Originally Posted by farmerkev View Post
Meadow, not sure what that would be.
dielectricunion, what's the way of fixing that?
The plug configuration.
https://www.google.com/search?q=nema...ed=0CAYQ_AUoAQ
Just to make sure you have the right plug.
Meadow is offline
Old 12-02-2014, 07:38 PM   #22
farmerkev's Avatar
Trade: Carpenter, remodel, landscape
Rewards Points: 74
Well I turned off the power to the outlet and took the cover off and tried plugging the welder in a few times. Looking closely when the welder plug goes in one of the hots and the ground lug would contact each other. Replaced the outlet and bingo, back in action. I just didn't notice it before because I never tried pluggin it in without the cover on. Thanks for all the help guys.
farmerkev is offline
The Following User Says Thank You to farmerkev For This Useful Post:
CarpenterSFO (12-11-2014)
Old 12-02-2014, 07:40 PM   #23
I'm The BOSS
jaydee's Avatar
Trade: builder / remodeler
Rewards Points: 4,733
your welcome.
Oh wait, I WAS going to say the receptacle is shorting to ground.
We'll give your home a NEW IMAGE
New Image Construction & Design
New image Construction.com
Facebook
jaydee is offline
Old 12-02-2014, 07:54 PM   #24
muskoka guy's Avatar
Trade: framer/builder
Rewards Points: 558
Might be a good idea to change that breaker back to the proper one. Just a thought.
muskoka guy is offline
Old 12-02-2014, 08:25 PM   #25
farmerkev's Avatar
Rewards Points: 74
Why is it the wrong breaker?
Old 12-02-2014, 08:41 PM   #26
jb4211's Avatar
Rewards Points: 2,306
I believe his point is the dedicated breaker's rating should correlate with the draw, not have excessive excess.
Jon
jb4211 is offline
Old 12-02-2014, 08:43 PM   #27
Box Builder
Morning Wood's Avatar
Rewards Points: 9,244
Yeah. 30 amp welder. 30 amp breaker.
Morning Wood is online now
Old 12-11-2014, 02:02 PM   #28
saynever's Avatar
Trade: electrical
Rewards Points: 229
Not correct. Because electric arc welders are based on duty cycle and their max current draws are normally not more than a few minutes, the section in the code book referring to dedicated circuits for welders allows a certain amount of up sizing of the breakers to prevent tripping at max duty cycles.
Look it up.
If its a general purpose 240v garage circuit I concur with the appropriate size ocpd for the wire's ampacity.
saynever is offline
Old 12-11-2014, 10:06 PM   #29
Box Builder
Well, I'm not an electrician, I just post on electrical threads. That said. I run my welders that are supposed to be 30 amps on 20 amp breakers without any issues.
Old 12-11-2014, 10:51 PM   #30
CarpenterSFO's Avatar
Rewards Points: 2,044
I install the breaker allowed by the wiring.
- Bob
CarpenterSFO is offline
The Following User Says Thank You to CarpenterSFO For This Useful Post:
Speedy Petey (12-13-2014)
Old 12-13-2014, 07:39 AM   #31
Electrical Contractor
Speedy Petey's Avatar
Trade: Electrical
Rewards Points: 1,244
The breaker protects the wiring, NOT the load (welder in this case). So a "30A welder", which is an inaccurate description btw, certainly CAN be plugged into a 50A circuit. How is this ANY different than a 1A radio plugged into a 20A kitchen counter receptacle?
In fact my Miller 175 draws in the 30A range max, and came from the factor with a 50A/250V plug attached. This is very convenient since many buying a medium sized mig such as this will already have a stick welder, as I did.
Speedy Petey is offline
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
Morning Wood (12-15-2014), Railman (12-14-2014)
Mig welder advice Bearded Wonder Tools & Equipment 27 08-24-2013 07:21 AM
Miller Arc Welder bellemech Contractor Swap 1 10-21-2010 10:43 PM
How many of u keep a welder around JKBARR127 Tools & Equipment 20 03-11-2010 08:51 AM
230V Welder...horrible with flux core Kastoria Welding & Steel Trades 6 11-12-2009 08:50 AM
Need guidance in helping a Welder in Virginia become a contractor... Max Nomad General Discussion 1 12-26-2008 06:28 PM