DavidC
Anyone Use Ledger Strips?
Back before Xmas I was holding down the couch while the flu ran it's course through me. So I got to watch more TV than normal. Danny Litford (sp?) was showing us all about building decks with various materials.
What I noticed is that all of the decks shown they used no joist hangers at all. Instead a ledger was installed inside the band joist and the joists rested on it and were nailed through the band into the ends. At least one deck used a larger band joist and the joist sat on the ledger top. Others notched the ends of the joists to keep the tops flush. The decking material was the topic so this wasn't discussed at all, I just noticed it. I've worked on enough old porches to know that this was an accepted and often used method (at least around here). Just wondering if this is still an accepted method and is anyone still using it. Good Luck Dave
www.CookContractingLLC.com |
#2 | |
The Deck Guy
Re: Anyone Use Ledger Strips?Quote:
2009....we use metal hardware. ALWAYS.
Trade: Residential Remodeler
That is how I was taught in late 70's. It doesn't fly today though. I like the idea of a larger rim and I suppose after that is bolted on to code and the appropriate hangers are installed you can then apply a ledger under the joists and ofcourse that would pass any code. But why bother?
Ledger strips all the way, all the time. I do use a larger band than I do on the floor joists. If I need 2x8 for the joists, I use 2x10 for the band. Much faster, cheaper, easier, and better than steel in my opinion. I feel that be the time you put a nail in every hole in the joist hanger, you have almost mutilated the band and the joist.
Cal You hired WHO
By the way, this does pass code in my area as long as you have three nails through the ledger strip and within an inch and a half from each corner of the joist. May not in yours though.
Cal You hired WHO
I always hate to disagree with Greg
![]() but, I have done, and I just did. A low deck (7" above grade) that intersects with a higher deck at a 30º angle, I've got 5 joist 12"oc spanning @1' - @4' from beam to ledger. I've used ledgers in other situations and can't see a problem if everything is sized and attached with care. Again, no disrespect.
#7 | |
Trade: Carpentry & Remodeling
Do what you would do, as if i won't Do anything after you Did It! |
It may be more about the band seperating away from the joists than actually supporting the load. I'm sure someone on here will chime in shortly with all kinds of studies from Simpson. I like many others just comply with the inspectors in my area who are Gods that you must worship.
DavidC
But why, why or why? You're suggesting that erroneous material would be allowed on TV?
![]() It has worked well in the past and looks to me like it would save labor. One thought I had was that glue would be a good idea. Bolting might make it more acceptable to the inspectors. I tend to see notching as decreasing the size of your joist though. I'll try to remember to ask at the code enforcement office next time I go in. Thanks for the respected input form both sides of the fence. Good Luck Dave
#10 | |
DavidC
Good Luck Dave
Trade: Deck Builder
I have seen guys still doing that here. 2x12 ledger, 2x8 joist, 2x4 nailed to 2x12 under joist. I don't think they'll pass with notched joist & 2x2 strips deal anymore like they used to tho.
#12 | |
The Deck Guy
Trade: Contractor
R502.6 Bearing. The ends of each joist, beam or girder shall
have not less than 1.5 inches (38 mm) of bearing on wood or metal and not less than 3 inches (76 mm) on masonry or concrete except where supported on a l-inch-by-4-inch (25.4 mm by 102 mm) ribbon strip and nailed to the adjacent stud or by the use of approved joist hangers. A ribbon is a ledger. And most places a ledger has to be nailed with 3 nails under each joist. That is IRC Code. |
Trade: Contractor
R502.6.2 Joist framing. Joists framing into the side of a
wood girder shall be supported by approved framing anchors or on ledger strips not less than nominal 2 inches by 2 inches (51 mm by 51 mm). Again IRC. |
#15 | |
Cal You hired WHO
Sean
Ledger strips on decks = another good place to collect rain & debris = quicker rotting
However, it is better than nothingNeedless to say I use hangers - unfortunately for most HO's around here they hire the guys that just use a couple of nails for the joists (no strips or hangers), bury the 4x4 posts anywhere from 6" to 18" in the ground, slap on some decking & call it a day |
Uber-Member
Trade: Carpenter...Deck Guy
Re: Anyone Use Ledger Strips? |
#18 |
Trade: SE Carpenter
I have had to do it on rare occesions wheere they dont want to look at any ugly metal connectors.
#19 |
The Deck Guy
Take your hangers to a powder coater and the problem is solved. The last job I did, I had 20+ powder coated in for $75 in one day. You can have any color in the rainbow.
#20 |
Trade: siding
now that's a great idea Greg
| SS Ledger Brackets, real or fantasy? | orson | Decks & Fencing | 8 | 09-26-2008 09:03 PM |
| ledger for pergola question | soupdizzle | Decks & Fencing | 20 | 08-30-2008 11:30 PM |
| Furring strips under plank ceiling? | bob_cntrctr | Drywall | 2 | 05-30-2008 05:40 PM |
| Nailing Strips for Crown | Mpeters | Finish Carpentry | 5 | 02-24-2007 08:53 PM |
| Rubber membrane behind ledger on stucco? | Woodcrafter74 | Decks & Fencing | 6 | 01-31-2006 08:27 PM |