GFCI Master Not Tripping
Old 12-27-2007, 07:30 PM   #1
Mark Twenhafel's Avatar
Trade: resi elec newbie
So we're doing a trim out today and new guy (me) is checking the exterior GFCI receptacles to make sure they trip. I'm using a plug tester with the pushbutton. The problem that we got stuck on was a master GFCI receptacle that didn't trip when tested. Of course, all the slaves on the load side behind it wouldn't trip, either.
So, I pulled it out and disconnected it's line and load cables and then tested each cable separately to check that (1) it was properly wired, and (2) it wasn't double-fed. Checked out fine: 120V on the line side and 0V on the load side. I noticed, however, that it would trip when only the line side was terminated (i.e., no load receptacles connected). Reconnected the load side and, again, no trip when tested.
Maybe it's a bad GFCI master. So I swap in a new-from-box GFCI master. Still won't trip. Maybe it's a bad batch.
What I do next is take a known-good GFCI master from the garage and swap it into the exterior location that's causing the problem. Once it's in, the known-good device stops working and acts like all the rest.
At this point, my lead with 5 years experience is stuck. So, I call the owner, a union-trained electrician with 26 or so years of experience. She says "that's strange," but has no ideas.
Anyone here have any ideas?
Mark Twenhafel is offline
Old 12-27-2007, 07:36 PM   #2
Canuck Sparky's Avatar
Trade: Electrical & General Contracting
Re: GFCI Master Not Tripping
Could it be that your tester is NFG?
Canuck Sparky is offline
Old 12-27-2007, 07:43 PM   #3
Thom
thom's Avatar
Canuk might have it.
A few years back my tester tripped a gfi, the inspectors didn't. His tripped the rest in the house, but one wouldn't trip. I had to replace the receptacle and everything was fine.
thom is offline
Old 12-27-2007, 08:20 PM   #4
Old School Marine
randomkiller's Avatar
Trade: Union Journeyman Electrician
Instead of using the plug type tester just use a wiggy and put one probe in the hot side of the outlet and touch the other probe to ground, it should trip right out.
"If we ever forget that we're One Nation Under God, then we will be a nation gone under." Ronald Reagan
randomkiller is offline
Old 12-27-2007, 10:43 PM   #5
goose134's Avatar
Trade: Union Electrician
Random is right, this is how I found out a commercial kitchen GFI wasn't tripping.
goose134 is offline
Old 12-28-2007, 08:12 AM   #6
Tester bad?: I wondered about that, too. The tester properly tripped other GFCI masters on other circuits before and after it didn't trip the suspect outlet. In fact, the same tester properly tripped the "known-good" master in the garage before I moved that GFCI master to the exterior, where it wouldn't trip. Will try shorting the protected outlet to ground.
My thought: I'm thinking of testing continuity on each side of the GFCI, from the panelboard to the master and then from the master to the first slave.
This was the last house on which a guy they had to let go helped on, and were finding bad make-up in various places.
Old 12-28-2007, 05:15 PM   #7
Service & Repairs
Magnettica's Avatar
Trade: Electrician
The problem is on your load side because when the load is attached, the GFI trips. Isolate the known load side of the circuit and go one-by-one until you find the culprit. My guess would be one of the subs on the job has a faulty power tool.
Magnettica is offline
Old 12-28-2007, 05:46 PM   #8
220/221's Avatar
Trade: electrician Phoenix AZ
I test GFCI with a wiggy to ground also. If the receps on the load side didn't trip I would suspect reverse polarity.....but a neutral to ground short should trip it too so......I'd pull everthing apart and looksee. It's only a few outlets, shouldn't take too long.
Just because it's within code doesn't make it safe.
Just because it's against code doesn't make it unsafe.
220/221 is offline
Old 12-28-2007, 05:49 PM   #9
Baltimore Electrician
JohnJ0906's Avatar
Trade: Electrician
Will the GFCI trip with the test button? If it does, will the downstream receps lose power?
The plug-in tester requires a EGC to operate, as does the wiggy method randomkiller posted. Have you checked that?
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline
Old 12-28-2007, 06:56 PM   #10
Old 12-28-2007, 07:57 PM   #11
220/221's Avatar
If you lost your ground after the GFCI outlet the tester might not work.
I don't really know how the tester is designed. I know how a wiggy works though
220/221 is offline
Old 12-28-2007, 08:09 PM   #12
Service & Repairs
Magnettica's Avatar
Trade: Electrician
I don't know if this is appropriate or not but, normally I use the term line/ load when working GFCI circuits.
Old 12-28-2007, 09:45 PM   #13
JohnJ0906's Avatar
Trade: Electrician
It just shunts from the "hot" to the EGC (through a resistor). No EGC, it will not trip the GFCI.
The test button on the GFCI shunts from load hot to line neutral. EGC not necessary for the test.
Mark, are the load side receptacles working properly, and just not tripping?
Does the test button on the GFCI work?
Is the EGC good?
John from Baltimore
"One Day at a Time"
Old 12-28-2007, 09:46 PM   #14
JohnJ0906's Avatar
Trade: Electrician
These are the proper terms.
John from Baltimore
"One Day at a Time"
Old 12-28-2007, 10:34 PM   #15
Is the EGC good?
Thanks for the info on how the tester works vs. how the GFCI works.
It's the load side that's not working. Disconnect the load, and then the GFCI trips. Take the tester down the circuit to the subs, and the subs test okay, i.e., two yellow lights, but they won't trip when the button is pushed.
We didn't go there today. Maybe Wednesday. Thanks for all the suggestions.
Old 12-29-2007, 02:20 AM   #16
Service & Repairs
Magnettica's Avatar
Trade: Electrician
And that's really the best way to learn. There's so many nicknames for things in our industry that it can create some unnecessary confusion. For instance today, me and another had to replace a T87 thermostat. He kept calling the heat anticipator the "differential device".
Old 01-31-2008, 12:23 AM   #17
It took a while for us to get back there, and I didn't get to go. What I heard, in some detail, is that somehow the circuit feeding the GFCI master in the garage got interconnected with the circuit feeding the GFCI master on the exterior. Co-worker said that it took them a while to figure it out and that even then they didn't entirely understand the cause, but everything worked when they left.
What they learned from testing is that shorting one particular exterior recep tripped the garage master, and after the garage master tripped, everything else worked properly.
From this, I came to the conclusion that something was double-fed, interconnecting the two GFCI circuits. Not sure what they changed, but the guy telling me worked with a bunch of pot-heads for a while, so he got pretty good at troubleshooting. :-)
Mark
Old 02-03-2008, 06:08 AM   #18
JohnJ0906's Avatar
Trade: Electrician
That's how I learned...
Mark
Thanks for letting us know what the problem was... or at least that it is fixed.
John from Baltimore
"One Day at a Time"
gfci and bathroom outlets 72chevy4x4 Electrical 9 11-24-2007 09:11 PM
GFCI breaker vs GFCI Receptacle gravtyklz Electrical 14 10-20-2007 05:33 PM
need help with gfci dave0419 Electrical 4 08-18-2007 09:31 AM
Master Bedroom Placement ridgeline_dev Remodeling 4 05-09-2006 08:44 AM
Double GFCI Problem Or No? CGofMP Electrical 2 01-26-2006 09:43 PM