Is This OK?
Old 03-22-2009, 07:14 PM   #1
dtsinc's Avatar
Trade: New construction, remodeling
Is This OK?
I am building a house where the HO is an electrician and did his own wiring. It passed inspection, but the inspector didn't look very closely at anything. The HO ran several circuits with 12/3, junctioned it in a outlet box to feed another circuit, two circuits with one pull I guess to save running another wire. What do you guys think?
dtsinc is offline
Old 03-22-2009, 07:25 PM   #2
Electrical Contractor
jbfan's Avatar
Trade: Electrical Contractor
Re: Is This OK?
Happens all the time, and is code compliant!
We are the people (our parents warned us about) (Jimmy Buffett)
jbfan is offline
Old 03-22-2009, 07:27 PM   #3
And I do electrical, too!
480sparky's Avatar
Re: Is This OK?
It is the inaleinable right of every American to burn down their own house.
Site : the area or exact plot of ground on which anything is, has been, or is to be located.
Sight : The power or faculty of seeing; perception of objects by use of the eyes; vision.
Cite : To mention in support, proof, or confirmation; refer to as an example.
480sparky is offline
Old 03-22-2009, 07:40 PM   #4
johndel1971's Avatar
Trade: carpenter/mechanical contractor
Re: Is This OK?
you are allowed to do it for some things but i personally dont recomend it nor would do it.the cost savings is just not worth it. example: 12-2rx is 35 a roll for 250 ft. 12-3 is 65 for 250 ft. and when u share a neutral u have to use a 2-pole breaker by code which is double the cost of a single pole breaker plus ur putting the load of 2 circuits on 1 neutral wire. bottom line is that its on the ho not u. it still amazes me things that custumers to save a couple bucks. best of luck
johndel1971 is offline
Old 03-22-2009, 07:52 PM   #5
480sparky's Avatar
Re: Is This OK?
Use of 2-pole breakers and sharing neutrals have gone out the window with the AFCI requirements.
As an electrician, it's hard for even me to keep up with the Codes. I shudder to think what the homeowner doesn't know that will hurt him.
And there is absolutely no freaking way an average homeowner is going to wire a home as fast and as good as a pro. Note the word fast. Not cutting-corners fast, but been-there-done-that-a-million-times-before fast.
Old 03-22-2009, 08:26 PM   #6
Re: Is This OK?
ur absolutly rite sparky. in my area if an inspector knows a ho is doing the wiring and doesent know him as an electrician they look for everything very closely.think about it, we sometimes fail inspections and we do it everyday,codes r constantly changing and its tough for us to keep up sometimes u would think inspectors would be more critical of a ho doing work but i guess not in this case.
Old 03-22-2009, 08:35 PM   #7
wireless's Avatar
Trade: Electrician
Re: Is This OK?
The savings is in the labor. A 2 pole breaker may be double the money, but how is that more expensive if you are using it in place of two single pole breakers?
wireless is offline
Old 03-22-2009, 08:43 PM   #8
Multi-tradesman defender
Handymanservice's Avatar
Trade: Handyman
Re: Is This OK?
I would assume he knows what he is doing if he is an electrician.
"You can shear a sheep every year, but you can only skin him once!" Remember that when dealing with your customers and pricing.
http://www.yourhandymansite.com
Handymanservice is offline
Old 03-22-2009, 08:44 PM   #9
Re: Is This OK?
u know after i wrote it i thought the the same thing and new it was a matter of time before one of you called me on it, my bad, but as far as labor savings, the house is all open so it really shouldent be much more time to pull another circuit.plus its worth it anyway.
Old 03-22-2009, 08:55 PM   #10
scourt11's Avatar
Re: Is This OK?
you dont need a 2 pole breaker for 2 branch circuits. only if u split the receptacle by breaking the tab off .
scourt11 is offline
Old 03-22-2009, 09:01 PM   #11
480sparky's Avatar
Re: Is This OK?
Yes you do. 210.4(B).
Now try finding a 2-pole combination-type AFCI breaker as required by 210.12.
And everyone thinks electrical is easy.
Old 03-22-2009, 09:04 PM   #12
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Re: Is This OK?
That's old school wiring. The 2008 NEC changes that rule.
210.4 (B)
Magnettica is offline
Old 03-22-2009, 09:06 PM   #13
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Re: Is This OK?
Ahh, but yes, wouldn't the exception in 210.12 allow for some shenanigans with AFCI devices?
Old 03-22-2009, 09:09 PM   #14
480sparky's Avatar
Re: Is This OK?
210.4 (B)
Besides, split-wired (or half-hot) receptacles are generally on the same circuit, and only need a 1-pole breaker.
Old 03-22-2009, 09:11 PM   #15
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Re: Is This OK?
At the time I'm wiring up a switched receptacle (which is very rare), I'm not even thinking OCPD.
Old 03-22-2009, 10:53 PM   #16
dtsinc's Avatar
Re: Is This OK?
Thanks for all your input. It only has taken him 4 months to get his rough in done. And that is only the main floor, he's still working on the basement and garage. Thank God I have other work to fill in with. Good luck to all.
dtsinc is offline
Old 03-22-2009, 11:02 PM   #17
480sparky's Avatar
Re: Is This OK?
Holy cow! I'd be ashamed if it took me 4 days to do it. So how much does he think he's saving?
And it's not just about money. What about missing the kids' soccer games, dance recitals, school plays, an evening out with his better half..........
Old 04-01-2009, 07:53 PM   #18
ampman
ampman's Avatar
Trade: providing pathways for electrons and protons
Re: Is This OK?
i have a question (i already know the answer) on a multiwire branch circuit 2 hots 1 neut. each hot wire load is 15 amps how much is the neut load.
ampman is offline
Old 04-01-2009, 08:11 PM   #19
480sparky's Avatar
Re: Is This OK?
Single or three phase?
Old 04-01-2009, 09:15 PM   #20
jasonec500's Avatar
Trade: General Contracting
Re: Is This OK?
15 amps? I'm not an electrician, but because the hots are different poles don't they cancel each other out or something like that?
jasonec500 is offline