Could Hot Aluminum Fascia Run Power Bill Up?

 
Thread Tools Search this Thread Display Modes
Old 06-24-2009, 06:30 PM   #21
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by 220/221 View Post
Power was going to the light, thru the light and TRYING to get back to "ground" via the metal facia.
No, neutral was hot, receptacle ground was hooked to neutral (no I didnt do it and thats not the problem anyway though it shouldnt be done that way I know), receptacle screwed to fascia. Neutral should not be hot. Apparently neutral was getting power from same side of panel otherwise I'd had 220.

Customer was not interested in having the light fixed, so I did not run a new circuit.

willworkforbeer is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 06-24-2009, 06:35 PM   #22
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by ampman View Post
when you showed up on our job and claimed electronics knowledge all you got was the shovel
Back when I was a jobsite superintendent I gave the electricians the shovel.
willworkforbeer is offline  
Old 06-24-2009, 06:37 PM   #23
Capra aegagrus
 
Tinstaafl's Avatar
 
Trade: Remodeler
Join Date: Jan 2008
Location: Central Pennsylvania
Posts: 9,758

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
No, neutral was hot,
Yes, but was it a "hard" hot? IOW, if you hooked it to a good ground, would it have popped a breaker?

If hot is being applied to one side of a load and the neutral side of that load is hanging in mid-air (or tied to fascia), it will appear to be hot--both to your body and to a meter.
Tinstaafl is offline  
Old 06-24-2009, 06:40 PM   #24
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by Tinstaafl View Post
Yes, but was it a "hard" hot? IOW, if you hooked it to a good ground, would it have popped a breaker?
Yes nothing hooked to it just hot wire and neutral, hot wire switched on and off with lightswitch, neutral stayed hot, no current pass between them switch on or off.
willworkforbeer is offline  
Old 06-24-2009, 06:41 PM   #25
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
Back when I was a jobsite superintendent I gave the electricians the shovel.
You were a jobsite superintendent?

You'll have to excuse me, I didn't know who I was messing with.
Magnettica is offline  
The Following User Says Thank You to Magnettica For This Useful Post:
walkerj (06-24-2009)
Old 06-24-2009, 06:44 PM   #26
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by Magnettica View Post
You were a jobsite superintendent?

You'll have to excuse me, I didn't know who I was messing with.
Yes I was, over 150 unruly brats, clawed my way up the hard way.
willworkforbeer is offline  
Old 06-24-2009, 06:45 PM   #27
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
I guess that apartment I panel installed and wired last winter wired itself, sheesh. Dude your little wiring stuff is simple technically. Try wiring an entire car from scratch or work on a cars computerized fuel system. I knew more about electronics when I was 13 then you do now.
And yet you're still walking the aisles at Home Depot.
Magnettica is offline  
Old 06-24-2009, 06:48 PM   #28
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by Magnettica View Post
And yet you're still walking the aisles at Home Depot.
I hate structure and I hate new construction, I just got sick of it. Money is nice but it aint everything. Never sell my soul for it again.
willworkforbeer is offline  
Old 06-24-2009, 06:49 PM   #29
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by ampman View Post
Roger, Roger.

What's your Vector, Victor?
Magnettica is offline  
Old 06-24-2009, 06:52 PM   #30
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
I hate structure and I hate new construction, I just got sick of it. Money is nice but it aint everything. Never sell my soul for it again.
Before this gets real ugly, and I know better because I've posted here for a few years, do you now understand the condition you found at the fascia and why you got shocked?
Magnettica is offline  
Old 06-24-2009, 06:53 PM   #31
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Nobody wants to or doesnt know the answer to my question fine, I gotta go get some beer.
willworkforbeer is offline  
Old 06-24-2009, 06:56 PM   #32
Capra aegagrus
 
Tinstaafl's Avatar
 
Trade: Remodeler
Join Date: Jan 2008
Location: Central Pennsylvania
Posts: 9,758

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
Yes nothing hooked to it just hot wire and neutral, hot wire switched on and off with lightswitch, neutral stayed hot, no current pass between them switch on or off.
Well, that could still be leakage through a different load somewhere else on the circuit. But if you found receptacles wired backward too, it's anybody's guess.

I'd vote with 220. The current leakage, if any was probably on the order of microamps or at best milliamps. Whatever the resistance from fascia to ground would allow. I'd really doubt it had much effect on the electric bill. Except maybe during rainstorms.
Tinstaafl is offline  
Old 06-24-2009, 06:58 PM   #33
strat hd
 
strathd's Avatar
 
Trade: framing contractor , remodeler , GC occasionally
Join Date: Jan 2009
Location: NW Ohio
Posts: 1,696

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
I hate structure and I hate new construction, I just got sick of it. Money is nice but it aint everything. Never sell my soul for it again.
I will agree to that ! Putting out fires every day when I'm a GC. Getting beat down by GC's when I'm framing. F it. Even when and if things get better I'm done with new const. 29 years I have had enough. I'll live longer doing remods.
strathd is offline  
Old 06-24-2009, 08:01 PM   #34
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by Tinstaafl View Post
Well, that could still be leakage through a different load somewhere else on the circuit. But if you found receptacles wired backward too, it's anybody's guess.

