Old 03-10-2006, 11:43 PM   #1
Registered User
 
do0f4i's Avatar
 
Trade: electrical
Join Date: May 2005
Location: california
Posts: 14

Round House


im not to sure if that is the correct term but how many round house's(blk,red,blue,white,green thhn) can i put into a 3/4 conduit by code im not to sure of how many current caring conductors can be in the same conduit

do0f4i is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 03-11-2006, 12:59 AM   #2
Pro
 
macmikeman's Avatar
 
Trade: Master Electrican, Electrical Contractor
Join Date: Sep 2005
Posts: 348

Re: Round House


Hey doof, what size wire are you talking about?
macmikeman is offline  
Old 03-11-2006, 07:00 AM   #3
Electrical Contractor
 
jbfan's Avatar
 
Trade: Electrical Contractor
Join Date: Mar 2004
Location: Newnan GA
Posts: 744

Re: Round House


The amount of current carrying conductors can fill the pipe to a cross section of 40%. Of course after derating they may only be good for 10 amps. What size wire are you talking about?

BTW What is a round house???
__________________
We are the people (our parents warned us about) (Jimmy Buffett)

Last edited by jbfan; 03-11-2006 at 07:04 AM.
jbfan is offline  
Old 03-11-2006, 07:48 AM   #4
Electrical Contractor
 
Speedy Petey's Avatar
 
Trade: Electrical
Join Date: Sep 2003
Location: NY State
Posts: 2,179

Re: Round House


Mr. Doof,
Your profile says you are an electrician. Are you seriously asking this question? Especially the way it is worded?
__________________


Last edited by Speedy Petey; 03-11-2006 at 12:38 PM.
Speedy Petey is offline  
Old 03-11-2006, 11:38 AM   #5
Registered User
 
do0f4i's Avatar
 
Trade: electrical
Join Date: May 2005
Location: california
Posts: 14

Re: Round House


im not an electrical contrator im a aprentice my boss quizes me randomly since we are starting my first commercial job i just want to make sure i just want to make sure a can answer his question correctly the wire size is # 12thhn
do0f4i is offline  
Old 03-11-2006, 11:46 AM   #6
DGR,IABD
 
mdshunk's Avatar
 
Trade: Electrical; Commercial and Residential Service
Join Date: Mar 2005
Location: Central PA
Posts: 9,680

Re: Round House


"Round House" is a regional slang term. Some of us may be more famaliar with the more popular term "full boat". Either slang phrase means a full 5 wire pull, consisting of a black, red, blue, white, green.

Exactly house many "round houses" doesn't make any sense in the context of the question. You only need one ground, sized to the largest conductor in the pull. Actually, you don't even need that if you're using a metallic raceway system, but current good trade practices dictate that you pull one.

You may have up to 16 #12 THHN conductors in a 3/4" pipe. Once you have that many, you'll need to derate the ampacity of the conductors.
mdshunk is offline  
Old 03-11-2006, 12:03 PM   #7
Pro
 
macmikeman's Avatar
 
Trade: Master Electrican, Electrical Contractor
Join Date: Sep 2005
Posts: 348

Re: Round House


Ok then Doof the apprentice, it depends on wire size and type of raceway. You said #12, so now look in a current code book at annex C (back end of the book) in the appropriate table for each type of raceway. Annex C is not a mandatory thing, it is an informative table worked out so you don't fill past 40% conduit fill which is mandatory as another poster said. And once you fill this here conduit up, you now will have to consider de-rating issues, which in a nut shell means there will be less amps allowed on your #12 wire depending on how many more than three conductors are in the conduit. I bet your boss doesn't have all the different types of conduit/fill allowances memorized, so now is your chance to turn the tables on him. You memorize maximum fill for #12 for several types, then try quizzing him on liquid tight, flex, schedule 80, and so forth. When you are an apprentice you should try reading the code book for about at least 1/2 hour per day every day. And keep asking questions. You won't be a doof very long this way.
macmikeman is offline  
Old 03-11-2006, 07:47 PM   #8
Registered User
 
do0f4i's Avatar
 
Trade: electrical
Join Date: May 2005
Location: california
Posts: 14

Re: Round House


thanx for all your advice guys i appreciate it

by the way the do0 is my nick name
and a f4i is the type of motorcycle i ride but i can settle for doof lol
do0f4i is offline  
Old 03-11-2006, 07:52 PM   #9
Pro
 
wackman's Avatar
 
Trade: Builder, Additions, large remodels...Lately also small remodels.......
Join Date: Nov 2005
Location: Portland Oregon
Posts: 889

