Millivolt Reading
Old 08-24-2008, 04:22 PM   #1
listen twice talk once!
Bkessler's Avatar
Trade: electrician
Millivolt Reading
How does a breaker leak millivolts in the open position? And how accurate is this when testing breakers in a residential situation? Also is it good practice to test all of the breakers in a homes panel and replace ones with a high milivolt reading?
Bkessler is offline
Old 08-24-2008, 04:24 PM   #2
mdshunk's Avatar
Re: Millivolt Reading
They don't. You're measuring 'phantom voltage' in this case.
Are you talking about a Fall Of Potential (FOP) test, maybe, where you measure millivolts from line to load on a circuit breaker in the closed position? If so, that's not leakage, that's resistance, and the FOP test is a test that has some value.
mdshunk is offline
Old 08-24-2008, 04:42 PM   #3
Bkessler's Avatar
Trade: electrician
So the other day I was testing breakers with them open from ground to the load side of the breaker all showed about 0-8 millivolts and then had one with 30, I took it off the bus bar and it was showing the usual signs of overheating. Pitted and discolored. An old employer called this a voltage leak test. So what exactly am I looking at and is this good practice for every panel I stick my nose in?
Bkessler is offline
Old 08-24-2008, 04:53 PM   #4
mdshunk's Avatar
I maintain that it was only a coincidence that the one with the 30 volt reading was also overheated. There are many other reasons for voltage to ground at the terminal on the load side on an open breaker. "Leakage" is dead last on the list.
If you were using a DMM, your numbers you thought you measured were totally bogus: http://www.nema.org/stds/eng-bulleti...ulletin-88.pdf
If you want a "real" test, you measure millivolts with the breaker "ON" from the lug feeding the panel bus to the branch breaker's load side terminal. This is called a Fall of Potential test. The higher the millivolts, the more resistive connections are (both inside the breaker package and the breaker-to-bus connection).
mdshunk is offline
Old 08-24-2008, 05:01 PM   #5
Bkessler's Avatar
Trade: electrician
That makes sense, do you do this test everytime your working in a panel. And do you recommend replacing breakers from this test alone? And also what is to high of a reading or do you just compare to other readings in the same panel. Thanks bk
Bkessler is offline
Light referral reading on TOH web site kirbymurphy Online Leads Services 2 08-21-2008 07:24 PM
Millivolt stats mdshunk HVAC 7 05-11-2007 08:18 PM
biue print reading RAZOR BLADE Construction 13 01-16-2007 09:15 AM
reading plans Wensdy Drywall 3 08-30-2006 08:40 PM
invaluable reading GMW Business 5 12-23-2005 05:12 PM