Ground Rods At Pnl And Mtr
Old 01-31-2006, 03:14 AM   #1
seattle_sparky's Avatar
Trade: Electrician
I had an inspector tell me I needed a ground rod driven at the meter and at the panel in a house i'm remoding and changing the service. The panel is over 15 feet from the meter, but i didn't think that would matter. I would think running a ground wire from either station and using one ground point would prevent a grounding redundancy and prevent a possible voltage gradient situation in the event of a short or ground fault. I may be just over thinking ( or under thinking) this one. thanks.
seattle_sparky is offline
Old 01-31-2006, 06:38 AM   #2
Electrical Contractor
Speedy Petey's Avatar
Trade: Electrical
Re: Ground Rods At Pnl And Mtr
You're a bit vague. Is the meter on the house? It sounds like no.
Is there an outside disconnect? It sounds like no.
If this is a pedestal meter it is typical to require a ground rod (or two) at the pedestal and another at the house. This is what my POCO requires.
If the meter is on the house a disconnect would typically be required closer to the point of entry.
Speedy Petey is offline
Old 01-31-2006, 11:37 AM   #3
Trade: Electrician
we are dropping into the meter and then yes, into a disconnect and the meter is attached to the side of the house.
Old 01-31-2006, 02:45 PM   #4
ATS's Avatar
Trade: Electrical and mechanical contractor
Strange. The way I would do this would be to bond at the disconnect and install the ground rods there. Our utility prohibits a grounding electrode connection in the meter socket. Then run SER 4 conductor cable from the disconnect to the panel. The ground bars and neutral bars would be isolated in the panel . No ground rods would be installed here. This would be different if the panel housed the main disconnecting means, if it did, I would bond there and terminate the GEC at the panel. So he's telling you that within the same building, 2 sets of rods need to be driven? Never heard of that.
ATS is offline
Old 01-31-2006, 05:18 PM   #5
Trade: Electrical
Exactly what ATS said.
Same structure, outside disconnect, NO rod at the panel, even if it is a 200 amp panel.
Ground rods AND water bond to the main disconnect.
Old 02-01-2006, 08:47 PM   #6
Trade: Electrician
thanks for the info guys. Thats pretty much the way I was thinking. I don't know what the hell the 2 location ground rod thing was about. I called the electrical inspector supervisor and he said the same thing. thanks again.
Old 02-01-2006, 08:53 PM   #7
ATS's Avatar
He said what we said, or what the original inspector said?
ATS is offline
Old 02-01-2006, 09:04 PM   #8
Trade: Electrician
he said what you guys said and what i was thinkin the whole time. Maybe i'll try and apply for that inspectors job! I got a good GFCI ques for you guys i'm typing up.
Old 02-01-2006, 10:33 PM   #9
GC/JE
steveprichard's Avatar
Trade: electrical
Here in Odessa, Tx., we have to ground the main AND water line AND natural gas line.
Steve
"Keep thee thy airspeed, lest the earth rise up and smite thee!"
steveprichard is offline