#21 | |
Trade: sparky
Re: Ground Fault On A Delta
I'm confusing things?
You're the one that does not understand the voltages you are reading. I do. The fact this floating delta is used in a apartment building would be highly unlikely due to the inherent safety problems associated with a floating delta but you say it is a floating delta. I do not believe you would find a floating delta in use in the US for such a situation. It is out of place. ou never answered my question about bonding and grounding. It should be a rhetorical question because I know how things are supposed to be but the fact there are no GF detectors in place with this system, I wouldn't take anything for granted. on top of that, you asked this question (which I provided answers for): Quote:
Best of luck to ya cuz from what you have posted, you have no business working on this system. The problem you are having is not difficult to diagnose nor fix if you know what you are doing. I gave you the most likely answer and I get BS from you. Good luck and I hope you do not get hurt. |
#22 | |
Trade: Licenced Electrician
Your problem is your trying to show everyone how smart you are instead of trying to help people. Your first three post were useless, just trying to be a smartass. After I post that mabey you should try to help intead of being an ass, you come back with questions and answers that have already been addressed.
I've solved my problem already which you would know if you read all the posts. Actually, all but one of your posts came after I posted that I had found the faults. Just because YOU haven't seen or worked on something, doesn't mean it's not out there. Quote:
This whole deal has reminded me why I should stay away from these sites, too many smart-ass's hiding behind their computers who think they know everything and not enough helpfull people. Last edited by Eddy Current; 12-27-2008 at 09:56 AM. |
#23 | ||||||
Trade: sparky
Re: Ground Fault On A DeltaQuote:
Oh, I see. Correcting you is being a smartass. My mistake for recognizing your mistakes and intitially only seeking clarification. You got offended and and somehow it became my fault you don't know what you are talking about. I see it now. Quote:
Like I said, good luck and I hope you don't get hurt. |
#24 |
Professional Instigator
This is where a joint and a couple shots of Jack Daniels would come in really handy.
#25 |
Trade: Electrical contractor/General contractor/ ICC certified electrical inspector
Eddy I hope this "STUPID" back and forth with Nap does not stop you from posting your questions and findings ( I find this informative ) I would only suggest not to reply to posts that are strictly there to cause conflict.
I am wondering what the inspector said about the Ground detection, or lack there of, has he gotten back to you yet ? |
#26 | ||
Trade: sparky
#27 | |
I stopped reading when it just got argumentative. You can only trouble shot so much without being there is my point, so why get into useless bickering??????????? |
#28 | ||
Trade: sparky
![]() I didn't get into bickering until my last couple of posts and that was only to defend myself from what I saw as unwarranted attacks by the person I was offering information to. Prior to that, they were for clarification of a point. Each of my questions were for a reason and had not been answered previously in the thread (regardless what eddy wants to claim). I continued to provide additional info even after OP's initial attacks. Am I wrong for trying to help some guy that is a jackass? Probably, but I am a sucker for the disabled. Bottom line: eddy does not understand this system and should not have been playing with it evidenced by this: Quote:
You find out what the circuit powers and investigate long before tossing in another fuse. If eddy continues to work like this thread shows, I suspect he won't be an electrician (I use the term very loosely) very long as he will get hurt or killed. |
#29 | |||
#30 | |||
Trade: sparky
You can take this for what its worth;
you may have more problems than you realize. In your first post, you implied the fuse was in the 600 volt side of everything. If you had a ballast popping such a fuse, you really need to look at the OCPD in the circuit for the lighting. Coordination of protection is important. btw; how do you lock off the circuit that shows a GF, since this was indicated to be on the high side, and still have anything out of that panel running. You did say this circuit fed the transformer that runs the 120/208 panel with the outside lights. If you locked out that circuit, nothing in that panel would be working becuase you would be locking out a 3 phase breaker that fed that -panel. I am sure the owner would notice all of that not working. Quote:
btw: a gf on the low side of the transformer is not going to be seen as a gf on the 600 volt side. In fact, since the low side is required to be grounded, a gf on the low side had better trip the OCPD involved. If not, you have problems. If you have a gf fault on the low side and the OCPD in the low side does not trip, you could cause an overload on the high side and trip the feeder OCPD but that would mean you have problems with the OCPD on the low side circuit. so acrwc10, Still see this as stupid? Something is wrong here and eddy isn't getting it. |
#31 |
My License Ain't 4 Sale..
Trade: Electrical Contractor
Is this a common thing in Canada, to feed a building with a floating delta? Seems like it would either be corner grounded or more likely wye connected. To be honest, I have never seen a utility supplied delta that was floating. They have either been corner grounded or center tapped with a high leg. The only floating deltas I have seen were derived for special equipment purposes with GF detectors, or zig-zag grounded.