I'd vote with 220. The current leakage, if any was probably on the order of microamps or at best milliamps. Whatever the resistance from fascia to ground would allow. I'd really doubt it had much effect on the electric bill. Except maybe during rainstorms.
Thats why I checked all the outlets also, an old real stone house with aluminum fascia trim touching stone so house is somewhat of a ground right? We'll see in a couple power bills. Thought maybe by chance someone else had some sort of similar experience. Should know better then to ask a legit question on this site.
willworkforbeer is offline  
Old 06-24-2009, 08:03 PM   #35
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by Magnettica View Post
Before this gets real ugly, and I know better because I've posted here for a few years, do you now understand the condition you found at the fascia and why you got shocked?
Yes, and the reason I got shocked by fascia was that I had one hand on aluminum ladder (sunk in ground) and my back bumped the non-painted corner (cut edge). Working on detached garage built close to house.

Last edited by willworkforbeer; 06-24-2009 at 08:08 PM.
willworkforbeer is offline  
Old 06-24-2009, 08:14 PM   #36
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by strathd View Post
I will agree to that ! Putting out fires every day when I'm a GC. Getting beat down by GC's when I'm framing. F it. Even when and if things get better I'm done with new const. 29 years I have had enough. I'll live longer doing remods.
If I can make 1-2k a week and hit a lick once in a while I'm good now. Not going to let stuff own me. At least with HO's I get a little happiness, mostly . No more jobsites for me unless it comes on my terms.
willworkforbeer is offline  
Old 06-24-2009, 09:01 PM   #37
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
Yes, and the reason I got shocked by fascia was that I had one hand on aluminum ladder (sunk in ground) and my back bumped the non-painted corner (cut edge). Working on detached garage built close to house.
Oh, is that why?

Gee, is that normal that current flows on aluminum fascia's or is that objectionable?

Btw, only a complete fool would work on electrical circuits using an aluminum ladder.
Magnettica is offline  
Old 06-24-2009, 09:11 PM   #38
Home Depot aisle walker
 
willworkforbeer's Avatar
 
Trade: home remodeling
Join Date: Mar 2009
Location: Tulsa OK
Posts: 917

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by Magnettica View Post
Oh, is that why?

Gee, is that normal that current flows on aluminum fascia's or is that objectionable?

Btw, only a complete fool would work on electrical circuits using an aluminum ladder.
You sir are a complete idiot, I was working on the garage putting tin on it. Nothing to do with electrical. Do I need to write a small word only essay for you to understand? You remind me of all the "electricians" I know. I got a liscense, whoo, hoo. Electricians like you are pea brained idiots, usually whimpy too.

I'm 45 and have a 145 IQ bitch, what you got? You have nothing except a big stupid mouth.

Last edited by willworkforbeer; 06-24-2009 at 09:22 PM.
willworkforbeer is offline  
Old 06-24-2009, 11:38 PM   #39
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Could Hot Aluminum Fascia Run Power Bill Up?


I've got an IQ of 146!!! Now what are you gonna do about that?!!

I've had run-in's with dumb handymen like you for seemingly all my life. It's people like you who make problems like the one you learned about the hard way and had to come here searching for answers on how to fix it to probably make a quick buck. But you are no electrician. Electrical licenses are not given away without years of practical experience, schooling, and continued education, something you obviously lack, (at least as a wannabe electrician).
Magnettica is offline  
Old 06-24-2009, 11:57 PM   #40
Capra aegagrus
 
Tinstaafl's Avatar
 
Trade: Remodeler
Join Date: Jan 2008
Location: Central Pennsylvania
Posts: 9,758

Re: Could Hot Aluminum Fascia Run Power Bill Up?


Quote:
Originally Posted by willworkforbeer View Post
Should know better then to ask a legit question on this site.
Asked in the right way (which basically you did), a legit question stands a very good chance of getting legit answers here.

But followed up with less than exemplary interrelationship techniques, including denigration of the skills and knowledge of community members with accepted experience and credentials, makes that a tad less likely.

Testing such a circuit for current leakage to ground is a very elementary procedure that any 16 year old electricity/electronics student could do with ease. Apparently you didn't do that; probably I wouldn't have either unless specifically asked by the HO to troubleshoot high-usage problems.

Again, the answer is: Not likely, but possible.

Good luck with it.
Tinstaafl is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Fascia eglanc Windows, Siding and Doors 38 05-02-2009 11:41 PM
aluminum soffit and fascia Something new General Discussion 11 05-01-2009 07:43 PM
wanted: Aluminum Fascia Roller jcalvin Tools & Equipment 38 02-05-2009 04:00 PM
Estimating Aluminum Soffit and Fascia DaNortWoods Roofing 7 07-14-2008 10:41 AM
How do you guys attach your aluminum fascia? dkillianjr Windows, Siding and Doors 30 11-14-2007 08:05 PM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
ContractorTalk.com is for
PROFESSIONAL CONTRACTORS ONLY!

At ContractorTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?