It's a damn thick book, but this is what i could come up with:
Group M = Merchantile
The following are straight from the book:
Group M. An automatic sprinkler system shall
be provided throughout buildings containing a Group M
occupancy where one of the following conditions exists:
1. Where a Group M fire area exceeds 12,000 square
feet (1115 m2);
2. Where a GroupMfire area is located more than three
stories above grade plane; or
3. Where the combined area of all GroupMfire areas on
all floors, including any mezzanines, exceeds 24,000
square feet (2230 m2).
Group M. A manual fire alarm system shall be
installed in Group M occupancies having an occupant load
of 500 or more persons or more than 100 persons above or
below the lowest level of exit discharge. The initiation of a
signal from a manual fire alarm box shall initiate alarm notification
appliances as required by Section 907.9.
Exceptions:
1. Covered mall buildings complying with Section
402.
2. Manual fire alarm boxes are not required where the
building is equipped throughout with an automatic
sprinkler system and the alarm notification appliances
will automatically activate upon sprinkler
water flow.
Occupant notification. During times that
the building is occupied, the initiation of a signal from a
manual fire alarm box or from a water flow switch shall
not be required to activate the alarm notification appliances
when an alarm signal is activated at a constantly
attended location from which evacuation instructions
shall be initiated over an emergency voice/alarm communication
system installed in accordance with Section
907.2.12.2.
The emergency voice/alarm communication system
shall be allowed to be used for other announcements provided
the manual fire alarm use takes precedence over
any other use.
Hope this helps. Good luck.