Hey Guys,
I usually post in the Flooring section as Im a hardwood floor contractor, but Im doing some work in my own home.
Wiring a mini-split a/c and the manual says use a 14 awg & 20A breaker.
I ran about twenty feet of 14 awg exterior sheathed solid wire through conduit at the panel through the exterior wall and to the outside condenser unit.
...*then* I read "use a 20A breaker". Isnt code 12/20?
I thought I was going to use a 15A breaker until I read to use a 20.
Can I use a 20A breaker with this wiring?
This is the manual. See page #24 of the .pdf
http://us.lge.com/download/product/f...%29_011607.pdf
Can this unit operate on a 15A breaker?
See page #11 (first column unit LAN091CNP / LAU091CNP)
InterCounty is offline
Old 06-16-2011, 11:10 AM   #2
LRG WoodCrafting
Leo G's Avatar
Trade: Woodworker Extraordinaire
Rewards Points: 8,347
Re: A/C Wiring Manual Says 14 Awg & 20 Amp Breaker?
On average 14ga should have a 15A and 12ga should have a 20A breaker. In motor circuits the breaker sized can be adjusted for the motor instead of the wire.
In your case I would run the wire as 12ga and use the 20A breaker. The breaker is probably used for the startup current.
Sawdust Follows Me Everywhere
Carpenter by day.
Mad scientist by night.
http://lrgwood.com
Leo G is online now
smasher666 (08-30-2011)
Old 06-16-2011, 11:17 AM   #3
Rewards Points: 896
Yeah I was hoping to avoid repulling.
Would the 14awg on a dedicated line be safe to use?
(20 feet, exterior sheathed, in a conduit)
I assuming LG knows what its unit can handle and what type of wiring is needed.
Is 12awg just being conservative?
Old 06-16-2011, 11:22 AM   #4
LRG WoodCrafting
Leo G's Avatar
Put the 15A breaker on the line to start with. See how the unit handles it. If it works well then leave it. If not, you may have to repull the line. Wait for a real sparky to show up here. 480Sparky will know the answer.
Carpenter by day.
http://lrgwood.com
Leo G is online now
Old 06-16-2011, 12:44 PM   #5
I own stock in FotoMat!
480sparky's Avatar
Rewards Points: 10,308
Originally Posted by InterCounty View Post
................ Isnt code 12/20?............
No. There is no such thing as a single conductor having a single ampacity. Motors have their own set of rules (Art. 430), and they modify the "12/20" rule per 240.2(G).
There are cases where AWG 14 is legal on a 35a breaker. All you really need to look at is the nameplate of the unit... it will tell you the smallest wire size and the largest breaker allowed.
Why is there not a Flat Mars Society?.
480sparky is online now
The Following 4 Users Say Thank You to 480sparky For This Useful Post:
MALCO.New.York (06-16-2011), Rio (06-23-2011), sparks1up (06-26-2011), WildWill (09-11-2011)
Old 06-16-2011, 02:06 PM   #6
GettingBy's Avatar
Rewards Points: 6,486
I believe you, but under what conditions?
35A gives approx. (35A/15A)^2 = 5x the wire heating you'd get with 15A and so probably gives you almost 5x the temp. rise above ambient for the insulation.
I do not understand this.
GettingBy is offline
Old 06-16-2011, 03:21 PM   #7
LRG WoodCrafting
Leo G's Avatar
Motor circuits have there own protection.
Carpenter by day.
http://lrgwood.com
Leo G is online now
Old 06-16-2011, 03:29 PM   #8
480sparky's Avatar
Motors.
What the hell is all this gibberish?
Electricians do. It's called Knowing the Code and Years of Experience.
See how electricical is NOT 'so simple a 12-year-old person of diminished capacity' can do it?
Old 06-16-2011, 03:30 PM   #9
LRG WoodCrafting
Leo G's Avatar
Or a wise guy woodworker.....
Carpenter by day.
http://lrgwood.com
Leo G is online now
Old 06-16-2011, 04:20 PM   #10
GettingBy's Avatar
Motors.
Thanks, I'll scrounge through my '99 NEC on motors and Mullin's explanation of it.
Re: gibberish
I thought the ampacity of a conductor had to do with how hot the insulation gets, due to the ambient temp and wire heating.
The current squared and the wire gauge determines the heating in a length of wire.
So, the same wire carrying 35 amps dissipates 5x more watts than when it's carrying 15A.
Who are you quoting? I doubt there are 12 YO electricians at any level, high or low, of mental capacity.
Old 06-16-2011, 04:22 PM   #11
480sparky's Avatar
As well as the temperature rating of the insulation.... there's more than one. There's also temp. ratings of terminals, number of conductors in a cable/raceway, lots of stuff to consider.
