-2009, 07:17 PM   #2
gene2's Avatar
Trade: HVAC
Re: Boiler System No Heat
Sounds like the air needs to be bled out of each radiator. Sometimes it takes multiple bleedings. This has to be done each time a line is drained. A competent heating contractor will know this.
gene2 is offline
Old 11-13-2009, 08:55 PM   #3
rav1964's Avatar
they have bled out the system and the unit several times. thanks
rav1964 is offline
Old 11-14-2009, 05:53 AM   #4
beenthere's Avatar
Trade: HVAC
Is this apartment, the highest one above the boiler?
Could still be an air problem. If they had to change some piping to this apartment. they may have accidentally piped in an air trap without realizing it.
What pressure is the system running at.
PS: Draining a boiler and filling it up with fresh water, is one of the worse things you can do to a boiler system.
beenthere is offline
Old 11-14-2009, 07:23 AM   #5
rav1964's Avatar
its a lower unit. each unit is piped off the main line hot supply and then returns to the main return. one thought is that the line is going from the main hot and returning to the main hot instead of the return causing the water to stay at the same temp at in the lines. i think the pressure is 40 or 50 psi. the piping is in the cieling and then runs down to the unit
rav1964 is offline
Old 11-14-2009, 07:31 AM   #6
beenthere's Avatar
Trade: HVAC
It the supply and return of this unit were both piped to the supply manifold. You wouldn't get any heat. Anytime. You would get hot water out of the bleeders while bleeding. but thats it.
40 or 50 PSIG? Is the boiler rated for that pressure. Many aren't.
Piping in ceiling and then running down to unit. Is an indication of air troubles. Does this line have a purge set up on it? It should.
Next. What circulator is being used. It may not have the ability to over come the head pressure, of trying to force hot water down, and cold water up. Incorrect sizing of a circulator is a common problem.
Old 11-14-2009, 10:12 AM   #7
rav1964's Avatar
we dont have heat. i think we will open the cieling and check out to make sure the lines are not crossed. also pex was used, would be an issue?the boiler/pump are existing only thing done was the repiping to the units. thanks for the info i will be out there monday and check this out. will post what i find and thanks again for the help!
rav1964 is offline
Old 11-14-2009, 11:22 AM   #8
beenthere's Avatar
Trade: HVAC
Using pex instead of copper. Can increase the head the circ must work against. So if 3/4" copper was replaced with 1/2" pex, it more then doubled the resistance to flow.
Old 11-14-2009, 07:51 PM   #9
rav1964's Avatar
thanks for the info beenthere, i will be over there next week. the pump on the system pumps out of the boiler to the units. i need to add the system is in the center of the building and feeds 32 units. only have a problem with the replumbed side
rav1964 is offline
Old 11-18-2009, 06:54 PM   #10
rav1964's Avatar
we checked the lines today. all is hooked up correctly. the return of the apartment in question is at the end of the return. the main supply and return are one loop and the return is at the end of the loop. would this cause no heat in the unit. also all the pex was sized properly.
thanks
rav1964 is offline
Old 11-18-2009, 07:07 PM   #11
beenthere's Avatar
Trade: HVAC
Dumb question. How did you determine the pex was sized properly.
You need to know the PD it has for its length , at the GPM you need to flow through it.
Most likely. The pex is NOT sized right. And is increasing the systems head pressure loss above what the circ can move the amount of water you need.
You probably need to increase the size of your circ. Might want to use a Taco 0010 3 speed. And adjust its speed to the one that provides good water flow, without noise.
I'm just guessing that a 0010 will work.
Can you post the brand and model number of the circ.
Old 11-19-2009, 10:45 AM   #12
rav1964's Avatar
the pex was sized by the manufacturer
rav1964 is offline
Old 11-19-2009, 11:34 AM   #13
beenthere's Avatar
Trade: HVAC
Ok.
You told them the flow rate required, and the BTu output needed for each rad/baseboard, and the average temp those emitters need. And thats how they determined what size to use, and what head pressure increase it would be on your circ. And then told you that your circ is able to handle the additional head pressure.
Right?
Meaning you have different sizes of pex running to your different baseboards/rads. Because ¾" pex, doesn't flow as much water as ¾" type M copper pipe.
Or did they tell you to use a different sized circ?
Old 11-19-2009, 11:35 AM   #14
beenthere's Avatar
Trade: HVAC
Its always possible, you still have air trapped in the pex.
Does it sag anywhere.
Old 11-19-2009, 06:59 PM   #15
BCConstruction's Avatar
Trade: Construction
Was the system balanced?
BCConstruction is offline
Old 11-19-2009, 10:52 PM   #16
72chevy4x4's Avatar
does the apartment have a radiator or an HVAC closet w/ heater core and air handler? If you have heated water one one side of the radiator how can you not have heat...is something impeding flow?
72chevy4x4 is offline
Old 11-20-2009, 08:12 AM   #17
Trade: Construction
There's a few reasons for this. Air is the main reason, Sludge build up in the rads but normally take over 10-15 years before it's so bad that the rad stops heat in all areas and the next is system balanceing.
If it's air then only a certain % of the bottom of the rad is going to get hot. But if the rad is getting hot from the top to bottom but not all the way across then Balance the system, If that dont solve it then it could be sludge. What colour is the water when you vent the system? Your pump could also be faulty like broken impeller or clogged. What kind of system is it? Open vent or closed loop/sealed system?
Old 11-20-2009, 06:16 PM   #18
DuMass's Avatar
Trade: EC/ACR
This may sound like a dumb question, but… is the circulator pump for that zone installed correctly? I’ve seen them installed backwards before.
I’ve also seen small 3-phase 3-HP taco circ pumps running backwards because the motor wiring was reversed during replacement and nobody bothered to check for proper rotation at start-up.
DuMass is offline
Old 12-06-2009, 06:00 PM   #19
rav1964's Avatar
thanks for all the replies, the loop was terminated and now the apartmant in questions has heat and its been working for the past week.
thanks
again
rav
rav1964 is offline
Hip Truss system KentWhitten Framing 91 01-31-2012 10:32 PM
any triple pane windows advocates here? advanced_energy Windows, Siding and Doors 43 02-22-2009 07:47 PM
heat pump jdager HVAC 2 01-31-2009 04:17 PM
Outdoor Wood Boiler Question RopeaGoat Plumbing 12 11-16-2007 05:43 AM
heat pump help!?!!! maxkd HVAC 1 11-10-2006 08:57 PM