Trade: Electrician
Ungrounded Recept
I cant find anyting in 2005 that says I must have a grounded receptacle if the circuit has a ground...
My realator friend called me and said they switched all the recepts. to 2 prong even though there is a ground avalable... Her Engineer husband thought you had to, becuase the old ground wires were insufficient..After a chuckle or two I told her Ill check... The home inspector says they must change em to grounded recepts. What do you guys think????? |
Mod / ArchiBuilder
Re: Ungrounded Recept
Why would they make the switch to 2 prong?
Tulsa's Leader in Outdoor Living Construction | Facebook | Tulsa Pergola Builder | Tulsa Outdoor Kitchens |
Trade: Electrician
Thats what I asked...I never had to argue it this way...Its usually about trying to put 3 prongs into a ungrounded circuit...
I guess somewhere along the line when selling a house they were told to switch to 2 prongs. (probably for the obvious) so when they rehabbed this one they changed em ALL to 2 prong......If I was buying the house I would want em to change them back as well..Bottom line is they didnt know what the hell they were doing,,,but since they have been a help to me in the past I told them I would check to see if they have an arguement to leave them as is.... |
406.3 General Installation Requirements. Receptacle
outlets shall be located in branch circuits in accordance with Part III of Article 210. General installation requirements shall be in accordance with 406.3(A) through (F). (A) Grounding Type. Receptacles installed on 15- and 20- ampere branch circuits shall be of the grounding type. Grounding-type receptacles shall be installed only on circuits of the voltage class and current for which they are rated, except as provided in Tables 210.21(B)(2) and (B)(3). |
Union Electrician
Trade: Inside Wireman
A good question is how would they be deemed insufficient?
A low impedance ground path is the goal, but at what point does the impedance of the ground wire gauge become a hazard? |
Trade: Electrician
Thanks again MD....I just skipped right over that part..Duh I was whipping through looking for "un grounded circuits" to pop out at me.........
Electrical Contractor
Trade: Electrical Contractor
Could it be that it is an older house with undersized grounds.
That may be why he thought the grounds were insufficient.
We are the people (our parents warned us about) (Jimmy Buffett) |
I've seen people "rewire" a house, but they continue to use the ungrounded home runs. The appearance of a ground wire at the receptacle doesn't necessarily mean it's hooked to anything at the other end.
#9 | |
Union Electrician
Re: Ungrounded ReceptQuote:
If the ground wire is way undersized and poses too much resistance to trip a 20 amp breaker, it then becomes a bigger hazard than having no ground wire at all by energizing the entire grounding system |
Master Electrician
Trade: Electrical
Couldn't you just ring out each receptacle from ground to neutral. If you get 0 then put a 3 prong. if its over 20ohms or so put the 2 prongs in ???? Just a random thought.
If it's old work with flex conduit, I've been grounding to a bond screw in the steel box if I read continuity to the panel. Is this wrong?
#12 | ||
Baltimore Electrician
Trade: Electrician
120/20 ohms = 6 amps. That's not tripping any breakers.
John from Baltimore "One Day at a Time" All replies based on the 2008 NEC Quote:
Union Electrician
Re: Ungrounded Recept |
Depends on what you're calling "flex conduit". The sheath of the old type AC cable without the thin aluminium sheath bonding strip inside (pre-1957 or thereabouts) is not and never was rated for use as an equipment grounding conductor, regardless of what shows up on your ohm meter.
Service & Repairs
Trade: Electrician
406.3 (D)(3)(b)... tells me, where a grounding means does not exist (the box) to change a non-grounding receptacle to a GFCI type. I had to do this earlier this week.
#16 | |
| three hole receps on a ungrounded system? | Steve Unkie | Electrical | 2 | 12-09-2006 11:44 AM |
| Recept. in FL | Teetorbilt | Electrical | 4 | 02-21-2006 01:26 PM |