Chief Toilet Mover
Trade: Bathroom Remodeling
Triped GFCI Outlet
I was replacing a vanity light in a bathroom a few days ago and when I touched the neutral against the ground the GFCI outlet on the wall tripped, obviosly they are on the same circuit but why did it trip? I reset it and did it a couple of times just to make sure.
Trade: underground
Re: Triped GFCI Outlet
Even with the breaker and switch 'open', or off, the neutral side of the circuit remains intact and connected to all the other neutral branches in the house. I suspect that when you grounded the neutral wire the GFCI must have detected the very, very minute change in potential that took place as current, from other circuits in the house, strayed from the house's neutral path to ground. Just a guess.
A GFCI will detect a neutral to ground short as part of it's normal test. This sometimes shows up when you wire up a new GFCI and stuff it back into the box, and the bare ground may touch the neutral screw on the side. In your case, it was a neutral to ground short at the vanity light.
Chief Toilet Mover
So if I am reading right - it waz suposzd to do dat? That means it is working correctly?
Doesn't sound right to me, Mike, - - as far as I know, - - lighting shouldn't be on the GFCI circuit, period. Of course, md gets the final word on this.
http://www.tr-built.com |
#6 | |
Re: Triped GFCI OutletQuote:
Unless it's been changed since, - - which I doubt, - - try this, - - 1999 N.E.C. [210-11c3], - - Separate 20 amp circuit required for bathrooms (No Lights), - - I do know this is the rule we are required to go by around here.
Electrical Contractor
Trade: Electrical Contractor
The code is 1 20 amp to supply one or all bathroom recepticles, or 1 20 amp to supply everything within 1 bathroom.
We are the people (our parents warned us about) (Jimmy Buffett) |
#9 | |
md, you are really making me feel old. LOL I remember hooking up to the lamp receptacle just like my father did. 2 prongs, no problem, get'er'done. BTW, I'm back to blades and thinking about electrolysis or lasers, I'm over the facial hair thing. Too much wasted time.
Funny, - - to me the definition of 'old' has NEVER changed (yet it never includes 'me'), - - it's alway's been 'my age' + 20 years
Tom, I know what you mean. Brain says 20 but body tells you 50+ later. Takes days too. You think that you are hurting and the next day....it gets worse! I could really do without this 'getting old' stuff.
Ouch!! 'Fifty' is a bad word right now, - - or at least it will be in about a month and a half!!
#14 | |
Chief Toilet Mover
Even better was the fact that the vanity light didn't have a box, it was a wire sticking out of the wall! I added a new work box in order to give the new light something to properly hang from. I have a hard time believing a builder could have gotten that past the inspector, so I suspect somebody added the vanity light later? That is very hard to imagine since the vanity is 8 foot long double sink with full length wall to wall mirror. Hard to imagine the bathroom would have been built in 1994 without a vanity light. Also the switch for this light is on the wall outside the bathroom, no bathroom door, it is master bathroom suite with 48 " wide arched openning. |
#15 | |
210.11 Branch Circuits Required. (C) Dwelling Units. (3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets. Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (2). This text is repeated word for word in the 2003 IRC §E3603.4 In summary: * If this branch circuit serves that bathroom only, it may serve everything in that bathroom. * If this circuit also serves a receptacle in another bathroom, it may serve bathroom receptacles ONLY. * If this circuit serves a bathroom receptacle and also serves lights or receptacles in other rooms other than this bathroom, this is a code violation and has been for a decade or more. |
#16 | |
Since your new fixture needed a box, you did the right thing by installing one. It's usually a flip of the coin when you take a vanity light down whether there will be a box in there or not. |
Thanks md, - - and my apologies for the error, - - I actually 'cited' it word-for-word DIRECTLY out of the 'Code-Check' book, - - my guess is that the '(no lights)' reference being in parenthesis was their way of condensing/abbreviating the variations and/or local options. Thanks for the correction/clarification.
http://www.tr-built.com Last edited by Tom R; 07-22-2005 at 11:12 PM. |
#18 | |
I like to keep in touch with the latest: National Electrical Code (NEC) International Residential Code (IRC) International Building Code (IBC) [commercial work, mostly] International Fuel Gas Code International Mechanical Code International Plumbing Code International Energy Conservation Code International Existing Building Code International Fire Code This seems like a big list, but there's tons of overlap, so it's not too bad. If you're doing mostly resi work, the NEC and the IRC are most of the time all you need to worry about. Last edited by mdshunk; 07-22-2005 at 11:21 PM. |
#19 |
Yeah, I know what you're saying, - - but I like them, they do somewhat cover the basics, - - admittedly, they're the 'code-for-dummies' version.
#20 |
Chief Toilet Mover
Thanks MD, intersting to know. So what appears to me to be an added light and switch because of the way it was set up is most likely in reality the original wiring from the builder. I didn't realize that you could ever install any light without a box. And yes it was a hollywood strip light that I took out. I'm copying your reply into my contractor's bible for reference in the future, thanks.
| GFCI breaker appears to be bad | 72chevy4x4 | Electrical | 14 | 06-03-2008 12:11 PM |
| GFCI question | RobertCDF | Electrical | 15 | 08-17-2007 07:29 PM |
| t-shoot gfci breaker | hurricaneflyer | Electrical | 10 | 11-14-2006 08:56 PM |
| How does a GFCI brk function | mdcorreia | Electrical | 8 | 05-27-2006 09:24 PM |
| Double GFCI Problem Or No? | CGofMP | Electrical | 2 | 01-26-2006 09:43 PM |