Trade: general contractor
Grounding Rebar
when pouring a footing who would usually do the grounding of the rebar, the mason or an electrician?
Re: Grounding Rebar
Rebar is not grounded. It can be used as a ground.
Trade: sparky
Re: Grounding Rebar
WWHHOOAAAA there pardner.
If the rebar fits the bill as described in the NEC, it MUST be utilized as a grounding electrode. It is commonly called a Ufer ground (after the man the engineered it in 1946 (I think) in Arizona or some other dry desolate western state) and I would strongly suggest an electrician do it so it is correct. what I do is tell them to stick the end of one of the rebars out in a location I choose so I can attach to it later. but to further make a point, the rebar is grounded by virtue it is inside moist, mineral bearing concrete which is in contact with the earth. That is why it is used as an electrode; it is already grounded. |
Re: Grounding Rebar
On new construction we, (the footing crew), will provide and put in place a solid copper wire that serves as the Ufer Ground.
We make sure it exits the concrete in the correct location and with sufficient length to reach the electrical panel. On remodels/additions it is usually not required. |
#5 | |
Re: Grounding RebarQuote:
http://www.mikeholt.com/mojonewsarch...r~20030914.htm ...and yes. I leave it to the electrician. Last edited by tkle; 01-03-2009 at 06:37 PM. |
I'm a Mac
Trade: ICF Construction
Re: Grounding Rebar
Hey, I just had something similar answered. Should be the electrician who installs it, but most times there is no electrician when I am building and pouring foundations so I install it. Mag tells me use #4 and you can't go wrong.
Chris |
#7 | |
Trade: sparky
as a matter of fact, a ground rod is not even required when there is a Ufer ground. A rod is a supplemental electrode required when other electrodes are not used or available. you are really misinterpreting what the link you provided states. |
#8 | |
Trade: sparky
and on remodels; it is not required to damage existing concrete so as to be able to attach. A ufer ground is only required to be utilized when new 'crete and bar is used. |
#9 | |
Here is where I got my knowledge on Ufer. |
#10 | |
Trade: sparky
and it may get approved that way but has the inspector ever actually seen this or simply seen the GEC hanging out of the concrete? It is not legit nor legal. this is where you need to get the specific requirements:http://www.constructionbook.com/2008...nec-code-2008/ Last edited by nap; 01-03-2009 at 07:40 PM. |
#11 | |
Other that that we're saying the same thing. The ufer is the ground. Also copper reacts to the alkali in the concrete. http://www.psihq.com/iread/ufergrnd.htm |
#12 | |
In fact we had an instance last summer where the wire left out of the footer got cut, the inspector made us dig a trench minimum 10 feet long and lay a cooper wire in it, hold it off the soil with stakes, he looked at it and then we poured concrete around it. No rebar in the trench. I will make it a point to ask about this on the next one we do. |
Re: Grounding Rebar
That's what I was thinking. I'll just clamp the wire to the rebar and let it run wild, have the electrician hook it up latter. Saves a trip by the electrician.
Trade: electrical contractor
Re: Grounding Rebar
You need to know what code cycle they (AHJ) are using before you can answer this question. But if your using it it should be attached to the rebar not just laying in the concrete.
www.srelectric.org Texarkana,TX Electrical Contractor |
Re: Grounding Rebar
My understanding was the connection had to be exposed. Perhaps a void during concrete placement along with heat and cold cycles or a reaction due to the ph factor could result in a poor connection. I thought all electric connections had to be accessible for that matter. I don't know, other just being a dumb mason I have studied electrical codes in school but that was in 85'.
Thom
Re: Grounding Rebar
Our inspectors require the connection to be accessible. The rebar in the footing is all connect by lapping and wrapping all the joints with tie wire. One piece of rebar is bent up to extend into a wall cavity. The connection to the grounding wire must be accessible. Generally we screw a mud ring to a stud in front of the connection and put a blank cover on it.
At the time of the final inspection the inspector will check to insure that connection is accessible. He will remove the blank cover to check the connection. If the connection is improper or not accessible we will get a correction notice. |
Re: Grounding Rebar
As a flatwork guy, I had to ask why there was a piece of rebar sicking up out of the footing in the basement. Here, they leave a piece of rebar that is tied to the grid of rebar in the footing sticking up in the basement, and I finish around it. Then they, as I was told "bond" the rebar that is left sticking up.
#18 | ||||||||
Trade: sparky
Other that that we're saying the same thing. Quote:
from your link: Quote:
#19 | |||
Trade: sparky
#20 | |
Trade: sparky
Like I said, you do have to use a bonding method listed for use in concrete. I typically cadweld the copper to the rebar. I'm not trying to be an ass here guys. I am merely telling you what the code requires and the reasons behind it, as best as I can. If I came across any other way, I apologize. I simply wanted your installs to be proper. If they aren't, there is really no reason to even bother with them. Last edited by nap; 01-04-2009 at 10:57 PM. |
| Need help with a shocking outside waterspout | Badoish | Electrical | 23 | 12-27-2008 04:18 PM |
| shocked when touching bath faucet | earl964 | Electrical | 28 | 09-16-2008 05:50 PM |
| Generator Grounding | K2 | Electrical | 8 | 09-22-2006 12:16 AM |
| What do you guys think? | krthomp33 | Electrical | 18 | 06-27-2006 08:59 AM |
| Grounding | brian11973 | Electrical | 20 | 06-03-2006 07:18 PM |