Metal Connectors
Old 12-05-2007, 12:18 AM   #1
When It Rains, It Pours..
highlife77's Avatar
Trade: Remodeling(Everything)
Metal Connectors
Is it safe (code) to use a metal connector in a plastic box?? Is it okay to run MC (greenfield) into a plastic box??Thanks.
"When It Rains, It Pours"....
highlife77 is offline
Old 12-05-2007, 12:47 AM   #2
Mark Twenhafel's Avatar
Trade: resi elec newbie
Re: Metal Connectors
This new guy says probably so:
Art. 314.3 Nonmetallic boxes shall be permitted only with open wiring on insulators, concealed knob-and-tube wiring, cabled wiring methods with entirely nonmetallic sheaths, flexible cords and nonmetallic raceways.
Exception No. 1. Where internal bonding means are provided between all entries, nonmetallic boxes shall be permitted to be used with metal raceways or metal-armored cables.
Exception No. 2. Where integral bonding means with a provision for attaching an equipment bonding jumper inside the box are provided between all threaded entries in nonmetallic boxes listed for the purpose, nonmetallic boxes shall be permitted to be used with metal raceways or metal-armored cables.
Sounds like all you need is a do-hickey fitting that allows you to bond the cable armor of all entries into the box.
Mark Twenhafel is offline
Old 12-05-2007, 05:32 AM   #3
Baltimore Electrician
JohnJ0906's Avatar
Trade: Electrician
Are you using MC cable or Greenfield? Different creatures.
MC cable comes with the conductors, Greenfield is a flexible conduit that is installed, then the conductors are installed.
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline
Old 12-05-2007, 07:16 AM   #4
Electrical Contractor
Speedy Petey's Avatar
Trade: Electrical
More likely probably NOT.
When was the last time you saw a plastic box with: 1) an internal bonding means are provided between all entries
or
2) an integral bonding means with a provision for attaching an equipment bonding jumper inside the box are provided between all threaded entries in nonmetallic boxes listed for the purpose
These are very specialized plastic boxes. Not the ones you see on the shelf at Home Depot.
Speedy Petey is offline
Old 12-06-2007, 12:39 PM   #5
or
Okay, thanks, AGAIN, Speedy Petey. I'm going back to stealth mode, now.
Peace out, bro.
Old 12-06-2007, 03:16 PM   #6
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Are these boxes listed and identified for the use connecting Metal-Clad Cable?
NEC 330.40
Magnettica is offline
Old 12-06-2007, 04:09 PM   #7
Trade: Electrical
330.40 is referring to the fittings. Not the boxes.
Old 12-07-2007, 12:12 AM   #8
mdshunk's Avatar
I think there might be a few instances where you an use a metallic raceway or cable system with nonmetallic boxes by utilizing the exception 1 with ordinary plastic boxes with knockouts.
Exception 1 requires that the conduit or cable entries have internal bonding (inside the box), as opposed to the integral bonding (built into the box) required by exception 2. If you have only one cable entry, then no internal bonding is required (duh, no other cables or conduits to bond over to). If you have more than one cable or conduit entry, there are a variety of fittings available that you might use. A bond bushing comes to mind, for instance.
Matter of fact, Arlington's version of the Smart Box (I think they call it the "In Box") is fire rated, making it an ideal old work solution for old work in a commercial building. This box features standard sized knockouts, as opposed to NM cable clamps, making it suitable for use with MC cable within fire rated assemblies.
mdshunk is offline
Old 12-07-2007, 12:17 AM   #9
Welcome home!
You wuz missed.
neolitic is offline
Old 12-07-2007, 12:53 AM   #10
Service & Repairs
Magnettica's Avatar
Trade: Electrician
330.40 Boxes and Fitttings
Old 12-07-2007, 06:33 AM   #11
Trade: Electrical
OK. READ the text son.
330.40 Boxes and Fitting
Fittings used for connecting Type MC cable to boxes, cabinets, or other equipment shall be listed and identified for such use.
Metal Roofing question? fullhouse Roofing 9 07-01-2011 10:32 AM
metal cold roof question ..... Vermonster Roofing 30 09-06-2007 01:30 AM
Braking metal for a brick exterior? Luke's Dad Windows, Siding and Doors 8 01-07-2007 06:59 AM