Ground Fault On A Delta
Old 01-01-2009, 12:20 PM   #41
acrwc10's Avatar
Trade: Electrical contractor/General contractor/ ICC certified electrical inspector
Re: Ground Fault On A Delta
[quote=Eddy Current;566328]Glad to see you have a good sense of humor
No, the neutral is bonded to the tranny case and that's as far as it goes. The tranny is fed using a metal conduit which is bonded back in the electrical room.
Yes, all unenergized metal is bonded to an EGC. The electrical room is small but has two seperate feeds from the vault. One 600v delta and one 120/208 wye. Both of these systems look like they are bonded to the same EGC.
I will be back there next week to intall the GF lights so I will bring my camera, give you a better picture of what I'm dealing with.
quote]
So if I read this correctly, Your 600 volt system HAS the XO on the output connected to an earth ground and the transformer case and all metal piping is grounded to that? Is this the way it is wired ?
Because if it is you don't have a floating delta. You just have a straight delta that isn't using the neutral for utilization equipment.
Is the XO on the 600 volt connected to anything ?
acrwc10 is offline
Old 01-01-2009, 08:25 PM   #42
Eddy Current's Avatar
Trade: Licenced Electrician
No, the 600v system comes from the vault which only Hydro can access. I got three wires in a metal pipe, 600v Delta
Sorry, let me re-phrase. Both systems have all their unenergized metal bonded to the same EGC.
Eddy Current is offline
Old 01-02-2009, 11:40 AM   #43
acrwc10's Avatar
Here is another link , it is not exactly about the issue you have but it really has some good diagrams to help visualize the fault path on an ungrounded system.
http://www.cooperbussmann.com/pdf/b9...b2b664f5ca.pdf
acrwc10 is offline
Old 09-24-2009, 12:23 PM   #44
millert2's Avatar
Trade: electrical
Intermittent ground fault
Just a hunch but I would look at 600 volt lighting.
Is the building or parking lights on a photo cell or timer?
If the ballast in the lights is shorted to ground you wont see it if the lighting contactor is not energized
And it is a code requirement to have ground fault indication on a delta system.
good luck.
Originally Posted by Eddy Current View Post
Three days in a row I've got a late night service call for a retirement high rise. They have a small emergency panel that's loosing a phase. When I get there I find a blown 15amp-600volt fuse on the "A" phase. Put in a new fuse and all is good. Next day, same call, same problem.
I went back during the day and tested the circuit with a megger. Everything Megs clear?
Got the call again Friday morning, threw in a fuse but it blows right away. Take some readings on the main 3phase 600v and this is what I find.
Any phase to any other phase----600volts
phase "A" to ground ----600volts
phase "B" to ground ----600volts
phase "C" to ground ---- 0volts
Also, there are no ground fault indicating lights on this service.
millert2 is offline
Old 09-24-2009, 01:04 PM   #45
Doofenshmirtz Evil Inc.
JumboJack's Avatar
good luck.
Being that this happened in January,it would be a safe bet that he has figured it out..
in texas with framing and cornish people will do it for 3.00 a foot. What do yall think about that? Just laber
JumboJack is offline
Old 09-24-2009, 08:08 PM   #46
Master Electrician
Bubbles's Avatar
Trade: Electrical
Hey. Don't leave us hanging like this. What happened? I have blueballs now.
Bubbles is offline
2/0 solid ground wire Higgs Electrical 8 11-18-2008 01:39 PM
Using RMC as a ground. CNC Electrical 1 10-30-2008 06:27 PM
Delta seat cups AJX4 Plumbing 2 08-28-2008 10:52 PM
Well, THAT'S a different ground wire! rhinoguy Electrical 5 04-01-2007 01:21 AM