tags, as close as possible to the opening tag. Creation Date: 12/20/2017 -->
Wet Locations And GFCIs Code Help
Old 02-04-2018, 09:24 PM   #1
Hardly Working's Avatar
Rewards Points: 808
So to be specific about my question. My inspector is calling me out on my shower can lights. The trims are plastic but he stating that they need to be GFCI protected. All hes been telling me is its in the code book but were just starting to enforce it. So I look to my fellow CT members to help me out. What code might he sighting?
Hardly Working is offline
Old 02-04-2018, 09:26 PM   #2
edward trowelhands
Golden view's Avatar
Trade: Diplomat
Rewards Points: 3,966
Re: Wet Locations And GFCIs Code Help
The one for bath fans.
Golden view is online now
Old 02-04-2018, 09:28 PM   #3
I own stock in FotoMat!
480sparky's Avatar
Rewards Points: 10,110
When an inspector tells you "It's in the Code", then your response should be "Tell me where."
That said, I'll take 110.3(B) for $600, Alex.
Chuck Norris can cut through a knife with hot butter.
480sparky is online now
The Following User Says Thank You to 480sparky For This Useful Post:
kirkdc (02-05-2018)
Old 02-04-2018, 10:06 PM   #4
Irishslave's Avatar
Rewards Points: 2,990
Just put the whole bathroom on a combination Arc fault/ground fault breaker and be done with it $50
"An argument against democracy, an astute observer once said, is to spend five minutes with the average voter.
Irishslave is online now
The Following User Says Thank You to Irishslave For This Useful Post:
kirkdc (02-05-2018)
Old 02-04-2018, 11:17 PM   #5
tjbnwi's Avatar
Rewards Points: 1,824
Originally Posted by Hardly Working View Post
So to be specific about my question. My inspector is calling me out on my shower can lights. The trims are plastic but he stating that they need to be GFCI protected. All he’s been telling me is it’s in the code book but we’re just starting to enforce it. So I look to my fellow CT members to help me out. What code might he sighting?
If it is in the shower zone defined in the NEC is needs to be wet location rated, outside the zone damp rated. I know of no NEC requirement for it to be GFCI protected. Your area may have amended the code to include it.
tjbnwi is online now
Old 02-04-2018, 11:58 PM   #6
General Contractor
greg24k's Avatar
Rewards Points: 7,090
Show him this
410.10 Luminaires in Specific Locations.
(D) Bathtub and Shower Areas. No parts of cord-connected
luminaires, chain-, cable-, or cord-suspended luminaires, lighting
track, pendants, or ceiling-suspended (paddle) fans shall
be located within a zone measured 900 mm (3 ft) horizontally
and 2.5 m (8 ft) vertically from the top of the bathtub rim or
shower stall threshold. This zone is all encompassing and includes
the space directly over the tub or shower stall. Luminaires
located within the actual outside dimension of the bathtub
or shower to a height of 2.5 m (8ft) vertically from the top
of the bathtub rim or shower threshold shall be marked for
damp locations, or marked for wet locations where subject to
shower spray.
P.S Before you show him this, make sure the light is rated "for wet location"
greg24k is online now
Old 02-05-2018, 12:31 AM   #7
Irishslave's Avatar
Well yeah it is a wet location. I put the wet location switch covers on anytime I open up anything or add anything to a bathroom drives my customers nuts as I can only find them in one color.
Old 02-05-2018, 02:53 PM   #8
480sparky's Avatar
Originally Posted by greg24k View Post
Show him this
shower spray.
None of which applies to a recessed light requiring GFCI.
greg24k (02-05-2018)
Old 02-05-2018, 04:47 PM   #9
XJCraver's Avatar
Trade: Building Official
Rewards Points: 156
Good question.
Per the NEC and the IRC it just needs to be wet-location rated, it does not have to be GFCI protected. 210.8 calls out "receptacles" in a bathroom. A can light is not a receptacle.
I can't paste the picture here because the NFPA protects all its images, but there's a good pic in the 2014 NEC handbook that covers it (exhibit 210.9).
The IRC refers to receptacles as well, not outlets.
Receptacle: A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.
HOWEVER: The UL listing on the wet location fixture will almost always require the fixture to be GFCI protected. So, technically, the answer is: it depends on the listing on the light fixture. See here:
http://www.jlconline.com/how-to/plum...wer-lighting_o
XJCraver is offline
The Following 2 Users Say Thank You to XJCraver For This Useful Post:
Golden view (02-05-2018), TxElectrician (02-05-2018)
Old 02-05-2018, 07:27 PM   #10
General Contractor
greg24k's Avatar
Yes, that doesn't apply in this case... I checked in my house and I have a recess in my shower and I have a blank GFI on the wall for that and the sconces around the tub.
Old 02-05-2018, 08:53 PM   #11
rrk's Avatar
Rewards Points: 1,122
The sconces are wet location rated?
rrk is offline
Old 02-06-2018, 08:12 AM   #12
General Contractor
greg24k's Avatar
[QUOTE=rrk;6764450]The sconces are wet location rated?[/Q]
I don't remember I build my house 15 years ago, and my wife picked out everything. So either they connected to the GFI or safe distance from the tub. I remember vaguely this question came up during rough, but I don't remember exactly what it was. The town is pretty tough and every inspection was done with a "fine brush" so I'm pretty sure it's code compliant.