Block Not Level Around Perimeter.


I need to install sill plate on block begining this week and the mason has left me in a mess. The block is out at least 1 1/2" higher in one area the the rest of the block around the perimeter. Also there is a center support wall running through the basement which is 1" higher than perimeter and it is the center support for I-joist which will span from one side to other. How do you go back and compensate for this with sill plate? Can you go back and level the top of the block in anyway? I thought of pouring a 6" cap ontop of block to make it level all the way around perimeter what you guys think?

straightline is offline  
Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ContractorTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 10-05-2009, 01:04 AM   #2
Pro
 
lukachuki's Avatar
 
Trade: Customer Education & Development
Join Date: Feb 2005
Location: Aiken SC
Posts: 1,333

Re: Block Not Level Around Perimeter.


Quote:
Originally Posted by straightline View Post
I need to install sill plate on block begining this week and the mason has left me in a mess. The block is out at least 1 1/2" higher in one area the the rest of the block around the perimeter. Also there is a center support wall running through the basement which is 1" higher than perimeter and it is the center support for I-joist which will span from one side to other. How do you go back and compensate for this with sill plate? Can you go back and level the top of the block in anyway? I thought of pouring a 6" cap ontop of block to make it level all the way around perimeter what you guys think?
Hold your "Mason" (handyman?, out of work electrician) accountable for his crappy work if he can't afford it buy him a string.


If your "mason" won't stand behind his work I suppose you could cut out the High spots using a 1/4" grinder and 7" masonry blade or a quickie saw and the low spots fur out with treated.
__________________
"The problem with internet quotes is, you never know if they are authentic." -Abraham Lincoln-

Less with the jaw more with the paw!

Last edited by lukachuki; 10-05-2009 at 01:06 AM.
lukachuki is offline  
Old 10-05-2009, 01:12 AM   #3
Super B
 
skyhook's Avatar
 
Trade: General Contractor Lic. since 1985
Join Date: Mar 2007
Location: Socal Ground Zero
Posts: 4,166

Re: Block Not Level Around Perimeter.


Quote:
Originally Posted by lukachuki View Post
Hold your "Mason" (handyman?, out of work electrician) accountable for his crappy work if he can't afford it buy him a string.
String sags.
Be easier to add some concrete to make it level.
skyhook is offline  
Old 10-05-2009, 02:04 AM   #4
Registered User
 
_SpinDrah's Avatar
 
Trade: Mason
Join Date: Sep 2009
Posts: 8

Re: Block Not Level Around Perimeter.


Is this a joke? if not, don't pay him untill he fixes it.

sure lines sag, thats what twigs are for.
_SpinDrah is offline  
Old 10-05-2009, 06:49 AM   #5
Pro
 
CJKarl's Avatar
 
Trade: Masonry
Join Date: Nov 2006
Location: Ivoryton CT
Posts: 1,992

Re: Block Not Level Around Perimeter.


Could add or could cut off. Probably faster to cut it, probably look better poured.
__________________
There's Always A Market For Quality
http://www.kaufmannmasonry.com/
CJKarl is offline  
Old 10-05-2009, 07:16 AM   #6
Pro
 
rselectric1's Avatar
 
Trade: Licensed Electrical Contractor and Remodeler
Join Date: Sep 2009
Location: Chicago Suburbs
Posts: 7,002

Re: Block Not Level Around Perimeter.


Sounds like you need a better mason.

If you are the GC and hired this guy, make HIM fix it.
If you are the carpentry sub, show the GC/homeowner the issue and explain that you cannot build on top of his work without compromising the quality of your work.
__________________
220...221...whatever it takes!
rselectric1 is offline  
Old 10-05-2009, 07:58 AM   #7
Pro
 
6stringmason's Avatar
 
Trade: masonry
Join Date: May 2005
Location: Green Bay, WI
Posts: 2,021

Re: Block Not Level Around Perimeter.


