Gfci Protection
Old 07-18-2009, 12:54 AM   #1
dmanola7's Avatar
Trade: Electrician
Send a message via Yahoo to dmanola7
Gfci Protection
Is there a limit to the number of receptacles connected to the load side of a GFCI or GFCI C.B. ?
The job I am doing is @ a bar and there are (5) 4" square boxes with (2) receptacles per box spread out about 5' apart. There is one circuit feeding these receptacles and they are being utilized for coolers. There is no GFCI protection and the last set of receptacles falls out next to the sink. Would a 20A GFCI C.B. be sufficient protection for these receptacles?
dmanola7 is offline
Old 07-18-2009, 08:50 AM   #2
woodchuck2
woodchuck2's Avatar
Re: Gfci Protection
Your worried about how many rec you can put on one GFCI? I would begin with breaking up circuits for these coolers and putting a GFCI at the start "line" of each circuit. Even if the coolers are not maxing out the circuit i think you will find over time the GFCI will be stressed and fail. I just ran into this in a kitchen at a local bar/restaurant where a GFCI had failed and they were running a cooler and 2 food warmers off of it. I talked the owner into installing 2 more circuits that were GFCI protected to operate each appliance. I am sure someone else will chime in with better advice for you but that is where i would go with your problem. Good luck.
woodchuck2 is offline
Old 07-18-2009, 09:04 AM   #3
And I do electrical, too!
480sparky's Avatar
Re: Gfci Protection
Not in the NEC.
You may have a local amendment that has a limit. And some manufacturers used to have a numerical limit, but I haven't seen any for years.
Site : the area or exact plot of ground on which anything is, has been, or is to be located.
Sight : The power or faculty of seeing; perception of objects by use of the eyes; vision.
Cite : To mention in support, proof, or confirmation; refer to as an example.
480sparky is online now
Old 07-18-2009, 08:51 PM   #4
dmanola7's Avatar
Trade: Electrician
Re: Gfci Protection
I think I am going to run another circuit and break up the load, all the receptacles and conduit are behind the coolers, so once I get the area cleared I will do it to Code Standards. The bar is filled with hot girls so the longer I am there the better lol. Thanks for the advice woodchuck
dmanola7 is offline
Old 07-19-2009, 01:37 AM   #5
huntington beach, ca.
hbelectric's Avatar
Trade: electrical
Re: Gfci Protection
Ok I would use a GCFI per 2 cooler's, depending on loads, if they are between 1-5 amps each. Most likely needs 2 circuits. These are continuous loads also.
hbelectric is offline
Old 07-19-2009, 11:18 PM   #6
In the learning
electrichelper's Avatar
Trade: Student/Electrical
Send a message via AIM to electrichelper Send a message via Yahoo to electrichelper
Re: Gfci Protection
What I recommend is splitting the circuits to whatever, depending on amperage draw on each cooler. Then do voltage drop. There are two ways to run this circuit. You can run just breakers, due to easy access in my opinion since it's a bar, or place a GFCI receptacle at the beginning of each circuit for protection, but not so much convenient for being able to access it. As far as the limit, NEC states no limit but just look at local codes and specs in the direction booklet. Hopes this helps and good luck to you....
electrichelper is offline
Old 07-20-2009, 05:16 PM   #7
ampman
ampman's Avatar
Trade: providing pathways for electrons and protons
Re: Gfci Protection
would the coolers be considered dedicated appliances not requiring gfi
an army of sheep lead by a lion will defeat an army of lions lead by a sheep
ampman is offline
Old 07-21-2009, 06:31 AM   #8
Electric_Light's Avatar
Trade: student again
Re: Gfci Protection
Inductive loads can cause false GFCI trips from kickbacks from compressor cycling. If it goes undetected, things may spoil.
Electric_Light is offline
Old 07-21-2009, 06:37 AM   #9
crazyboy's Avatar
Trade: Electrical
Re: Gfci Protection
If you are concerned about this you could have an alarm of some sort downstream of the GFCI, and have it go off when there is no power.
crazyboy is offline
Old 07-21-2009, 06:49 AM   #10
Re: Gfci Protection
What are you going to do when it goes out Friday evening, then not discovered until Sunday night?
