Trade: builder remodelor
Electric Codes For Outbuildings/detached Garages
A question about electric codes for outbuildings/detached garages.Specificly are exposed /romex plastic boxs ok or do i need to run conduit . Also would bx/metal boxes be ok,these building are not sheetrocked so all wiring is exposed to interior of building.
Re: Electric Codes For Outbuildings/detached Garages
That's a pretty straightforward question....
334.15 Exposed Work. In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C). (A) To Follow Surface. The cable shall closely follow the surface of the building finish or of running boards. (B) Protection from Physical Damage. The cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, or other approved means extending at least 150 mm (6 in.) above the floor. Where Type NMC cable is installed in shallow chases in masonry, concrete, or adobe, the cable shall be protected against nails or screws by a steel plate at least 1.59 mm (1⁄16 in.) thick and covered with plaster, adobe, or similar finish. (C) In Unfinished Basements. Where the cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards. To summarize, if the cable will be exposed to physical damage, you need to protect it somehow. This may cause you to choose a conduit wiring system. Additionally, if this is a non residential outbuilding, the following also applies (which does not allow Romex): ARTICLE 334 NONMETALLIC-SHEATHED CABLE: TYPES NM, NMC, AND NMS 334.12 Uses Not Permitted. (A) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be permitted under the following conditions or in the following locations: (1) In Type I or II construction unless permitted to be Types III, IV, or V construction. (2) In non-dwelling construction unless the cables are concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15- minute finish rating as identified in listings of firerated assemblies FPN: Building constructions are defined in NFPA 5000™- 2003, Building Construction and Safety Code™, or the applicable building code. |
Thats why you get 6 different inspectors and 6 different interpretations of the code. I've been in construction for 35 years and have worked with people from all over U.S. and have a Commercial GC. license and an electrical license. What the flip is a running board????? > thanks for posting MD. Even though I think the people who write this *^&** never worked for a living I guess i still will have to learn it. RT
#4 | |
Re: Electric Codes For Outbuildings/detached GaragesQuote:
Rob, seriously, I'm not sure where the confusion comes in. This posted code section is really clear to me. I'm not sure how you can get different interpretations. If there's something else that puzzles you, I'll take a stab at clearing it up. |
#5 | |
| New OSHA standard | OsNap | Health & Safety | 8 | 01-08-2010 09:19 PM |
| plumbing codes question for new construction?? | national | Plumbing | 19 | 07-12-2007 05:54 AM |
| Electric planers | mab123 | Tools & Equipment | 18 | 01-15-2007 04:30 AM |
| Electric range makes you fat? | mdshunk | Electrical | 8 | 09-21-2006 08:38 AM |
| Consolidated Diesel Electric Genset | thecrose12 | Electrical | 0 | 03-08-2004 04:34 PM |