Sky hook I didnt expect a response like that from you.

String sag is common, but so is the solution. LIke Spindrah said, thats what twigs are for. Or tighten the line up!

I assume were talking about a garage wall, house, or addition here? The run shouldnt be that long where he couldnt tighten the line up or twig it to get the sag out.

And if you bring it up to him Im sure he will say something about the footing being out of level, unless he did the footing too.

If he does, tell him he should have taken that into acct on his first course and cut the block as needed to make his starter course level.

It amounts to shoddy work.

Did you go with the cheapest one?
__________________
Kamps Masonry & Concrete Countertop Design Green Bay, WI
920-680-3195
Visit our website @
http://www.concretecountertopsdesign.com/
6stringmason is offline  
Old 10-05-2009, 08:35 AM   #8
Pro
 
genecarp's Avatar
 
Trade: LI,NY designer, new homes, renovation work, concre
Join Date: Mar 2008
Location: Long Island, NY
Posts: 5,426

Re: Block Not Level Around Perimeter.


Leveling up with concrete gets messy and you cant feather out or go to thin. Shoot the site with a transit or laser, find your high point, using acq build up accordingly. Lay your plates(double), there will be random gaps, go around with slate shims, poge with concrete. You can get it right, it may take a day or two depending on the size of the job and the details. Backcharge the mason. Dont forget the termite shield, the sill seal will probably be a waste of time with the mess you describe .G PS, i have found cutting back the high spots , and correcting with concrete to be a more difficult way to repair these types of messes.
__________________
genecarp is offline  
Old 10-05-2009, 09:08 AM   #9
New Guy
 
straightline's Avatar
 
Trade: new construction/remodel
Join Date: Oct 2009
Location: Tenn
Posts: 29

Re: Block Not Level Around Perimeter.


Thanks for replies, I am the framing sub and had nothing to do with the mason. After checking further on the front of the garage door opening from one side to the other a 9'3" opening the mortor joints is out of line by 1" 1/2. There is one section that has a hight point of 1 1/2" and then runs down 1 1/4 over 10 ft area problem is that is the high spot on the whole foundation and I would have to shim the rest of the foundation up to match that high area. I hate to have a 1/4 million dollar house sit up on shims. If I could get the whole thing to double plate out to maybe 1/2" that would be within acceptible range. There is several off sets on this foundation with the longets wall being 64ft straight. These are the basement walls.
straightline is offline  
Old 10-05-2009, 10:21 AM   #10
Pro
 
lukachuki's Avatar
 
Trade: Customer Education & Development
Join Date: Feb 2005
Location: Aiken SC
Posts: 1,333

Re: Block Not Level Around Perimeter.


Quote:
Originally Posted by straightline View Post
Thanks for replies, I am the framing sub and had nothing to do with the mason. After checking further on the front of the garage door opening from one side to the other a 9'3" opening the mortor joints is out of line by 1" 1/2. There is one section that has a hight point of 1 1/2" and then runs down 1 1/4 over 10 ft area problem is that is the high spot on the whole foundation and I would have to shim the rest of the foundation up to match that high area. I hate to have a 1/4 million dollar house sit up on shims. If I could get the whole thing to double plate out to maybe 1/2" that would be within acceptible range. There is several off sets on this foundation with the longets wall being 64ft straight. These are the basement walls.
Crappy Crappy Crappy Crappy Crappy Crappy Work.

This obviously is the GC's issue then. How he chooses to deal with it will say a lot about him. I wouldn't get your expectations to high though. As has been said already if the extra work falls on you, you need to have in writing what the extra compensation will be!
__________________
"The problem with internet quotes is, you never know if they are authentic." -Abraham Lincoln-

Less with the jaw more with the paw!
lukachuki is offline  
Old 10-05-2009, 12:39 PM   #11
Super B
 
skyhook's Avatar
 
Trade: General Contractor Lic. since 1985
Join Date: Mar 2007
Location: Socal Ground Zero
Posts: 4,166

Re: Block Not Level Around Perimeter.


