240 To Ground = 0
Old 09-29-2007, 07:57 AM   #1
Master Electrician
Bubbles's Avatar
Trade: Electrical
240 To Ground = 0
Were on a commercial job doing lighting and just for fun we took some numbers on one of the subpanels. We get 240 to ground on 2 and the center phase we get 0. On a 2 pole 20 amp breaker we get 240 to ground and 240 to ground on both screws. I've seen all kinds of other numbers on 3 phase weve been on just havent seen this one yet. Going to have to get books out but is there an old timer out there that has seen this and has some insight on this one. It doesnt affect our job there at all just curious.
Thanks in advance
Bubbles is offline
Old 09-29-2007, 08:34 AM   #2
Baltimore Electrician
JohnJ0906's Avatar
Trade: Electrician
Re: 240 To Ground = 0
Sounds like a corner grounded delta. 240v 3 ph.
The leg you are getting 0v to ground is the leg that is grounded. You should have 240v between any 2 legs.
John from Baltimore
"One Day at a Time"
All replies based on the 2008 NEC
Originally Posted by celtic
Deny Everything, Admit Nothing, Demand Proof
JohnJ0906 is offline
Old 09-29-2007, 08:47 AM   #3
Service & Repairs
Magnettica's Avatar
Trade: Electrician
How is it that you get "240 to ground and 240 to ground on both screws?"
You should be reading 240 to ground, and 480 between the two phases.
Magnettica is offline
Old 09-29-2007, 09:16 AM   #4
Celtic's #1 Fan
mahlere's Avatar
Trade: electrical
ok...someones got bad numbers....
is it 240? 120? or 277? to ground?
mahlere is offline
Old 09-29-2007, 11:27 AM   #5
Philadelphia electrician
RobertWilber's Avatar
Trade: Electrical contractor
Absolutely agree.
Just 3 wires coming in?
No neutral, right? No 120 off this service? There is another 120/240 service here for receptacles, right?
Like he says, you will read 240 between any two "hot" conductors, but 2 read 240 to ground and one reads 0 to ground.
Straight 240 delta, corner ground.
Old, rare dog.
RobertWilber is offline
Old 09-29-2007, 11:41 AM   #6
Celtic's #1 Fan
mahlere's Avatar
Trade: electrical
Originally Posted by RobertWilber View Post
Absolutely agree.
Old, rare dog.
just like this EC from philadelphia I heard about...
mahlere is offline
Old 09-29-2007, 11:48 AM   #7
mdshunk's Avatar
I don't think I've ever worked on a corner grounded 240 delta, but the measurements taken pretty much square with what you'd expect from such a system. I wonder if the OP could say what sort of place this was where these measurements were taken? I expect that it's a very old industrial building of some sort.
mdshunk is offline
Old 09-29-2007, 12:34 PM   #8
Master Electrician
Bubbles's Avatar
Trade: Electrical
Yeah. Good eye everyone. I think this is a corner delta. Its definate a 3 wire delta config coming out of CT to main dissconnect then all kinds of transformers and subs all over to get 120v where needed. Its a big 20,000 sq ft warehouse. All the high bays are running on 240 now some 120. I think it was built in 50's or 60's. Appreciate the tips.
Bubbles is offline
Old 09-29-2007, 07:22 PM   #9
JohnJ0906's Avatar
Trade: Electrician
The reason I recognize this is that a funeral home we do service for has a dual service - 120/240 1ph and 240, 3ph delta for heat loads and the elevator. POCO still provides it in a few areas.
John from Baltimore
"One Day at a Time"
Old 09-29-2007, 07:32 PM   #10
Union Electrician
Sparky Joe's Avatar
Trade: Inside Wireman
The power company will still feed a building with 3 wire 240 3 phase, but grounding one of the phases to everything metal is something that's done on site.
Sparky Joe is offline
Old 09-29-2007, 08:32 PM   #11
mdshunk's Avatar
Yeah, I have a feeling that these are overhead services, derived from a bank of pole top kettles. If it comes from a padmount, I'd bet you're getting the neutral whether you need it or not.
mdshunk is offline
Old 10-15-2007, 10:35 PM   #12
HVAC_NW
Guest
HVAC_NW's Avatar
Posts: n/a
Can I assume that transformer is dedicated for that customer? If not, how is it determined which phase is the one to be grounded?
If there are more than one customers on that transformer and customer one decides to make phase one a ground, customer two decides phase to a ground, well bad things happen.
Old 10-16-2007, 09:43 PM   #13
goose134's Avatar
Trade: Union Electrician
I'm not sure if it it's actually stipulated anywhere in the code but I believe traditionally the B phase is the one that is grounded (at least around here). Same goes for high leg systems. A and C will have 120 each to ground, and B will be 240. Only seen 2 of these but if you start seeing circuits 1,5,9,11.. you'll know.
goose134 is offline
Old 10-16-2007, 11:01 PM   #14
Union Electrician
Sparky Joe's Avatar
The corner ground delta utilizes a high impedance ground. which still allows high fault tolerence that an ungrounded system does, but without all the personnel safety issues of a direct corner ground. And an added benefit of troubleshooting a fault because you still have current flow in the faulted conductor and the system is still up and running.
I highly doubt the power company would feed two customers a delta system from the same transformer, but if they did it would not be a problem.