tags, as close as possible to the opening tag. Creation Date: 12/20/2017 -->
Understanding The Bond Screw
Old 12-15-2011, 10:21 PM   #1
bluebird5's Avatar
Trade: Licensed G. C. carpenter, flooring, remodeling
Rewards Points: 694
I do not understand when to and when not to use the bond screw in panels. I the panel is a subpanel it goes in on the ground side to bond the panel to ground incase it ever got charged right? If the panel does not have the ground and neutral isolated do you need the bond screw. It just seems to me like you would use it every time to bond the panel to to the neutral or ground.
bluebird5 is offline
Old 12-15-2011, 10:32 PM   #2
Goin' Down in Flames....
Seven-Delta-FortyOne's Avatar
Trade: Builder/GC
Rewards Points: 1,718
Re: Understanding The Bond Screw
On most panels, the grounding bar is already bonded to the case. The grounding screw is there to connect the neutral and ground together, only at a main panel. On sub-panels, the neutral and ground are isolated.
I have an Edifice Complex.
bluebird5 (12-15-2011)
Old 12-15-2011, 10:34 PM   #3
I own stock in FotoMat!
480sparky's Avatar
Rewards Points: 9,910
As a general rule, after the first point of disconnect, you need to separate the neutral & ground conductors. If you don't use the panel as the FPOD, then you do not use the bonding screw.
Chuck Norris can start a fire by rubbing two ice cubes together.
480sparky is online now
The Following User Says Thank You to 480sparky For This Useful Post:
Old 12-15-2011, 10:41 PM   #4
bluebird5's Avatar
Rewards Points: 694
ok so main panel use it. Subpanel don't use it. What is the purpose of bonding the panel to the neutral bar?
Old 12-15-2011, 10:48 PM   #5
480sparky's Avatar
Because, in a main panel, the neutral is the conductor that will carry any fault current the box has back to the source of power, allowing the breaker to open properly.
In a subpanel, the ground wire performs that duty.
The Following 2 Users Say Thank You to 480sparky For This Useful Post:
bluebird5 (12-16-2011), Winchester (12-16-2011)
Old 12-17-2011, 10:52 AM   #6
SemiRetiredEL's Avatar
Trade: Electrial Contractor (master)
Rewards Points: 75
As was already mentioned, with few exceptions, the neutral and the ground buss can only be tied together at the service disconnect.
But, every metal enclosure is required to be grounded/bonded but a ground screw is not the only method (2011 NEC):
250.8 Connection of Grounding and Bonding Equipment.
Changed From 2008
•250.8: Revised to include specific reference to grounding electrode conductors and to delete reference to grounding conductor.
(A) Permitted Methods. Equipment grounding conductors, grounding electrode conductors, and bonding jumpers shall be connected by one of the following means: See related UL
(1) Listed pressure connectors
(2) Terminal bars
(3) Pressure connectors listed as grounding and bonding equipment
(4) Exothermic welding process
(5) Machine screw-type fasteners that engage not less than two threads or are secured with a nut
(6) Thread-forming machine screws that engage not less than two threads in the enclosure
(7) Connections that are part of a listed assembly
(8) Other listed means
SemiRetiredEL is offline
The Following User Says Thank You to SemiRetiredEL For This Useful Post:
bluebird5 (12-17-2011)
Old 01-07-2013, 05:16 PM   #7
Philby's Avatar
Trade: Electrical
1st time on site. Love that quote! Going to use it.
Philby is offline
Surety Bond for Contract on Indian Reservation lamanitta Business 11 07-17-2014 09:03 PM
Blanket building bond in El Paso OlyOlyPB915 Business 1 03-04-2011 02:30 AM
CA to allow Contractor LLC's with New Bond SuretyPro Contractor Licensing 8 12-15-2010 04:14 PM
stocking service trucks MO-AMPS Electrical 23 11-25-2009 10:39 PM
HVAC License vs Bond? Brian82 Contractor Licensing 2 08-20-2009 05:04 PM