3 Phase 208 Leg
Old 01-11-2005, 07:01 PM   #1
DEW's Avatar
3 Phase 208 Leg
I was wondering if the only way to use the middle 208v leg for 110v was to use a double pole breaker on the 208v leg and either of the 2 other hot legs,then put 110v on each pole.
Any help is greatly appreciated,
Doug
DEW is offline
Old 01-15-2005, 03:22 AM   #2
voltamp's Avatar
Re: 3 Phase 208 Leg
It appears that you have a 120/208 3 phase service
Any single pole or circuit breaker will give you 110 volts
Any double pole or two circuits A/B, A/C, B/C will give you your 208 volts single phase
All 3 phases A/B/C will give you 208 volt 3 phase.
One should know when to back away or something is over your head. Thats why there are specialists.
voltamp is offline
Old 01-16-2005, 02:10 AM   #3
marxlaws's Avatar
Rewards Points: 75
Re: 3 Phase 208 Leg
in a delta/delta config you 208 to neutral on l2 or b leg ( high leg) 120 to n on a and c and 240 between a,b and c , if that is what you got, there aint no getting around it. what do you have?