Thread Tools | Search this Thread | Display Modes |
|
|
#1 |
|
Registered User
Trade: Electrical
Join Date: Sep 2007
Posts: 1
|
Ansul Fire, Air Conditioning And The Code
In a commercial restaurant is there a code requirement that specifies the condition (on/off) of the air conditioning equipment in the event fire extinguishing equipment is activated? If so can I get the specific code reference?
I have a customer that has a number of location where the control panel wiring has jumpers across terminals intended for wiring going to a micro switch in the Ansul system. It is my understanding in the event the Ansul system is activated by a fire the micro switch opens and shuts down the roof top AC units to stop pumping oxygen into the building. I need clarification on this and the particular code reference. Thank you. Brittle |
|
|
|
|
|
#2 |
|
Pro
Trade: H.v.a.c.
Join Date: May 2008
Location: Boise, Id
Posts: 1,905
|
Re: Ansul Fire, Air Conditioning And The Code
Basicly, it's a control which shuts down the blower motor in the case of a fire/smoke. I think its required on all AHU's greater than 1200 cfm's, but I am not positive on that. I would call the local mechanical inspector for the reference on the code.
|
|
|
|
|
|
#3 |
|
Fentoozler
Trade: Professional Pie and Pastry Taster
Join Date: May 2007
Location: New Jersey
Posts: 5,585
|
Re: Ansul Fire, Air Conditioning And The Code
NFPA 96: Standard for Ventilation Control and Fire Protection of Commercial Cooking Operations
You'll need to set up a free account, before you: View the 2008 edition of this document. View the 2004 edition of this document.