GFCI Breaker Appears To Be Bad
I"m checking out a GFCI breaker installed for an outside (single) outlet. A plug-in line tester shows correct wiring at the outside duplex outlet, but whenever a load is placed on the circuit, the breaker trips. This is a new circuit and run of wire, leads me to believe the breaker is at fault. Do you get bad breakers from time to time which trip with low current (tested w/ a 60w load) instead of rated (15A in this case)?
Ideas are welcome :-) Its a GE breaker (no Siemens here!) |
Re: GFCI Breaker Appears To Be Bad
Did you terminate the circuit's neutral wire ON THE BREAKER? and connect the breaker pigtail to the neutral bar? Is this circuit 1/2 of a multiwire branch circuit? (black, red, white, ground) You can't protect 1/2 of a MWBC with a single pole GFCI breaker. Just some ideas to start off.
thanks for the ideas. Its a homerun circuit (no sharing of neutral). Hot wire on breaker and pigtail connected to the common neutral/ground bus. I did shorten the pigtail-will that effect the resistance of the internal circuitry?
BUT... is the white wire of that cable connected to the breaker or the neutral bar? This is the important part.
Union Electrician
Trade: Inside Wireman
I think your load is faulty, because your little plug tester is also a load, and if that's not tripping it then it's whatever else you're plugging in.
Naw, those plug in testers will not trip an improperly connected GFCI breaker. That is well established, as the current of the neon lamps in them is below the trip current.
Union Electrician
Well excuse me
What is the resistance on one of them anyway, mine looks like it has little christams tree bulbs in it, but I can't read the resistance even in the 10k setting. Which i guess would make sense seeing as the GFI won't see anything greater than 2.4k ohms |
#8 | |
Re: GFCI Breaker Appears To Be BadQuote:
mdshunk figured it out-the load neutral was connected to the panel's neutral bar where as it should have been connected to the GFCI's load neutral connector. Thanks for point it out. |
Trade: MCSE
FYI neon bulbs have no filament. They rely on the electricity to excite the gas and produce the glow. The resistance would be somwhere between extremely high, and infinite.
woodchuck2
Re: GFCI Breaker Appears To Be Bad |
It happens all the time. I have a journeyman that has done that for all arc-faults and GFCIs in a panel. It took a few houses to settle in for him. In his defense, he's one hell of a pipe bender.
Trade: Electrical
I have learned to doubt existing circuits and installations before suspecting modern GFCI breakers are bad.
JumboJack for president!
Trade: Hilti walking billboard
![]() Trade: student again
GFCI is a very high gain current transformer setup as a differential amplifier.
You know how you only put ONE wire when using a clamp meter, because when you put both wires in you get no reading. In a GFCI, both conductors go through the clamp meter and magnetic field cancels out perfectly, so it actually does not know that current is flowing. It detects a ground fault when there is a leakage, because a very small amount of current that does not return by the neutral is detected as asymmetry. It doesn't even know how much current is flowing through the conductors. It just knows the amount of asymmetry. So... the wiring incorrect and using the ground as the return path or there's an insulation failure in the wiring. If the wiring is verified to be correct, you need to isolate the suspected section of wiring, open both ends and megger each conductor against eachother and ground. |
| GFCI breaker | seattle_sparky | Electrical | 24 | 01-25-2009 11:38 AM |
| GFCI breaker | RobertCDF | Electrical | 19 | 05-09-2007 06:56 PM |
| t-shoot gfci breaker | hurricaneflyer | Electrical | 10 | 11-14-2006 08:56 PM |
| Breaker keeps popping | DErnest | Electrical | 2 | 09-15-2006 06:30 PM |
| gfci breaker | Browny | Electrical | 6 | 05-29-2006 07:45 AM |