THWN Vs THWN-2
What's the difference in insulation besides the columns used for derating?
I've seen THWN-2 written on large wires like 2/0 copper, but is there such an animal for say #12 copper? |
And I do electrical, too!
Re: THWN Vs THWN-2
The difference is obvious in reading T310.13(A).
Site : the area or exact plot of ground on which anything is, has been, or is to be located. Sight : The power or faculty of seeing; perception of objects by use of the eyes; vision. Cite : To mention in support, proof, or confirmation; refer to as an example. |
Service & Repairs
Trade: Electrician
Re: THWN Vs THWN-2
Thank you. I should have known it was just a temperature rating.
THWN is good for a maximum operating temperature of 167ºF and THWN-2 is good for up to 190ºF. Thanks again. |
#4 | |
Baltimore Electrician
Trade: Electrician
Re: THWN Vs THWN-2
Also, the -2 can be derated from the 90° column, where THWN would have to be derated from the 75° column.
John from Baltimore "One Day at a Time" All replies based on the 2008 NEC Quote:
Service & Repairs
Trade: Electrician
Re: THWN Vs THWN-2
But even still, the 'W' is abbreviated for water, so can the THWN-2 rating be derated from the 90º column if used as an underground conductor in a conduit?
#6 | ||
Trade: Electrician
Re: THWN Vs THWN-2Quote:
Check out the 310.13(A) table. THWN is 75°, THWN is 90°. As a comparison, take a look at THHW. The temp listings change with the location. 90° in a dry location, 75° in a wet location. From the looks of 310.13(A), a -2 designation seems to mean that the conductor holds the 90° rating in a wet location, as opposed to dropping from 90° to 75°