Trade: Fabricator
What Type Of Service Is This?
I'm turning my basement in to my work shop, I have a bunch of single phase 120/240 volt equipment and I just picked up a lathe that is 3 phase 220. I figured that I will use a phase converter for all the 3 phase equipment (1 for now and one more piece down the road for a total of 2). My question is I think that I might already have 3 phase in the house.
Now I hope you guys don't think that I am going to play with this setup my self. The truth of the mater is I already had one electrician look at it a couple of years ago and he said he wasn't sure. I will run some wire and install a outlet or two but I plan on having the meter moved outside by a pro so the utility company will stop knocking on my door to read the meter. I am just seeing if I can get a clearer picture of what I have before I call a electrician to move the meter out side. If you open up the cabinet below the meter you see where the wires come into the house (total of 4) then they go up through the meter then through a conduit to the main breaker panel and one small breaker box for the AC. Now I put a volt meter on the wires in the cabinet where the wires come into the hose. The wires go as follows "Red, Black, Black" and a white wire at the bottom of the cabinet which I assume is the ground. When it test across the red and white I get 210 volts, when I test the other two black wires across the white I get 120 volts. When I test across both the blacks I get 240 volts and when I test across either of the blacks to the red I get 240 volts. The words "caution red leg first phase on block" and a 3,2,1, underneath the wires in the cabinet. So what do you guys think, do I have 1 phase or 3 phase coming into the house. |
Re: What Type Of Service Is This?
Yeah, sure sounds like you have a 3-phase service already. What yours would be called in electrician trade slang is "Delta high leg". You're the envy of your neighborhood. The only thing that's wrong is that your high leg is in the first position, but that's really no big deal to a competant electrician.
A word of caution... get a good electrician to work on your place. Delta high leg installations are nothing to take lightly. I'd guess that 7 out of every 10 electricians have no business messing around with these. Last edited by mdshunk; 09-06-2007 at 08:38 PM. |
Union Electrician
Trade: Inside Wireman
Yes you have 3 phase 240volts in your house.
It's called a 'center tapped delta system' which is becoming more uncommon by the minute. The red wire is called the high leg(hence the high reading to ground). You can run any 3 phase 240volt machine on this system, but have to be very careful when adding new 120 volt circuits(as 1 of the legs to ground is nearly twice the 120 desired, 208 would be the mathematical reading on the high leg) Last edited by Sparky Joe; 09-06-2007 at 08:43 PM. |
Electrical Contractor
Trade: Electrical
Have you guys seen the pic he linked over on the DIY site?
http://www.diychatroom.com/showthread.php?t=11320
Wow that looks harcore to me. Your a big player with that in your house and your neighbors they not even in the game.
Trade: Fabricator
Well I am going to have a licensed electrician do most of the electrical work for me. I am going to run a few outlets my self both 120/240. I will probably run the 3 phase outlet me self because I have done 3 phase before at a old job. But installing a new pan, updated breaker box and running the new wires in from the outside I will leave to the pro. I just feel better now that I know what type of service I have for when I start making phone calls.
My big question is since I have a 3 phase and I have a lathe that is 220v 3 phase can I run it on the delta 3 phase? I always though that the 3 phase was 120 degrees apart and had equal voltage on each leg? Wouldn't the 208/120/120 be unbalanced to run directly to the lathe with out balancing the voltage? |
Re: What Type Of Service Is This? |
#8 | |
Re: What Type Of Service Is This?Quote:
The high leg only becomes a concern in three cases: -120 volt loads -120/240 loads, such as ranges and dryers -3 phase, 5-wire machines that steal one leg for 120 volt internal control power. Just get a good electrician, and quit worrying so much. |
#9 | |
#10 | |
Trade: Squirrel Handler
Some people climb mountains. I take out the trash. But we both do it for the same reason. |
#11 | |
Trade: Electrical
Trade: Electric
n0ob 3 phase questions...
is the reason they put delta in houses that you can still use 2 pole, 240v appliances, as well as 3 pole, 240v 3 phase motors? You would only get 120v/208v with wye, right? Also, isn't wye more common in general? Does that mean every appliance for a wye system building has to be spec'd for 208v? Water heaters air handlers everything? Do they have multi tap applainces 208v/240v? Also, is most everything on a wye system going to be 3 pole, including 3 phase resistive heating elements, and 3 phase motors, or do they use many 2 pole circuits on a wye 3 phase system? Other than just relayed lighting? (1 of the 7 out of 10 electricians, d'Oh! )
#13 | |
The only reason a PoCo would provide a delta high leg service is because they can do it with two transformers instead of three, thus saving cost. This is how small 3-phase overhead services are most often done. Undergound, you're getting wye, because one padmount is one padmount. |
Union Electrician
You seem to know a bit about phase angles, so I'll just post the crude picture I made
![]() A to ground 120 C to ground 120 B to ground 208 phase to phase 240 If you subtract 120 at 60 degrees from 240 you get 208(at least I think I said that right) |
Union Electrician
Here's what MD explained, called an Open Delta
works just the same, but at a lower capacity
Service & Repairs
Trade: Electrician
Roxanne....
Turn on the Red Leg! Roxanne.... Turn on the Red Leg! |
Service & Repairs
Trade: Electrician
The answer is yes to using double pole breakers on any 3-phase system.
#18 |
Celtic's #1 Fan
Trade: electrical
what does the panel look like?
#19 |
You might want to re-evaluate that stand when you're talking about items like electric clothes dryers and electric ranges. You stand a pretty good chance of blowing up the control circuit in those if you just pop in a double-pole at random. Items such as these rob one leg to neutral for certain 120 volt loads. If that one leg happens to be the high leg, you're SOL.
#20 |
Trade: Electric
I guess it would be too expensive to get a 3 phase blower motor in every air handler for example, and 3 phase heating element in every water heater.... right. I have seen commercial dishwashers with 3 phase heating elements, but it was on a wye system, so no need to identify the high leg.
So the only determining factor whether a building gets delta or wye is if it's overhead or underground service? |
| Service Magic's new service | Grumpy | Marketing & Sales | 12 | 08-02-2008 04:31 PM |
| Setting up service department | pcisam | General Discussion | 0 | 04-27-2007 09:38 AM |
| Can anyone make any sense out of this? | Teetorbilt | Technology | 24 | 04-16-2007 12:21 PM |
| Service upgrade question | ATS | Electrical | 17 | 09-05-2006 09:48 PM |
| May offer a New Service ?? | tzzzz216 | General Discussion | 15 | 07-16-2006 12:00 PM |