Buck Boost Xfrmr
Old 11-13-2006, 07:04 PM   #1
Union Electrician
Sparky Joe's Avatar
Trade: Inside Wireman
Buck Boost Xfrmr
Anyone sized a buck boost transformer lately? We had one last Friday, the machine(a t-shirt heater) draws 13.5 amps at 230V according to nameplate, building has 208V. I tried to remember from school and we looked at an Ugly's, but finally resorted to a chart for a .75 kVA.
Anyone know what math is involved in figuring this out?
Sparky Joe is offline
Old 11-13-2006, 07:06 PM   #2
mdshunk's Avatar
Re: Buck Boost Xfrmr
I prefer Acme transformer as my brand for buck-boost transformers. They have an excellent calculator/product selector on their site: http://www.acmepowerdist.com/product...ide/index.aspx
mdshunk is offline
Old 11-13-2006, 07:11 PM   #3
Union Electrician
Sparky Joe's Avatar
Wow, those are all 8 to 10 times larger than what we bought, hope it works, and furthermore hoped we saved some money in buying what we did
And the one we bought was 23 pounds not 110
Old 11-13-2006, 07:21 PM   #4
mdshunk's Avatar
For single phase, you'll be using one very heavy transformer. For 3 phase, you'd use either 2 or 3 very light transformers. I calculate you'd need about a 5 KVA. That's got a little weight to it.
The formula for single phase is KVA=(output volts * secondary amps)/1000
In your case, 3.2, and the next common size is 5.
The 3 phase calc is necessarily much more involved.
mdshunk is offline
Old 11-13-2006, 07:25 PM   #5
Union Electrician
Sparky Joe's Avatar
A 5 kVA was what I figured while looking at them in the supply house too, but now figuring it's a 30 volt difference and would be connected to a 20amp breaker, I get .6 kVA and the next one to match was a .75. Just my guess though
Maybe I'll go post it in Mike Holt's seeing as neither my Dad or my teacher are responding to e-mails
Old 11-13-2006, 07:57 PM   #6
Union Electrician
Sparky Joe's Avatar
I know what kVA is, just a fancy way of saying watts, or kilo watts rather
That's what I was thinking(as noted above) you only figure the kVA of the boost, but by that logic would it be a negative kVA for buck?
Old 11-13-2006, 08:38 PM   #7
Union Electrician
Sparky Joe's Avatar
Now MD or Pete(the code Guru) would we now also need some sort of over current device after the transformer? something to do with the tap rules? Whereas the thing was originally cord and plug connected.
Old 11-13-2006, 08:47 PM   #8
mdshunk's Avatar
The OCPD for the primary of a .75 KVA buck-boost will be 20 amps. That will work to protect the secondary as well. The primary and the secondary are interconnected on a buck boost.
mdshunk is offline
Old 11-14-2006, 09:37 PM   #9
Union Electrician
Sparky Joe's Avatar
Here's what I got from Holt's forum. seemed to look right to me;
Boosting 208 using a 240:32V buck boost.
Have 208V available so boost is 208/240*32 = 27.73V
( 240:32 => 208:27.7 )
Total boost is 208 + 27.73 = 235.73V
Total load is 13.5A x 230V = 3105VA (given)
Current in secondary coil is 3105/235.73 = 13.17A.
Buck/Boost VA = 13.17 * 27.73 = 365.2VA
Current in primary coil is 365.2/208 = 1.76A
The currents add in this case for primary 13.17 + 1.76 = 14.93A
14.93A x 208V = 3105VA (input VA = load VA)
The kVA of the transformer is where it says 365.2VA (which is 0.3652 kVA for those slow on their math)