Quote:
Originally Posted by 6stringmason View Post
Sky hook I didnt expect a response like that from you.

String sag is common, but so is the solution. LIke Spindrah said, thats what twigs are for. Or tighten the line up!

I assume were talking about a garage wall, house, or addition here? The run shouldnt be that long where he couldnt tighten the line up or twig it to get the sag out.
Really now.
String is used to get a straight line, not a level line.
Water level, transit, builders level, lasers etc. is the only way to get accurate elevations.
skyhook is offline  
The Following User Says Thank You to skyhook For This Useful Post:
XanadooLTD (10-09-2009)
Old 10-05-2009, 05:35 PM   #12
Pro
 
DJ9222's Avatar
 
Trade: Mason Contractor
Join Date: Apr 2009
Location: Long Island NY
Posts: 157
Unhappy

Re: Block Not Level Around Perimeter.


If this was my job i would make the mason take the top course of block off and then relay with a lazer or transit..No way can this be fixed with a little cement...
DJ9222 is offline  
Old 10-05-2009, 06:27 PM   #13
Pro
 
Tscarborough's Avatar
 
Trade: Monkey Scratching Cat Herder
Join Date: Feb 2006
Location: Austin
Posts: 4,762

Re: Block Not Level Around Perimeter.


In masonry, stringlines are used for level and edge.
__________________
It ain't Rocket Science unless you are building rockets.
Tscarborough is offline  
Old 10-05-2009, 06:32 PM   #14
Pro
 
Warren's Avatar
 
Trade: framing/remodeling
Join Date: Feb 2005
Location: NE Ohio
Posts: 3,696

Re: Block Not Level Around Perimeter.


If its just the walkout walls at the basement, you could check each section with a laser and cut studs to fit. It is not uncommon on walkouts with several corners, to not be exact. For the garage, I agree with the other guys who say to add a plate and notch to fit. Make sure this change in elevation won't cause any problems anywhere else. And by all means, Notify the GC that this will be a serious "extra" which should be back charged to the mason. If the GC won't pay you to do it, good luck getting your money from the mason.
Warren is offline  
The Following User Says Thank You to Warren For This Useful Post:
essrmo (10-05-2009)
Old 10-05-2009, 07:15 PM   #15
Moderator
 
Double-A's Avatar
 
Trade: GC - Remodeling Specialists
Join Date: Jul 2006
Location: Arkansas
Posts: 4,618
Send a message via ICQ to Double-A

Re: Block Not Level Around Perimeter.


First of all, I don't know what trade "building" is. As far as I know, the Department of Labor doesn't recognize that as a trade. Are you general contractor, a home owner, a framer or what?

This is what site supervision is important. If you paying for site supervision, you're being ripped off. This should have been caught by the mason and the site super and corrected immediately.

At this point, its a matter for a mason or a framer to correct. If you're at most 1.5" out of level at your highest point, I would consider two half courses to correct, if you can go up without impinging on other aspects of your project, such as grade and aerial right of way, etc. If you can't go up, then take a course or two down and correct it.
__________________
"My clients’ wishes are the center of my attention." -- David Guido, a contractor in Woodstock, N.Y.
New York Times, July 20, 2006
Double-A is offline  
Old 10-05-2009, 07:31 PM   #16
menber
 
masonking02's Avatar
 
Trade: bricklaying
Join Date: May 2007
Location: cleveland ohio
Posts: 152

Re: Block Not Level Around Perimeter.


cut slabs
masonking02 is offline  
Old 10-05-2009, 07:43 PM   #17
Maxi-Pier Tech
 
essrmo's Avatar
 
Trade: foundation specialist
Join Date: May 2007
Location: Riverside, Ca.
Posts: 478

Re: Block Not Level Around Perimeter.


