Fried


Preparing to chomp down about 5:30 yesterday morning. Coffee brewing, the little lady whipping up some eggs and the toaster goes down .......lights blink .....I unplugged both laptops quick ......I hear a bang from the bedroom as the TV explodes.......smoke rolls out of a multiple .....I race downstairs to open the service panel and become the short man on the green mile ......I race outside .....with a limp I might add .......and pull the meter.....yippie ....problem solved ....but the eggs weren't done so I rocky'd them.

Here's the deal. New aluminum service line to where the weather head should be. both hots tied off on the old 60 amp cable with electrical tape and bent resembling a goose neck. The ground cable completely fried and burnt back about 6 inches. I retied the ground, shut down all 220, but lost a TV, a desktop PC and I think the HVAC handler has had it.

Also. The old line running threw the meter on the ground crumbles in your hand at touch.

Here's the big question. Before I contact the insurance company, should I cut down a conveniently located tree?

Any input would be helpful fellas.

__________________
Bob
Glasshousebltr is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 06-07-2007, 05:48 PM   #2
Baltimore Electrician
 
JohnJ0906's Avatar
 
Trade: Electrician
Join Date: Jan 2007
Location: Baltimore, MD
Posts: 1,249

Re: Fried


Bob, the "new service line" you refer to, is this from the pole to the house?
Is the wire that "Crumbles to the touch", is this the cable jacket or the insulation?
__________________
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Quote:
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline  
Old 06-07-2007, 06:08 PM   #3
Custom Builder
 
Glasshousebltr's Avatar
 
Trade: From dirt to ridge vent
Join Date: Feb 2004
Location: South Central Illinois
Posts: 4,403
Send a message via AIM to Glasshousebltr Send a message via Yahoo to Glasshousebltr

Re: Fried


Pole to house looks good. Service line down from power company connect threw the meter base looks real bad. The ground wire crumbles to the touch. Insulation looks.....pretty crappy... on the two lead lines.
__________________
Bob
Glasshousebltr is offline  
Old 06-08-2007, 09:43 AM   #4
Member
 
jbelectric777's Avatar
 
Trade: NJ Lic Electrical Contractor
Join Date: Jun 2007
Location: NJ~PA
Posts: 67

Re: Fried


was that a lightning hit ? if so dont cut anything just call em and get pictures.......
jbelectric777 is offline  
Old 06-08-2007, 11:13 AM   #5
DGFVT
 
CE1's Avatar
 
Trade: Electrical
Join Date: Dec 2005
Posts: 885

Re: Fried


Quote:
Originally Posted by jbelectric777 View Post
was that a lightning hit ? if so dont cut anything just call em and get pictures.......
And call Mr. Sparky and leave the poor tree alone.

When you get the pictures POST THEM!
CE1 is offline  
Old 06-16-2007, 11:15 PM   #6
Philadelphia electrician
 
RobertWilber's Avatar
 
Trade: Electrical contractor
Join Date: Mar 2006
Location: King of Prussia, PA [Philadelphia]
Posts: 346

Re: Fried


dunno ...
sounds like it could be the classic open neutral ...
60 amp gooseneck service entrance ... 50 years old?
Loose neutral connection finally burned away and left 240 across series loads. Happens alla time.
Dig out my website and go to my FAQ and blog.
__________________
Philadelphia electrician
RobertWilber is offline  
Old 07-10-2007, 10:04 AM   #7
Electrician
 
jrclen's Avatar
 
Trade: Electrical Contractor
Join Date: Jul 2007
Location: Central Wisconsin
Posts: 265

Re: Fried


Quote:
Originally Posted by RobertWilber View Post
dunno ...
sounds like it could be the classic open neutral ...
60 amp gooseneck service entrance ... 50 years old?
Loose neutral connection finally burned away and left 240 across series loads. Happens alla time.
Dig out my website and go to my FAQ and blog.
GEC should have prevented the damage. Is it missing? Cut off with the lawn mower?
jrclen is offline  
Old 07-10-2007, 04:57 PM   #8
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Fried


^^
But only if a grounding electrode system was in place. Not all houses have them. I know that sounds crazy, but it's true.
Magnettica is offline  
Old 07-10-2007, 07:04 PM   #9
Baltimore Electrician
 
JohnJ0906's Avatar
 
Trade: Electrician
Join Date: Jan 2007
Location: Baltimore, MD
Posts: 1,249

Re: Fried


Quote:
Originally Posted by jrclen View Post
GEC should have prevented the damage.
I doubt it. The GE system isn't meant to be a substitute for the neutral.

If a city water system with metallic pipe is there, then the neutral current will use it to return to the transformer via the neighbors service.(Not exactly what it's there for) If it is rods or a CCE (ufer) then the earth resistance would be too great to be an effective path.
__________________
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Quote:
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline  
Old 07-11-2007, 11:01 PM   #10
Philadelphia electrician
 
RobertWilber's Avatar
 
Trade: Electrical contractor
Join Date: Mar 2006
Location: King of Prussia, PA [Philadelphia]
Posts: 346

Re: Fried


Find it even with grounding electrode conductors intact. They don't usually serve as good alternate neutrals, at least not good enough to stabilize a centertap neutral that was lost. Don't know why - relatively high resistance?
__________________
Philadelphia electrician
RobertWilber is offline  
Old 07-12-2007, 05:03 PM   #11
Baltimore Electrician
 
JohnJ0906's Avatar
 
Trade: Electrician
Join Date: Jan 2007
Location: Baltimore, MD
Posts: 1,249

Re: Fried


Earth is not an effective neutral path at the voltages we are talking about.
__________________
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Quote:
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fried wirenut dkillianjr Electrical Picture Post 12 10-16-2007 12:56 AM
the august alabama heat fried my dewalt batteries! shelf guy General Discussion 12 08-17-2007 11:34 AM
Lightning & Power Surges Patty Electrical 13 04-16-2006 01:11 PM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
ContractorTalk.com is for
PROFESSIONAL CONTRACTORS ONLY!

At ContractorTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?