#32 | |
And to Nap yes I think getting argumentative without seeing it is a waist of time. It has been my experience that if you are rude enough and you are right , your not going to be told you were right for no other reason then, the person won't want you to have the satisfaction of being right.
#33 | |
Trade: sparky
If nothing else, I want him to think. 277. floating deltas are generally not used in my area anymore but there are still some around and yes, they are floating deltas from the POCO. .They are typically used in industrial situations. I have never seen one in a residential/commercial situation such as eddy has described this is. Doesn;t mean they were never installed as such, just that I haven't seen any. |
#34 | |
I'll try to explain again. Off of the main 600v splitter there are two 15amp disco's in question. #1 feeds a 10KVA tranny for a small 120/208v panel. #2 feeds exterior light poles(ballasts are single phase 600volts). The fault on #1 (tranny) I think was there for a long time and no one noticed(no GF lights). The fault on #2 (lights) is new and every time the lights came on, a fuse in the disco (#1) for the tranny blew. The fault on the 600v lights is strait forward but the fault on the tranny is the problem. The fault IS on the secondary side(120v hallway lights) and it blows the fuse on the primary(600v). (Now keep in mind that fuse only blows if you have both faults). Initially I thought the tranny fault (#1) was on the primary so I megged the disco, primary wires, the tranny and the secondary wires feeding the panel-all read infinite. Why does the fuse blow when there are two faults? When I first spoke with the inspector, before he even saw it he said that if you have two seperate ground faults the smallest fuse off of the main 600v service will blow. Even if the fault is on another circuit. Anyone ever heard that before? New to me. Nap pointed out (if you can read between all the stuff were he states I'm a hack ) that a fault on the secondary will not cause a ground fault on the primary which is true but that is what is happening here. When i turn off the 120v single pole 15 amp breaker in the panel the ground fault in the primary clears so that is the breaker that is locked off right now.Nap you have some good points concerning this situation. Your problem is you have to constantly prove to everyone that you know everything. From my experience, people who negatively comment on other people have insecurity issues. If you just concentrated on being helpfull, you'd be a good asset to this site. |
#35 | |
Do you happen to know if it happens instantaneously, or does it take awhile before it happens? If you ever go back, try reading continuity between the 600 V phase and the 120 V phase, with the power off of course ![]() p.s.: The inspector is full of bull if he thinks that any fault will blow the smallest fuse. Silly inspector! Electrical work is for pros. |
#36 | ||
Another odd thing that I noticed is that the tranny in question isn't grounded properly. X0 is bonded to the case of the tranny using 12awg wire and that's as far as it goes. The tranny is fed using metal conduit which bonds the case but there is no ground conductor from the tranny. There never was, all this work looks origional. Also there is a fire panel fed from this tranny/120-208v panel. The building owner told me they have replaced it 3 times over the years. I suspect that the tranny not grounded properly has something to do with the problems with the fire panel and possibly the ground fault. It's an odd one for sure. Quote:
#37 | |
Trade: sparky
.anyway. I'm going to read through this thread again. You most recent explanation does lay things out differently than I had read them. Won't blame you or me for that. It is what it is. If I can help, I will. one question and it is serious and sincere: grrounding systems and bonding systems Obviously the lower voltage wye is supposed to have neut bonded to a g e system, does it?. In your floating system, do you have an EGC and subsequent GE system? and is all unenergized metal bonded to it? Just humor me on this. It's not meant to be arguementative. Just trying to get a clear clear pic. Last edited by nap; 12-28-2008 at 04:54 PM. |
#38 |
Well first , I re-read through the whole thread again, and I apologize to you Nap if I it sounded like I was calling you stupid because I was not, I was saying the insults back and forth were stupid.
Second Eddy did you even read the link I posted ? It may or may not be relevant but there is some good information in it, especially about a restricking fault causing more damage in other parts of the system. http://www.mikeholt.com/safety.php?i...ems%20(2-21-2K A thought that occurred to me is a fault on the load side of something in the system ( like after a light ) this would not trip a fuse but would still cause a fault reading. |
#39 | ||||
The tranny is fed using a metal conduit which is bonded back in the electrical room.Quote:
I will be back there next week to intall the GF lights so I will bring my camera, give you a better picture of what I'm dealing with. Quote:
#40 | |
| 2/0 solid ground wire | Higgs | Electrical | 8 | 11-18-2008 01:39 PM |
| Using RMC as a ground. | CNC | Electrical | 1 | 10-30-2008 06:27 PM |
| Delta seat cups | AJX4 | Plumbing | 2 | 08-28-2008 10:52 PM |
| Well, THAT'S a different ground wire! | rhinoguy | Electrical | 5 | 04-01-2007 01:21 AM |