Conduit Spacing (and More)


Is there a minimum space that I can have between conduits?

How many 12AWG THHN wires can I put into a 3/4" conduit, 1/2" conduit? I know it is 40% the cross sectional area of the conduit but I don't know the size of the wire with the insulation on it.

Do I need to run a neutral for each hot in the conduit? Or will one take care of all the hots. (I think it's got to be one for each hot)

Thanks (MD or SP)

Leo

__________________
Sawdust Follows Me Everywhere

Quote:
Originally Posted by HusqyPro View Post
Carpenter by day.
Mad scientist by night.
http://lrgwood.com
Custom Cabinets in Hartford County Connecticut
Leo G is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 08-03-2005, 05:58 PM   #2
DGR,IABD
 
mdshunk's Avatar
 
Trade: Electrical; Commercial and Residential Service
Join Date: Mar 2005
Location: Central PA
Posts: 9,680

Re: Conduit Spacing (and More)


Quote:
Originally Posted by Leo G
Is there a minimum space that I can have between conduits?
No there is not any code, but there are standards on conduit spacing. The U.S. Iron and Steel Institute has the best chart. I'll look it up in a little while and try to post it to this thread.

Quote:
Originally Posted by Leo G
How many 12AWG THHN wires can I put into a 3/4" conduit, 1/2" conduit? I know it is 40% the cross sectional area of the conduit but I don't know the size of the wire with the insulation on it.
For 3/4 you can have up to 16 #12 THHN's. For 1/2 you can have up to 9 #12 THHN's. When you start to fill a pipe this full, you get into concerns about derating the conductor's ampacity. When you have more than 3 current carrying conductors (hots and neutrals, not grounds) in the pipe, it builds heat. This causes a #12 conductor to be rated at less than 20 amps under certain circumstances, depending on how many conductors you fill the pipe with.


Quote:
Originally Posted by Leo G
Do I need to run a neutral for each hot in the conduit? Or will one take care of all the hots. (I think it's got to be one for each hot)
For a single phase panel, two hots on different phases can share one neutral. For a 3 phase panel, three hots on different phases can share one neutral. If all your hots happen to originate on the same phase, then each need their own neutral.

Quote:
Originally Posted by Leo G
Thanks (MD or SP)
No problem Leo. The bill is in the mail.
mdshunk is offline  
Old 08-03-2005, 06:30 PM   #3
DGR,IABD
 
mdshunk's Avatar
 
Trade: Electrical; Commercial and Residential Service
Join Date: Mar 2005
Location: Central PA
Posts: 9,680

Re: Conduit Spacing (and More)


To use the chart, do as follows. If you have, for instance, a 1" conduit next to a 1/2 inch conduit look up 1/2" on the top of the chart and 1" on the left hand side. You can see that the proper spacing is 1-3/4" apart CENTER TO CENTER.
Attached Thumbnails
Conduit Spacing (and more)-conduit-spacing2.jpg  

Last edited by mdshunk; 08-03-2005 at 06:33 PM.
mdshunk is offline  
Old 08-04-2005, 04:44 PM   #4
LRG WoodCrafting
 
Leo G's Avatar
 
Trade: Master Sawdust Producer
Join Date: May 2005
Location: Windsor Locks, Connecticut
Posts: 13,218

Re: Conduit Spacing (and More)


Quote:
Originally Posted by mdshunk
No problem Leo. The bill is in the mail.
OK MD checks in the mail!!:Thumbs:
__________________
Sawdust Follows Me Everywhere

Quote:
Originally Posted by HusqyPro View Post
Carpenter by day.
Mad scientist by night.
http://lrgwood.com
Custom Cabinets in Hartford County Connecticut

Last edited by mdshunk; 08-04-2005 at 05:17 PM.
Leo G is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
ContractorTalk.com is for
PROFESSIONAL CONTRACTORS ONLY!

At ContractorTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?