Re: Round House


Quote:
Originally Posted by macmikeman
Ok then Doof the apprentice, it depends on wire size and type of raceway. You said #12, so now look in a current code book at annex C (back end of the book) in the appropriate table for each type of raceway. Annex C is not a mandatory thing, it is an informative table worked out so you don't fill past 40% conduit fill which is mandatory as another poster said. And once you fill this here conduit up, you now will have to consider de-rating issues, which in a nut shell means there will be less amps allowed on your #12 wire depending on how many more than three conductors are in the conduit. I bet your boss doesn't have all the different types of conduit/fill allowances memorized, so now is your chance to turn the tables on him. You memorize maximum fill for #12 for several types, then try quizzing him on liquid tight, flex, schedule 80, and so forth. When you are an apprentice you should try reading the code book for about at least 1/2 hour per day every day. And keep asking questions. You won't be a doof very long this way.
Very good advice.
wackman is offline  
Old 03-11-2006, 10:21 PM   #10
GC/JE
 
steveprichard's Avatar
 
Trade: electrical
Join Date: Jan 2006
Location: Odessa, Tx
Posts: 32

Re: Round House


Also, if you can, take some night classes. They should count as work time for your journeymans' requirements. And read everything you can.

Peace out.
__________________
Steve

"Keep thee thy airspeed, lest the earth rise up and smite thee!"
steveprichard is offline  
Old 03-12-2006, 11:26 AM   #11
listen twice talk once!
 
Bkessler's Avatar
 
Trade: electrician
Join Date: Oct 2005
Location: Orange county California
Posts: 668

Re: Round House


How about nine. current carrying conductors that is. So nine if your using #12 and still going to put them on 20 amp breakers. So that is only two full round houses. unless of course you have balanced loads and do not have to count the nuetral then it's three. ...............go wings!
Bkessler is offline  
Old 03-31-2006, 10:12 PM   #12
New Guy
 
wildwood's Avatar
 
Trade: general contractor
Join Date: Mar 2006
Posts: 15

Re: Round House


Mr. Doof, You would probably be best to pick up a copy of "UGLY'S" (check with your local bookstore or electrical supply house) and you can start to answer the bosses questions on your own. If you are going to be a good electrican than you need to become resourceful. It is much easier to pull out your book and find the answer (1-2 minutes), than to get confused by multiple answers. The last time I checked - the book was about $8 and it is small enough to fit in your back pocket or tool pouch - and it doesn't lie. Also, thhn is not a size of wire it is a type of insulation or jacket. You will also need to know what type of conduit you will be pulling through (rigid, imc, emt, pvc sch40, pvc sch80, sealtight, flex, etc.) because the maximum # of conductors may vary. By the way, aprentice is spelled apprentice and should be preceded with "an" instead of "a". Also, it is carrying not caring. Good Luck Dude - ak

Last edited by wildwood; 03-31-2006 at 10:15 PM.
wildwood is offline  
Old 04-08-2006, 07:43 AM   #13
Registered User
 
wavector's Avatar
 
Join Date: Dec 2004
Posts: 7

Re: Round House


The neutral counts as a current carrying conductor on nonlinear loads.
wavector is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Did you see Flip this house - Cat House? SuperiorBuilt Off Topic (Non Trade) 18 01-24-2011 05:17 PM
Question with quarter round haskl33 Carpentry 14 05-31-2008 07:49 AM
House moving Toolwh@#e Excavation & Site Work 10 10-21-2007 11:23 PM
`Flip This House' star accused of fraud AmeliaP General Discussion 28 06-03-2007 10:21 PM
Funding for first spec house? ruskent Business 28 01-17-2006 08:10 PM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
ContractorTalk.com is for
PROFESSIONAL CONTRACTORS ONLY!

At ContractorTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?