Trade: Electrician
Ansul System Wiring
I have been an electrician for 15 years, but have never wired an ansul system. I need wiring advice. I have the five 120v receptacles under the hood that must turn off when the ansul is activated, and an exhaust hood that must go on. The wiring on the system has four micro switches with a NO, NC, and common contacts. How do I wire this system to do what I need with shunt trip breakers. Any advice would be VERY helpful. Also, of course the exhaust fan must be switched.
Ummm wire guy?
Trade: Professional Wire Slinger and Part Time Haji Wrangler...
Re: Ansul System Wiring
I'm gonna leave the whole "search for threads" speech to someone more witty than I (MDShunk, Celtic, Speedy? Any takers?) and give you some help. There is also a link that will take you back to contractor talk, but a different thread (hence searching).
http://forums.mikeholt.com/archive/i...p/t-82683.html
Friendship is like peeing on yourself: everyone can see it, but only you get the warm feeling that it brings |
Fentoozler
....don't forget the FA tie in and the hood lights.
Trade: electrician Phoenix AZ
I've only done a few over the years and I always just have to start from the beginning and draw the circuit.
Basically, ex fan goes on, makeup air and anything elec under the hood goes off Lets see......Two contactors and two micro switches. One for exhaust fan, one for makeup air, lights and receps??? EXF... 120V power to supply side of toggle switch and common terminal of EXF micro switch. Load side of toggle sw to EXF contactor coil and MUA micro switch common terminal. NO terminal of micro sw to EXF contactor coil. MUA etc.. NC terminal to MUA coil. Draw it....I might be off somewhere. Any shunt trip breakers will be run thru the other micro switches. NO, NC ??? It's been 20 years since I saw a shunt trip breaker. I am thinking it ould be a NC situation.
Just because it's within code doesn't make it safe. Just because it's against code doesn't make it unsafe. |
Electrical Contractor
Trade: Electrical
I have done a few but the Ansul guys always had a schematic.
From an electrical standpoint they are easy. The micro switch just need to break the M-U air fan and make fan circuit as 220 said. In all the ones I have done the lights had nothing to do with the Ansul system. They are stand alone.
Trade: Electrical
Do not be afraid! It is easy to make this alot more complicated than it is. Simply set a sub panel fed by a shunt trip breaker. Have ansul system activate the shunt trip. Feed make up (supply) air,all electrical equipment and outlets, except for exhaust fan located under the hood through sub panel.
Trade: Fire Suppression Equipment Sales & Service
Is this a new install? If it is a Captive Aire Hood or Greenheck Hood, there may be an auxillary electrical panel included with the hood. Ask the hood installer. Is there an electric gas valve? If so, it needs to shut off when the fire suppression system trips. You need a relay to turn the gas back on. Check w/the suppression tech. The suppression tech will also have the wiring diagram.
When the exhaust fan is turned on, the make-up air is to turn on. All heat producing appliances under the hood need to shut off. Some inspectors may require the lights to shut off. |
Trade: retired electrician
I am in the same fix. Did you get a wiring diagram for this?
I am a retired electrician after 30 yrs. |
Trade: HVACR
NO- Normaly open
NC- " closed C- Common constant 110vac MAKE SURE THE COMMON IN THE ANSUL BOX HAS A CONSTANT 110vac hot wire. (no need for neutral in the Ansul box.) If you want something to go OFF(lights, outlets ect) 1st option NC to Contactor 110vac coil (use poles for diffrent circuts) Contactor stays closed... Ansul Activated, contactor opens ie. no power. 2nd option NO to a shunt breaker. ( a shunt breaker has 2 spaces behind the hot wires). Get a netural (white) anywhere. Wire the hot on the shunt breaker to NO...Ansul Activated , power to the shunt breaker, Trips breaker , No Power To turn something on Wire a parrall contactor (110vac coil ) with the Fan switch and wire to NO. In effect bypassing the switch. 2 wires from the fan switch...wired top and bottom of your contactor is easy as pie. SOMETIMES WHOLE PANEL BOXES ARE SHUNTED...The main is a shunt breaker. Wire that baby to the NO and the whole panel goes off. SWEET. Make sure your ex. fan, or constant 110 to Ansul, is not in this panel! |
woodchuck2
Here is a wire diagram that i found online on another site that may help you. Wiring these is simple and straight forward.
| The Following 2 Users Say Thank You to woodchuck2 For This Useful Post: | Bubbles (11-14-2009), plumelectric (08-10-2010) |
cowboym
Trade: Master Electrican and Electrical contractor
Thanks for making the wiring from micro switch so easy.I did not us shunt trip breaker,just two contactors with 120 volt coils in seperate j boxes. one turns off the 3 phase power make up air and one for recp under hood did not have to turn off lights under hood firemarshal told me.This is in Texas
| Styrafoam wall system? | mhillis | General Discussion | 6 | 10-31-2008 06:58 AM |
| System Bonding Jumper vs. Main Bonding Jumper | Mark Twenhafel | NEC Discussion | 3 | 02-09-2008 06:15 PM |
| Living Filter Septic System | jmic | Excavation & Site Work | 18 | 07-20-2007 09:31 PM |
| Systems Development List | Gordo | Business | 19 | 01-08-2007 07:28 PM |
| forced hot-water system | daniem1 | HVAC | 1 | 03-02-2006 05:37 AM |