Trade: Electrician - Self empl.
How Does A GFCI Brk Function
I have been instaling gfci of all types over the years. I actually don`t have a good explanation or know enough to explain how a 2 pole GFCI circuit breaker protecting a 3 wire cct operates? The neutral in the 3 wire is always carrying some unbalanced current due to each of the 2 ccts is feeding
a different set or group of devices, receptacles etc. Actually I don`t think I ever had to install a double pole gfci brk unless it was strickly for a 240 V hot tub, pool etc.. I would appreciate a response. Thanks Mdcorreia |
Union Electrician
Trade: Inside Wireman
Re: How Does A GFCI Brk Function
I'd imagine it just works like a regular GFI, but instead of the CT being around 1 wire it's around both hot, thus only picking up the inbalance between the two hots, then of course compares it to the neut.
Electrical Contractor
Trade: Electrical
Exactly. It monitors all three and compares the values. This is why we can use them for multi-wire circuits.
Electrician
Trade: Electrician
And, If it is 240v you do not use the nuetral pigtail.
Union Electrician
Do you mean 240 with no neutral being used at the ampliance?
#6 | |
Trade: Electrical
Re: How Does A GFCI Brk FunctionQuote:
Union Electrician
Yeah I saw that too, but figured y'all would get it. the letters aren't even close together, oh well
Thanks to all of you. It does make a lot of sense monitoring the 2 hots and the neutral.
While on the subject I do have another related question. Could someone confirm this for me? It seems that whenever I connect a hot tub (once every 2 years) it has been a 120/240 so I obviously connect the Neutral from the GFCI to the neutral terminal at the disconnect and continue with the neutral from the GFCI to the tub. However if it had been a 240V tub then I could use the spare #6 blue wire in the teck cable for it`s ground instead of running a seperate #6 bare back to the panel? I would not have to connect the neutral pigtail from the GFCI? would that be correct? Thanks all of you and have a great week end. MDC |
#9 | ||
Trade: Electrical
Seriously, I don't know if the CEC allows re-identifying blue to green. We can over a certian size (#4 and larger). Quote:
| GFCI breaker | seattle_sparky | Electrical | 24 | 01-25-2009 11:38 AM |
| GFCI question | RobertCDF | Electrical | 15 | 08-17-2007 07:29 PM |
| t-shoot gfci breaker | hurricaneflyer | Electrical | 10 | 11-14-2006 08:56 PM |
| gfci breaker | Browny | Electrical | 6 | 05-29-2006 07:45 AM |
| Double GFCI Problem Or No? | CGofMP | Electrical | 2 | 01-26-2006 09:43 PM |