When we stripped out the drywall
in a bathroom all of the wire we see is #12.
The bedroom boxes on the other side of the
wall are #12 as well. It's all aluminum.
Went to shut off the circuits we are working
around, the panel is piggy-back hell, and
all of the bedroom and bathroom breakers
are 20 amp. Were the original breakers
supposed to be 15's? Or are the 20's alright?
It's been a long time, but I thought aluminum
was #12 for 15amp, and I don't remember
20 amp circuits for bedrooms or
bathrooms back then.(1969)

Forgot:
House was built in 1969, I just want to know
if they have a problem there or if I just have
a bad memory for how this stuff went 40 years ago.

__________________
Put your location in your profile!
(Sorry....it seems there really are dumb questions)

Last edited by neolitic; 02-29-2008 at 07:16 AM. Reason: OOPS!
neolitic is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 02-29-2008, 07:19 AM   #2
Curmudgeon
 
neolitic's Avatar
 
Trade: carpentry/remodeling/"Yes M'am we do"
Join Date: Apr 2006
Location: Beech Grove, Indiana, Birthplace of the "King of Cool"
Posts: 11,707

Re: Aluminum Gague


bump
__________________
Put your location in your profile!
(Sorry....it seems there really are dumb questions)
neolitic is offline  
Old 02-29-2008, 03:06 PM   #3
Pro
 
dkillianjr's Avatar
 
Trade: Construction and Remodeling
Join Date: Aug 2006
Location: Pittsburgh, PA
Posts: 2,531

Re: Aluminum Gague


I do believe that a 15 amp circuit requires a 12 gauge aluminum wire as apposed to a 14gauge copper. I can remember reading in the nec book that all 14 gauge aluminum wire must be replaced, I could be wrong though. The real electritians should be around shortly to confirm or deny that



Dave

Last edited by dkillianjr; 02-29-2008 at 03:20 PM.
dkillianjr is offline  
Old 02-29-2008, 03:19 PM   #4
Electrician
 
jrclen's Avatar
 
Trade: Electrical Contractor
Join Date: Jul 2007
Location: Central Wisconsin
Posts: 265

Re: Aluminum Gague


#12 Aluminum is rated for 20 amps. But it must be protected by no larger than a 15 amp breaker or fuse. So your memory is fine.

Last edited by jrclen; 02-29-2008 at 03:24 PM.
jrclen is offline  
Old 02-29-2008, 06:05 PM   #5
Curmudgeon
 
neolitic's Avatar
 
Trade: carpentry/remodeling/"Yes M'am we do"
Join Date: Apr 2006
Location: Beech Grove, Indiana, Birthplace of the "King of Cool"
Posts: 11,707

Re: Aluminum Gague


Quote:
Originally Posted by jrclen View Post
#12 Aluminum is rated for 20 amps. But it must be protected by no larger than a 15 amp breaker or fuse. So your memory is fine.
Thanks, I'll start trying to line up
a sparky tonite.
I think half the breakers they have
will be over loaded when he
switches them back to 15's.
This is gonna get real interesting.
__________________
Put your location in your profile!
(Sorry....it seems there really are dumb questions)
neolitic is offline  
Old 02-29-2008, 07:17 PM   #6
Service & Repairs
 
Magnettica's Avatar
 
Trade: Electrician
Join Date: Dec 2006
Location: Rahway, New Jersey
Posts: 3,998

Re: Aluminum Gague


NEC Article 240.4 (D)

(D) Small Conductors. Unless specifically permitted in
240.4(E) or 240.4(G), the overcurrent protection shall not
exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG,
and 30 amperes for 10 AWG copper; or 15 amperes for
12 AWG
and 25 amperes for 10 AWG aluminum and
copper-clad aluminum after any correction factors for
ambient temperature and number of conductors have
been applied.
Magnettica is offline  
Old 03-01-2008, 10:46 AM   #7
Electrician
 
jrclen's Avatar
 
Trade: Electrical Contractor
Join Date: Jul 2007
Location: Central Wisconsin
Posts: 265

Re: Aluminum Gague


Quote:
Originally Posted by Magnettica View Post
NEC Article 240.4 (D)

(D) Small Conductors. Unless specifically permitted in
240.4(E) or 240.4(G), the overcurrent protection shall not
exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG,
and 30 amperes for 10 AWG copper; or 15 amperes for
12 AWG
and 25 amperes for 10 AWG aluminum and
copper-clad aluminum after any correction factors for
ambient temperature and number of conductors have
been applied.
That's exactly what my book says too Mag. We must have the same book.
jrclen is offline  


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Siding: Aluminum vs. Vinyl Grumpy Windows, Siding and Doors 21 03-30-2010 08:02 PM
Strange aluminum wire ? nywoodwizard Electrical 3 11-15-2007 10:00 PM
Aluminum to copper lug Mike Finley Electrical 21 06-03-2007 12:31 AM
Another aluminum wiring question ron schenker Electrical 18 03-08-2007 06:54 PM
Vinyl over aluminum? Sal616 Windows, Siding and Doors 6 02-20-2006 09:37 AM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
ContractorTalk.com is for
PROFESSIONAL CONTRACTORS ONLY!

At ContractorTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?