20 & 15 Breakers With 12/3 Awg
Old 01-08-2006, 12:13 PM   #1
louis bugaj's Avatar
Trade: electrical
Can I connect 20 amps and 15 amps breakers to 12/3 AWG, black and red, using the same common white?
I don't any where in NEC that I can not.
Louis Bugaj
louis bugaj is offline
Old 01-08-2006, 12:40 PM   #2
mdshunk's Avatar
Re: 20 & 15 Breakers With 12/3 Awg
Yes, you certainly may. It is never a violation to use a heavier wire than the circuit's overcurrent protective device. If the leg of the 12-3 that is on the 15 amp breaker will have any 14 gauge connected to it downstream, label that conductor in the breaker panel as such. That will keep someone in the future from scratching their head, thinking, "Hey, what's this #12 wire doing on a 15 amp breaker. I'll fix that and put in a 20". This proposed conductor labeling isn't a code requirement, but a "good idea" often times.
mdshunk is offline
Old 01-08-2006, 02:16 PM   #3
Electrical Contractor
Speedy Petey's Avatar
Trade: Electrical
Louis,
Yes you can but can I ask why you would want or need to?
Speedy Petey is offline
Old 01-08-2006, 02:30 PM   #4
copusbuilder's Avatar
Trade: Builder/Remodeler- Master Electrician
If I am following you correctly you will want the black and red on different legs (phases) if you are sharing the neutral.
copusbuilder is offline
Old 01-11-2006, 06:34 PM   #5
Trade: electrical
Originally Posted by Speedy Petey
Louis,
My customer overloaded his 15 amps circuit. The 14/2 ran under the crawspace from the main breaker. I want to give him 20 amps on one duplex and keep the remaining receptacles on the original 15 amps.
Louis Bugaj
ice breakers for repeat customers POOLMANinCT Pool Construction & Enclosures 3 03-11-2007 10:20 PM
The Breakers - Newport, RI MattCoops Flooring Picture Post 7 10-25-2006 08:58 AM
Arch fault breakers edirector Electrical 17 08-25-2006 03:27 PM
How many Breakers in a panel robertc65 Electrical 2 02-21-2006 02:09 PM
Using 12/3 to power Two Circuits robertc65 Electrical 18 02-16-2006 12:26 AM