how come residential panels ain't like commercial where the grounds are separeted from neutrals, shouldn't they be separate?
Trade: Electrician
Re: Residential Panels
they are, Main panels Share a common ground/neutral bus. Sub panels separate the neutral and ground.
listen twice talk once!
Trade: electrician
Your not working on your own are you GR? Looking at a couple of your previous posts seems like your a little inexperienced. To be changing out panels on your own.
Trade: Electrical
residential panels generally have two bus bars with a link connecting them and a grounding screw that bonds them to the panel when it is tightened or installed. This is typical of Seimans which is what I generally use, but I'm sure Square D, GE, and CH are similar.
When used as a subpanel, install the bonding screw, but remove the link. Most commercial I've worked on have a Distribution panel which means the downstream panels are all sub-panels with separated neutrals and grounds. |
#5 | |
Electrical Contractor
Trade: Electrical
Re: Residential PanelsQuote:
![]() To answer the "question" though, mot bigger commercial installations typically have an MDP. If you are not sure what this is it is a Main Distribution Panel. This MDP has all the "main" breakers for the branch circuit panels, so most lighting and power panels are sub-panels.
Trade: electrician
Yeah as things slow down a bit I am a little more touchy with all these hacks running around.
Trade: Electrical
everybody was a hack at one time or another.
Trade: electrician
Re: Residential Panels |
Trade: Electrical
You were born knowing this stuff? Impressive.
Trade: electrician
No why do you assume that. But I did learn from a very experience electrician and immediately cared about what I was doing. I learned if I was a hack no one would want to hire me. I learned if I was a hack I would be ridiculed by the guys that worked with me. You see I grew up playing sports and have always wanted to be the best at what I do. I was born knowing how to sht my pants and cry. I learned to become a good electrician.
#11 | |
Trade: Electrical
I agree. Speak for yourself.
Trade: Electrical Contractor
NO! But I did stay at a Holiday Inn last night!
![]() Couldn't resist
We are the people (our parents warned us about) (Jimmy Buffett) |
#13 | ||
Baltimore Electrician
Trade: Electrician
Neutrals and EGCs are separate in all panels, except the main service entrance, and at a SDS, (Separately derived system) In a house, the panel is often the main service disconnect as well, therefore the neutrals and grounds are together. In any downstream panels ("sub panels"), the EGCs and neutrals are separate. In commercial, the panels are generally not the main service, so the EGCs are separate. Also, please keep in mind that the EGC-to-neutral bond at the main disconnect or SDS is the ground fault path to source.
John from Baltimore "One Day at a Time" All replies based on the 2008 NEC Quote:
#14 | |
Trade: Electrical
I have no problem with people asking questions. At least they are sharp enough to ask. |
| Solar panels? | wizendwizard | Electrical | 51 | 02-09-2009 08:51 AM |
| Stamped Sample Panels for trade shows? | KevinA | Concrete & Paving | 2 | 06-08-2008 11:54 AM |
| Refridgerator Panels for Kitchen | trex | Kitchens & Baths | 6 | 04-02-2008 05:06 PM |
| Keeping panels from sticking. | Rich Turley | Masonry | 5 | 10-24-2007 01:16 AM |
| How many Breaker Panels can I have | robertc65 | Electrical | 6 | 02-10-2006 05:13 PM |