General Contractor
'Quick Wiring' Question
I'm refering to quick wiring as the 'bad' method of sticking the wire into the back of the receptacle or switch instead of side wiring it (wrapping it around the terminal). Anyway, it came up in conversation a while ago that when these fail, the wire usually bad/loose is the neutral. Anyone know why?
"History does not long entrust the care of freedom to the weak or the timid”. Dwight D. Eisenhower |
Master Electrician
Trade: Electrical
Re: 'Quick Wiring' Question
Neutrals don't really matter so no one really tightens them much
I think you got bad information. Backstabs certainly fail, but the neutral connection, in particular, certainly does not fail with any greater frequency.
Capra aegagrus
Ditto to MD. They're not like buttered toast.
...but I've seen plenty of 'em just plain toasted. |
#5 | |
Service & Repairs
Trade: Electrician
Re: 'Quick Wiring' QuestionQuote:
Nothing wrong with back-stabbing a receptacle. They are UL approved and if they were wrong or unsafe they wouldn't be. |
Just to add, there is nothing particularly "wrong" in the most liberal sense of the word with backstabbing receptacles. It is quite legal, but there are better ways. A screw termination is better. Pigtailing is better.
Electrical Contractor
Trade: Electrical
Wow. Do you bid jobs with this mentality? You must get a TON of work.
Handle It!
Who is it here who taglines.....Just cause it is to code doesn't make it safe.............
I have seen back stabs fail IMMEDIATELY because of a lack of good connection.
Trade: Electrical
Contractors who allow their employees to stab wires equals a TON of service work for those of us who don't. Keep up the good work!
#10 | |
Capra aegagrus
Those little springs only give you point contact, much less surface area involved than with any other accepted method. That means higher resistance, which means more heat generated when current flows. Over time, all those heating/cooling cycles are just about guaranteed to deteriorate the connection--leading to even higher resistance and more heat, along with the very real probability of arcing and/or intermittent contact (the spring loses its temper as well). I long ago lost count of how many switches and outlets I've troubleshot for that problem. Or for that matter, how many of 'em just blew fire out of the wall and nearly burned the house down. The only reason we're still allowed to do it with 14 gauge is because the lower current levels take longer to do the same damage. I fully expect the practice to be outlawed altogether some time in the next few years. |
#11 | |
Handle It!
Can not get a 12 in them thar holes!!! Kinda reminds me uv my liddlest sister last year. Yee Ha! Get er done!! (Same mentality as back stabbers!)
#12 | |
Service & Repairs
Trade: Electrician
What mentality are you talking about? The OP asked a question and I answered it. |
#13 | |
Service & Repairs
Trade: Electrician
Great post. And I totally agree. That is why I always use the terminals and not the stab-loks. |
Trade: Electrical
So your post above was simply to stir the pot?
Service & Repairs
Trade: Electrician
No, not at all.
Master Electrician
Trade: Electrical
I got in nice phone fight with a big electrical contractor over this topic last year. I got a call for an arc Fault breaker kicking off all the time. Basically, it was the brushes in Ceiling fan. I said well, either replace your fan or swap the arc fault because thats what was kicking it (isolated that). There were also a couple loose neutrals causing some flickering in some lights. Everything was backstabbed and fed through device and the 2 rec. I took out the neutral basically came right out as I pulled them out. .......When the EC found out I swapped the Arc Fault he got hightly irate and said I could not touch his property and he was going to make sure I never worked again in that part of town and yada yada....I said look buddy...I never backstabbed a device and never will even though it's legal. If there is going to be a fire it's going to be because you backstab all your stuff NOT because I took out one arc fault and if your so worried about peoples safety why didnt you put arc faults on all the circuits anyhow? no response I'm sure on a massive scale thats saves you lots of money overall, but seriously, anyone that likes to do quality work generally never backstabs.
2 cents |
Capra aegagrus
If all of his stuff is backstabbed, I'm not so sure that getting rid of an arc fault breaker is ultimately the best move.
#18 |
Master Electrician
Trade: Electrical
oh..btw...when I did that I changed all of the whopping 3 outlets and one switch and rewired ceiling fan in that room. It was a dedication arc fault on that bedroom. sorry forgot to mention that
#19 |
listen twice talk once!
Trade: electrician
I still backstab my outlets in new homes but I always pigtail the hot and neutral so the full current of the circuit does not go through the yolk of the device.
#20 | |
Capra aegagrus
| Tags |
i back stab females ![]() |