Diswasher Disposal - Electrical - Contractor Talk
Diswasher Disposal
Old 10-21-2017, 11:17 PM   #1
Hotneutral's Avatar
Trade: Electrical
Rewards Points: 12
Diswasher Disposal
I?ve come across some receptacles in new construction that have the diswasher and disposal circuits (both dedicated) on a single receptacle. The breakers have a mutual disconnect but the receptacles are only rated for 120. There is potentially 240 between the hot terminals which leads me to believe this is wrong but it passed the building inspection. Any thoughts?
Hotneutral is offline
Old 10-21-2017, 11:22 PM   #2
I own stock in FotoMat!
480sparky's Avatar
Rewards Points: 10,780
Re: Diswasher Disposal
Assuming you mean a duplex (not a single) receptacle............. it's perfectly legal.
Why is there not a Flat Mars Society?.
480sparky is online now
Old 10-21-2017, 11:23 PM   #3
back doors to hell put in
Irishslave's Avatar
Rewards Points: 2,632
http://www.contractortalk.com/f5/can...eutral-361025/
It's not that much trouble to just separate them....I think the change should be made to the code on MWBC
Television is fake...The internet is real
Irishslave is offline
Old 10-21-2017, 11:37 PM   #4
Hotneutral's Avatar
Trade: Electrical
Rewards Points: 12
So the rating on the receptacle is hot to neutral as opposed to the potential between any two points on the device? Do you have a code or manufacturer spec reference fore that?
Old 10-21-2017, 11:38 PM   #5
Hotneutral's Avatar
Trade: Electrical
Rewards Points: 12
Obviously a duplex otherwise you?d have a phase to phase fault
Old 10-21-2017, 11:55 PM   #6
480sparky's Avatar
Each receptacle will be rated and listed for 120v. You can put one, two or even three on a single yoke. Check section RTDV of the UL White Book.
Duplex receptacles rated 15 and 20 A that are provided with break-off
tabs may have those tabs removed so that the two receptacles may be
wired in a multi-wire branch circuit or multiple branch circuits.
A line-to-line fault will still be cleared by a properly-installed overcurrent device.
Old 10-22-2017, 12:03 AM   #7
Hotneutral's Avatar
Trade: Electrical
Rewards Points: 12
I'm confused. I'm not talking about multiple wires being tied into one receptacle. I'm talking about two dedicated circuits on one receptacle. Code requires those to have a mutual disconnect which in most modern panel leads to opposite phases. Therefore the potential between the hot terminals on the receptacle is 240 or 208 in certain situations. My question is why does that not violate the 120 listing for receptacles?
Old 10-22-2017, 12:05 AM   #8
480sparky's Avatar
You are only applying 120v to a each receptacle.
Old 10-22-2017, 12:52 AM   #9
tjbnwi's Avatar
Rewards Points: 4,146
A duplex by definition is a multiple receptacle.
Maybe this article will help.
http://www.ecmag.com/section/codes-s...nch-circuits-0
tjbnwi is online now
Old 10-22-2017, 01:25 AM   #10
Hotneutral's Avatar
Trade: Electrical
Rewards Points: 12
Very good article however I didn?t see any mention of opposite phase circuits on the same device. I agree a duplex device has two receptacles but with two circuits that have a mutual disconnect you?ve got 240 across the hot terminals. The device is not listed for that potential. What am I missing?
Old 10-22-2017, 08:09 AM   #11
480sparky's Avatar
Originally Posted by Hotneutral View Post
............ The device is not listed for that potential. ...........
Yes, it is. See post 6.
.........What am I missing?
A 240v load.
You're overthinking this. It's not an issue. Never has been.
Old 10-22-2017, 08:35 AM   #12
tjbnwi's Avatar
You're looking at the contact/connection points in the duplex as a pair of contact/connection points, they're not. Each opening/side is an individual contact point. This is no different than 2 single round 120v receptacles in an outlet (box).
Old 10-22-2017, 08:42 AM   #13
480sparky's Avatar
Same logic applies to a pair of one-pole breakers in the panel.