The 12-y.o. remark? Some now-banned member who claimed electrical was so easy a 12-year-old retard could do it.
Old 06-16-2011, 04:30 PM   #12
Carbon Dioxide Producer
DuMass's Avatar
Trade: EC
I guess if someone wanted to look it up for themselves, the NEC cluster hump would basically start with what is now Table 310.15[B],[16], then to 240.4[D], to 240 Table 240.4[G] then to Article 440 and I believe it probably ends at 440.4[C] with the required branch circuit rating and nameplate values in compliance with other sections of Article 440 that are to be provided by the equipment manufacturer.
I might be a concerned about estimated VD on motor or compressor branch circuits, so if it were going to be a long run for that #14, I would probably upsize to #12 instead just for the sake of the equipment.
DuMass is offline
Old 06-16-2011, 04:42 PM   #13
GettingBy's Avatar
Mr. 480sparky, I recommend "Verbal Judo", written by a cop who found a way to handle the daily insults these guys are paid to put up with.
Send this long-gone member to work on a commercial panel and see how long he lasts without being burned, blinded or killed.
Thanks, guys. I'll see if I can reconcile the rules with how I think physics works. Digesting this small chunk of the NEC over several sessions shouldn't give me too much heartburn.
Old 06-16-2011, 05:35 PM   #14
Head Grunt
woodchuck2's Avatar
Rewards Points: 2,196
480 said it best. As another said you can try to run it on the 15 amp breaker and the most it will do is trip the breaker. Otherwise pull a 12ga instead, put it on a 20amp breaker and not worry about it.
As 480 said motors and their manufacturer have their own rule of thumb when it comes to wire size and amp draw. Type of wire and its installation will also make a difference too. Such as aluminum wire, copper wire, solid wire, different types of stranded wire and the insulation used around the wire all play a facter in the amp load it can carry.
woodchuck2 is offline
Old 06-16-2011, 05:43 PM   #15
Fire up the BBQ
griz's Avatar
Rewards Points: 468
What ever you decide to do....
IMO I'd install per manufacturers specs.
If you don't & have a warranty issue, this will give them some wiggle room to stonewall you on any issues.
griz is online now
Old 06-16-2011, 05:46 PM   #16
480sparky's Avatar
Originally Posted by woodchuck2 View Post
........motors and their manufacturer have their own rule of thumb when it comes to wire size and amp draw. ............
Not really a 'rule of thumb'. More like engineering and design protocols, as well as listing requirements. I doubt you'll find a couple engineers sitting in front of a huge computer monitor and have the following conversation:
"Hey, Fred, I'm working on a new compressor design. Do you think AWG 12 and 40 amps will work?"
"Hmmmm. Lemme see, Jim. Well, I see you're using a simple piston-style pump. I've seen those run just fine with number 14 on a 35 amp breaker."
Old 06-16-2011, 06:15 PM   #17
Rewards Points: 896
wOw! Hyjack much?
Ok you guys fried my brain with all that elektikol hocus pocus string theory stuff.
Not to mention I'm an ELEVEN year old retard, so I should pick this all up next year.
So anyway............
Ignore what the manual says 14g & 20a and put a 15a in and wait to see if it trips?
OR
go with manufacturers recs and use the 14g & 20a
I'm inclined to use manufactures recs for warrantee issues.
And yeah, I'll be sure to pick up all your wire clippings the next time you tromp all over my hardwood floor to install receptacles and switches.
...and put 'em in your truck
Old 06-16-2011, 06:23 PM   #18
480sparky's Avatar
..............Not to mention I'm an ELEVEN year old retard, so I should pick this all up next year..............
Old 06-16-2011, 06:24 PM   #19
LRG WoodCrafting
Leo G's Avatar
I am not an electrician, therefore I clean up after myself.
Carpenter by day.
http://lrgwood.com
Leo G is online now
Old 06-16-2011, 06:29 PM   #20
Rewards Points: 896
I thought you meant I was the wiseguy woodworker
...I see you know what I mean about those messy electricians!
...oops did I say that here?
CertainTeed Roofing Updates Exclusive Shingle Applicator's Manual (SAM 10) for Roofin Grumpy Roofing 0 04-27-2011 10:01 PM
stocking service trucks MO-AMPS Electrical 23 11-25-2009 09:39 PM
Sized electrical wiring with breaker Seepaluce NEC Discussion 5 01-31-2009 10:27 PM
Manual, Parts catalog for engine and equipment technics TomDorvan Excavation & Site Work 0 12-05-2008 03:15 AM
Breaker keeps popping DErnest Electrical 2 09-15-2006 05:30 PM