Old 07-21-2009, 09:24 AM   #11
DavidsElectric's Avatar
Re: Gfci Protection
Around here All 110v Cord and plug appliances in a commercial kitchen have to be GFCI protected, Even dedicated ones. So those would need GFCI protection. I know a Bar is not a Kitchen, but they still consider that food service around here. I thought it would be a nightmare, and was worried about the warranty period of my first job. Amazingly, I have hade no issues in about a dozen jobs now. I guess the GFIS have been improved a lot in recent years. The GFCI protection on exterior Pop machines however, have been tripping. I know that wasn't a question, but thought I would give some warning.
And yes it does happen when no one is around and things do go bad. The Code doesn't address these things. There are alarms that can contact you in event of failure, but not heavily used do to cost. I have only installed these in large foods stores
DavidsElectric is offline
Old 07-21-2009, 09:39 AM   #12
480sparky's Avatar
Re: Gfci Protection
Originally Posted by DavidsElectric View Post
...........I thought it would be a nightmare, and was worried about the warranty period of my first job. .............
If whatever is plugged in is tripping the GFI, you don't have a warranty issue.... you have a safety issue. You should not be condemned to solving a problem with someone else's equipment, rather you should be commended for creating a safe environment your installation has provided.
The GFI didn't trip because it's installed incorrectly, it tripped because there's a safety issue and it is doing it's job protecting people.
Old 07-21-2009, 05:48 PM   #13
crazyboy's Avatar
Trade: Electrical
Re: Gfci Protection
What am I going to do? Well nothing. But you could have it trip a dialer when it loses power so it will call you on Friday evening. BTW what bar have you seen that's closed on a Friday evening?
crazyboy is offline
Old 07-23-2009, 07:04 AM   #14
Re: Gfci Protection
Although the specific example maybe for a bar, the described event can happen elsewhere.
Old 07-24-2009, 01:19 PM   #15
Blame-Storm Mediator
CK1's Avatar
Trade: MEP
Re: Gfci Protection
In answer to your initial question, the rule of thumb is 5 devices on the load side of the GFI receptacle....
AND, GFI are not designed to handle appliance or equip. loads. They're for plugs.
GFI's are almost as sensitive on the Nuetral as they are on the ground. It will wear out and fail after a while and the devise is like a diode, it has a finite amount of on/off cycles.
ALWAYS seperate appliances from standard counter-top GFI's.
Ofcourse, that's just my opinion based on 25 years in the business and having done houses in So. Cal as big as 50,000 sq.ft.
CK1 is offline
Old 07-24-2009, 01:52 PM   #16
480sparky's Avatar
Re: Gfci Protection
Originally Posted by CK1 View Post
...........GFI's are almost as sensitive on the Nuetral as they are on the ground..........
Huh?
Old 07-24-2009, 09:27 PM   #17
ampman
ampman's Avatar
Re: Gfci Protection
how many times have you been called out for a bad gfi when it was something that was plug in that had a ground fault people don't understand what we do.
ampman is offline
Old 07-24-2009, 09:41 PM   #18
480sparky's Avatar
Re: Gfci Protection
It's an excellent opportunity to educate them then!
Old 07-25-2009, 08:13 AM   #19
Ponsse's Avatar
Trade: Electrical
Re: Gfci Protection
As the GFCI is only monitoring the amperage between the current carrying conductors and tripping on an imbalance, could you elaborate on this statement. I would be most interested in your reasoning.
Ponsse is offline
Old 07-26-2009, 02:19 AM   #20
EMF, PLC specialist
Softy's Avatar
Trade: Professional Pan Handler
Re: Gfci Protection
Ya know you probably need a dedicated 15 or 20A circuit for that cooler alone GFCI or not. I don't normally use GFCI on major appliances, unless the job call for, because it suck to much juice and if it short out it'll trip the breaker anyway, probably just as fast as it trip GFCI. If you do try GFCI at the breaker it's much easier.
Softy is offline
Kitchen - use 20A GFCI at start w/ 15A outlets??? tmdelisle Electrical 25 07-28-2009 01:38 AM
AFCI Protection porject in class electrichelper NEC Discussion 2 07-14-2009 07:31 AM
GFCI question stp57 Electrical 6 04-18-2009 11:49 PM
GFCI protection for indoor spa/ hot tub Magnettica Electrical 30 04-25-2008 10:05 PM
gfci and bathroom outlets 72chevy4x4 Electrical 9 11-24-2007 09:11 PM