Microwave Circut
Old 05-19-2009, 01:36 PM   #1
cabinet runner's Avatar
Trade: cabinet installer
Microwave Circut
Hey sparkys I have a quick question .
I'm doing the cabinet removal and install portion on a condo remodel .
Electrician is going to tie a new undercabinet microwave outlet off the 20 amp circut the fridge is on . He says that is all that will be on that circut and will be fine .
His other option is to tie off the garbage disposal circut but it is only 15 amps . I think this is the better way to go as not using these appliances at the same time seems doable . Not so with the fridge /micro combo .
I'll admit it wold be almost immpossible for him to run a new circut to the breaker panel since the unit has concrete floors and ceilings .
I've expressed my concern about this not being right and the money I will have to charge if I must remove some cabinets because he is wrong and the breaker trips every time they use the micro .
I know enough about electric work to stay away from it and he is the proffesional BUT is he right ?
Thanks
cabinet runner is offline
Old 05-19-2009, 02:36 PM   #2
220/221's Avatar
Trade: electrician Phoenix AZ
Re: Microwave Circut
Code says that the built in micro must have it's own 20A circuit.
The refer is likely on with the counter top receps circuit. Refer + micro = coffee maker = tripped breaker.
If the refer is for some reason on a dedicated 20 amp circuit, you will be OK amps wise but still not to code.
If the refer is for some reason on a dedicated 20 amp circuit, use it for the micro and tap off the kit recep circuit to refeed the refer.
Conduit or cable ?
Just because it's within code doesn't make it safe.
Just because it's against code doesn't make it unsafe.
220/221 is offline
Old 05-19-2009, 03:04 PM   #3
mrmike's Avatar
Trade: Electrical & Carpentry
220 is right on. Also,If you read the installation instructions of that microwave it will state that in big letters that it should be wired to its own dedicated circuit. But I see more of them on with other appliances all the time, just like room A/C's .
If it were me I would insist on a dedicated Circuit on its own than to have it on with either fridge or disposer. Take the time now to get it done right to avoid future problems. There is always a way to get a wire there even if it means conduit on the backside of the wall...............
mrmike is offline
Old 05-19-2009, 03:37 PM   #4
solar guy
naptown CR's Avatar
Trade: solar contracting
Conduit or cable ?
ding ding ding the correct answer is in red
Whoever said run a conduit on the back side of the wall remember this is a condo probably a highrise and the back side of the wall is probably the neighbors kitchen.
naptown CR is offline
Old 05-19-2009, 06:23 PM   #5
Service & Repairs
Magnettica's Avatar
Trade: Electrician
210.23 (A)(2)
(2) Utilization Equipment Fastened in Place. The total
rating of utilization equipment fastened in place, other than
luminaires (lighting fixtures), shall not exceed 50 percent of
the branch-circuit ampere rating where lighting units, cord-
and-plug-connected utilization equipment not fastened in
place, or both, are also supplied.
So what that's saying is that if the microwave is say 1100 watts, that calculates to 9.1 amps at 120 volts. That could definitely be on with the refrigerator circuit.
But is it a good design that'll never get a callback?
Most likely NOT.
Magnettica is offline
Old 05-19-2009, 06:26 PM   #6
crazyboy's Avatar
Trade: Electrical
Originally Posted by Magnettica View Post
210.23 (A)(2)
So its legal as long as it only draws 50 percent of the amp rating of the circuit?
crazyboy is offline
Old 05-19-2009, 06:32 PM   #7
Service & Repairs
Magnettica's Avatar
Trade: Electrician
The microwave is legal, correct.
Old 05-19-2009, 06:34 PM   #8
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Btw, welcome to CT. What part of NJ are u from?
Old 05-19-2009, 06:34 PM   #9
crazyboy's Avatar
Trade: Electrical
I thought that was the case, was just clarifying. Thanks
crazyboy is offline
Old 05-19-2009, 06:35 PM   #10
TxElectrician's Avatar
Trade: Electrical
Mag has the requirements dead on.
New construction I prefer to run a dedicated circuit to microwave and refrigerator, in addition to the required minimum 2 small appliance circuits.
TxElectrician is offline
Old 05-19-2009, 06:43 PM   #11
Thanks guys ... good info there . It is an old hi rise buiding built in the mid 70's . The electrical feeds I saw when some of the drywall was removed were conduit coming out of the concrete ceiling . However the microwave wall is against the adjoining unit and in that space the wires are the old metal clad stuff .
I am going insist that he tells the owner that what he is doing is not up to code . Thanks again for the info . I didn't think what he was doing was correct BUT he is the expert so I didn't want to run my mouth without being sure .
Old 05-19-2009, 06:48 PM   #12
solar guy
naptown CR's Avatar
and don't use romex either
Old 05-19-2009, 08:44 PM   #13
ampman
ampman's Avatar
Trade: providing pathways for electrons and protons
true
an army of sheep lead by a lion will defeat an army of lions lead by a sheep
ampman is offline
Old 05-19-2009, 08:50 PM   #14
ampman
ampman's Avatar
we did a job early 90's where they poured a floor a day three stories and we ran smurf with some kind of connectors for concrete but we taped all boxes and connections because concrete will get where you dont want it any way you could add or subtract circuits at will with this wish i could remeber that system name
ampman is offline
Old 05-20-2009, 07:43 AM   #15
mrmike's Avatar
I said this just to use it as an example, that it can be done somehow & should be done!!
There is some mis-information here in these replies.
You cannot just take the appliance tag ratings & say one circuit will handle it & you should be fine????. Those are just the running currents stated. You Must figure in the Starting currents especially the Fridge !!! There are also defrost heaters in them.
Why take the chance?? What would you do if it were your own kitchen?
mrmike is offline
Old 05-20-2009, 07:54 AM   #16
ampman
ampman's Avatar
You cannot just take the appliance tag ratings & say one cicuit will handle it & you should be fine????. Those are just the running currents stated. You Must figure in the Starting currents especially the Fridge !!! There are also defrost heaters in them.
what?? so what do you do take the fridge nameplate and multiply x 125%
ampman is offline
Old 05-20-2009, 08:15 AM   #17
Jim M's Avatar
Trade: Electrical Contractor
The instructions for the microwave will call for a dedicated circuit as others have pointed out.
To play games trying to get it to work is not worth it, and would still be a code violation. Is this the type of work you want to be known for doing?
Jim M is offline
Old 05-20-2009, 10:54 PM   #18
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Speaking of dedicated circuits... how many of you are running 20 amp homeruns for kitchen hood exhausts?
Some of those require their own dedicated circuit too.
Old 05-21-2009, 07:07 AM   #19
Trade: Electrical
You must be talking about the commercial type hoods that many HOs are putting in. I have done a few of those. When you have done them, which trade does the install?
Old 05-21-2009, 11:43 PM   #20
220/221's Avatar
We are required to.....if it's plugged in I think.
I believe the reasoning is that someone will likely change it to a micro/vent in the future.
220/221 is offline
2008 Code & Microwave SLSTech Electrical 23 03-05-2009 04:18 PM
Ventilation short circut, Fix from above or below? WarnerConstInc. General Discussion 33 03-05-2009 10:29 AM
Microwave antennae exposure? Tonkadad Electrical 11 03-02-2008 11:44 PM
Microwave in your truck? mdshunk Tools & Equipment 10 01-22-2008 10:03 PM