Trade: ELECTRICAL
Main Trips
hi everybody im new here . Ive been having a problem with one of my customers plant. its about 60000 square feet theres a main distribution panel 347/600Volts 1200 amps has u can see this is canadian voltage, anyhow a few months ago theve been calling me cause the main would trip during the night and once during the day i get there all that is trip is the main which does not help me to find and correct the problem, so i close all the other swiths after the main to try an isolate the problem put them on 1 at the time and nothing, then one day i did that again 1 switch blew 300amp i followed the pipe broght me to find that the problme was an a/c unit so i close the power feeding the a/c unit told my customer call the ventilaation guy to check out his unit, so now im happy thinking i found the problem NO MORE 3 am wake up calls... Wrong 2 months later 3 am wake up call the main triped again now . the a/c unit was repaired and its not triping any other switchs take in consideration that this is an old plant over 60 years so theres alote of old stuff in there. i just bought a megger thinking i can find the problem wit this ... How does it work ive never used one before and wat am i suppose to be looking for when i use the megger is there a web site (megger for dummies) anyone.....
Trade: Electrical
Re: Main Trips
I am not familiar working with Canadian voltages or codes. Is the MDP equiped with ground fault protection?
Trade: ELECTRICAL
Re: Main Trips
this is an old military base the main is new was redone id say about 10 years ago but most of the stuff most ppl in the trade never seen stuff like they have in these buildings. the main is a MCC from square D
Master Electrician
Trade: Electrical
Re: Main Trips
Overload (set amprobe on peak hold overnight) see if it's overloading. Kicking 1/2 way or all the way?
Short (maybe since they happen at those time heating cooling expansion). Something is touching at those times. Meggar might pick up the culprit when you deengergize and check branch circuits. Bad Main Thats what I can think of for the moment. Or it could be the Boogieman. I'm staying tuned to hear what others think.... |
Re: Main Trips
I think you're a world-class nutcase if you reset any of that without doing a megger check. Megger things out before you reset anything. It may save your life one day.
Service & Repairs
Trade: Electrician
Re: Main Trips
I'm thinking a short in one of the feeders to one of the panels.
I had this happen at a garbage disposal company truck storage/ repair shop once. One of the ungrounded feeders got knicked on the original pull and it took a few years before it finally began to arc during a rainstorm, a portion of the run was on the exterior of the bldg. |
Trade: ELECTRICAL
Re: Main Trips
but its not normal that an a/c makes a 1200 main trip its feeding of a 30 amp. can the main be to sensetive. can something be done,
#8 | |
Re: Main TripsQuote:
Brother, you really need to bone up. You're seriously going to get yourself or someone else hurt bad one day. Last edited by mdshunk; 08-20-2008 at 05:25 PM. |
listen twice talk once!
Trade: electrician
Re: Main Trips
I shorted out a 20 amp receptical circuit that tripped a 2000 amp main in a medical facility once. Before it was occupied.
Service & Repairs
Trade: Electrician
Re: Main Trips
I had the same thing happen once. Accidentally tripped a 20 amp branch circuit and the MLO panel's MB tripped. It had something to do with the short-circuit rating of the circuit breaker which I am still a little confused about.
Service & Repairs
Trade: Electrician
Re: Main Trips
Correction.... not that I am totally confused about the short circuit ratings, just that the branch circuit circuit breaker had the same short circuit rating as the main did. the main had a 10k rating, as did the branch circuit circuit breaker. The main should have been whatever the transformer supplying it required, it did not. It was undersized and that's why the whole panel tripped and not just the branch circuit.
Trade: ELECTRICAL
Re: Main Trips |
Trade: electrician
Re: Main Trips
People here are going to tell you the things you need to here as well as things you want to hear and also the things you don't want to here. Don't be so touchy.
Trade: Electrical
Re: Main Trips
hear here
| Why basement & main on same system? | Cache | HVAC | 5 | 05-15-2008 12:25 PM |
| System Bonding Jumper vs. Main Bonding Jumper | Mark Twenhafel | NEC Discussion | 3 | 02-09-2008 06:15 PM |
| Main v.s. Load 2 Gang Meter | Bubbles | Electrical | 5 | 10-05-2007 08:05 PM |
| Main beam sagging 1/2 inch? | AllGoNoShow | Construction | 10 | 10-12-2006 08:20 PM |
| Main Breaker trips | DUMBfouneded | Electrical | 5 | 09-05-2004 09:51 AM |