Point Load And 2hr Fire Resistance
Old 02-12-2009, 09:04 AM   #1
jjwee's Avatar
Trade: Main Contractor
Hi,
I am working in Singapore. The project involve in right now, requires the use of CMU blocks of various sizes. And ALC blocks.
Having a difficult time searching for the 90mm CMU blocks 2hr FR test report. As I have only manage to find 140mm and 190mm.
Point loads for ALC are very low, are there any tests done or available reports for both ALC and CMU?
JJ
jjwee is offline
Old 02-12-2009, 09:20 AM   #2
Tscarborough's Avatar
Re: Point Load And 2hr Fire Resistance
Contact your local supplier as any information relating to these 2 specific properties will rely upon the materials used in that location.
Tscarborough is offline
Old 02-12-2009, 09:25 AM   #3
concretemasonry's Avatar
Trade: Masonry consultant
According to most standards, you will not find a 90 mm CMU that has a 2 hour rating without any covering.
Different building codes refer to different material standards. Your standards may be different.
The fire resistance of a block depends on the type of aggregate used to make it. The same size and shape (same face shell thickness also) can have differenr fire ratings depending on the aggregate.
Point load capacity on a wall will depend the height and thickness of the wall in addition to the obvious bearing area.
I have no idea that your term "ALC" refers to.
One of the most commonly used masonry design codes in the world is ACI 530 that also lists the appropriate materials standards to the code is based on.
Dick
concretemasonry is offline