Quote:
Originally Posted by straightline View Post
I need to install sill plate on block begining this week and the mason has left me in a mess. The block is out at least 1 1/2" higher in one area the the rest of the block around the perimeter. Also there is a center support wall running through the basement which is 1" higher than perimeter and it is the center support for I-joist which will span from one side to other. How do you go back and compensate for this with sill plate? Can you go back and level the top of the block in anyway? I thought of pouring a 6" cap ontop of block to make it level all the way around perimeter what you guys think?
Bite the bullet and trim a few studs.
Frame it up and quit your belly-achin'.
Be glad you have a job.
Are you sure you're not in over your head ?>
essrmo is offline  
The Following User Says Thank You to essrmo For This Useful Post:
skyhook (10-05-2009)
Old 10-05-2009, 08:20 PM   #18
Pro
 
concretemasonry's Avatar
 
Trade: Masonry consultant
Join Date: Nov 2006
Location: MSP, Minnesota
Posts: 2,447

Re: Block Not Level Around Perimeter.


Don't forget the nuts on the anchor bolts!!! (if the bolts are really there) - Framers are notorious for this. I did a study after some tornadoes and found over 70% of the homes damaged/destroyed did not have nuts on the bolts. - This is in comparison to 30-40% for nuts missing on the other homes.

Dick
__________________
Dick

Engineer, designer and consultant recently active domestically and internationally on construction and design in about 35 countries.
concretemasonry is offline  
Old 10-06-2009, 09:20 AM   #19
New Guy
 
straightline's Avatar
 
Trade: new construction/remodel
Join Date: Oct 2009
Location: Tenn
Posts: 29

Re: Block Not Level Around Perimeter.


After talking with GC we have decided to have mason remove top layer of block and try to re-level I will let you know how this works out.
straightline is offline  
The Following User Says Thank You to straightline For This Useful Post:
DJ9222 (10-06-2009)
Old 10-06-2009, 09:40 AM   #20
Registered User
 
CMSStoneworks's Avatar
 
Trade: Hardscaping & masonry
Join Date: Mar 2009
Posts: 13

Re: Block Not Level Around Perimeter.


Quote:
Originally Posted by skyhook View Post
Really now.
String is used to get a straight line, not a level line.
Water level, transit, builders level, lasers etc. is the only way to get accurate elevations.
someone gets it! lol

I get line levels for free all the time when I buy chalklines etc....they go right in the garbage. I trust my 1000 dollar laser....not a 4.50 cent string that stretches and sag's. I only use stringlines for edges....and even then i use my 48 inch level to further insure im where i wanna be.


Straightline....might i suggest you or the GC stand over this guys shoulder. If I ever laid block like that i wouldnt have my business.

Last edited by CMSStoneworks; 10-06-2009 at 09:46 AM.
CMSStoneworks is offline  
The Following User Says Thank You to CMSStoneworks For This Useful Post:
skyhook (10-06-2009)


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes Rate This Thread
Rate This Thread:

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
block work rebar question paintbob7 Masonry 4 05-31-2009 11:46 AM
window return in concrete block house bmancanfly Remodeling 10 05-15-2009 04:30 AM
Does fireplace opening in block wall opening need support? Square-One Masonry 6 11-22-2008 02:31 AM
concrete block installed out of level pawlooch Masonry 10 05-04-2008 11:41 AM
Does fireplace opening in block wall opening need support? Square-One Construction 1 02-28-2006 01:59 AM

Join Now... It's Fast and FREE!

Privacy Badge
I am a professional contractor
I am a DIY Homeowner
ContractorTalk.com is for
PROFESSIONAL CONTRACTORS ONLY!

At ContractorTalk.com we cater exlusivly to professional contractors who make their living as a contractor. Knowing that many homeowners and DIYers are looking for a community to call home, we've created www.DIYChatroom.com DIY Chatroom is full of helpful advices and perfect for DIY homeowners.

Redirecing in 10 seconds
No Thanks
terms of service

Already Have an Account?