Youngster
Trade: Builder / Consultant / Designer
Joist Hangers, Good Or Bad?
Getting ready to build a 2-story and running into a design issue. The 1st floor greatroom is 23' long, north-south. As designed right now the south wall is exterior and the north wall is interior load bearing. It's gonna take some pretty heafty I-joists to make a 23' span 16"oc. I could always spend more money and go to 12"oc or larger I-joists, but the intent is to try to keep costs down.
Conversely, I could run an LVL beam east-west and cut the span down to about 17'. Then 9 1/2" joists 16"oc would be adequate. Design restrictions require that I use joist hangers to fasten the joists to the beam. In the past I've always preferred to run joists on top of bearing walls and beams. My question is whether joist hangers are prone to squeeky floors in time. They simply don't seem as sturdy as placing the joists over the bearing wall/beam. |
#2 | |
Professional Instigator
Re: Joist Hangers, Good Or Bad?Quote:
I lived in a Hurricane prone area for years and about 30 years ago I was introduced to Simpson products joist hangers, ties, straps etc. They work well If installed properly. The first time I saw them I was like yeah right this is gonna hold what where?? They do Last edited by rbsremodeling; 02-17-2009 at 10:57 PM. |
#3 | |
Trade: Framing Contractor
You have four options that you should really figure out cost wise. 1) I-joists big enough to handle the span at 16" centers. Might be 14" I-joists. 2) I-joists at 12" centers maybe 12" high instead of 14". 3) Flush beam using 9-1/2" I-joists with hangers. 4) Dropped beam 9-1/2" I-joists with no hangers. The other problem you might have using clear-span I-joists is the height might effect your ceiling heights and floor height. If you have existing 2x10's and you your first floor ceiling height has to match the existing first floor and the top of the new I-joists have to match the top of the existing floor joists so that you have no steps, Using 12" or 14" I-joists will be a problem and you will have to lower your first floor wall height.
Joe Carola |
I would check with an engineer and your local AHJ about sizing, that is what they get payed to do. Second, glob some construction adhesive in the hangers before setting the joists and you should have no problems.
Average Joe
Trade: D/B, Management, Consulting, Contracting.
Not to go over anyone here but...you should probably atleast double up the lvl if you're going to use it as a break point for all your I beams. Are you using TGI's? Then what about the posts for your new lvl's?
Definately use PL and definately use the right caliber of nails for your hangers. Make sure you get all of them in. I also say seriously consider your price options. 24' TGI's 16 oc...what's the width? 12 oc over a 20 ft span vs 16 oc 20 ft span...difference is 21 pieces vs 16 pcs= 5 extra tgi's. At say $100 each...that's only $500. 2 new lvl's = $200. Plus hangers and nails =$200 + extra labour...probably $500....=$900. Supposing posts aren't a problem. So far...off of very rough estimations...you're better off just going 12 oc with your I beams. Unless I'm off on your prices. ALSO...Hangers aren't your only option: Joists on ledger Joists bearing on steel flange Joists hung from nailing plate All equally economical...more or less. Hit me up if you need more info...or consult an engineer. GL. |
Joists squeaking all depends on the person putting them in. like Joe Carola said above, if you put a dab of construction adhesive in the seat, there's a much better chance of your joists being squeak free. It's all how you pay attention to the joist sitting in the seat of the hanger and if it rubs up on the sides.
Something I always take into consideration, if I need to, is the mechanical aspect. You know plumbing, hvac, and electrical layouts will play an important roll in your decision. If at all possible use whatever will clear span the width and if that won't work maybe a dropped beam.
Youngster
Thanks guys. Yeah, it looks like it would actually be more expensive to use LVL beams to shorten the span, vs going with 12oc, or larger joists.
I would really like to switch the direction of the load bearing walls and run the joists east-west. That would only require 15-16' spans. I would then be able to use smaller joists without beams at all. The problem there comes with HVAC design. In my area, basements are the norm. So much so, that a well finished basement is considered normal living space and pretty much valued as if it were above ground. As long as it has normal height ceilings and full egress windows. It would really be a bummer if I couldn't get the ducts out of the way. Of all aspects of building, HVAC is what I'm least familiar with, but certain design aspects seem intuitive. If I run the joists the other direction, the most logical place for the main HVAC trunk would be right through the middle of the family-room ceiling. Not asthetically pleasing at all!! If I was able to locate the furnace on the west end of the basement I could at least avoid that situation. Tough decisions. Any input?? |
I used 16" TJI's 16"OC when I built my place. I have a 23' clear span and the floor is rock solid. I have a 2nd fl laundry and bath and I did run them at 12" OC under the machines and tub area. I recently bought front loader machines and was a little nervous when I read all the feedback about front loaders high speed spinning and floor vibrations. When I hooked them up though there were no problems whatsoever and you can't even here the washer downstairs when it is spinning on high speed.
The one benefit that all the subs will love you for is that there is loads of room to work in the joist bays. |
Thom
I've done a lot of work with tji's. Did a job on my own house that I needed to use 12" tall ones to span 23-1/2'. Used the ones with the 3-1/2" flanges at 12"oc. It works but you can't put anything through them, there just isn't enough room.
About 4 years ago I switched from tji's for the second floor deck to engineered trusses. I draw each truss detailing the exact length and exact location of the duct chase. Everything lines up perfectly. It's way easier to get hvac and plumbing installed. They cost a little more but are well worth it. |
Trade: remodeling contractor
How far would the LVL beam have to go, east/west? You may not be able to use 9.5 LVL's if its to far. I've had an engineer tell me that 4 9.5 LVLs wouldn't do it. Had to give up on the flush beam idea, and call the arch, who said it 3 lvl's would work. When I told her what the engineer said, she said "oh, well lets put a 11-7/8 LVL underneath and box it" freaking architects!
You should have asked him if they would work with flitch plates in between because they usually do. There are many options when using a flush beam. He could've seen if you can use 3/4' X 9-1/2" flitch plates in between, or maybe a 1/2" flitch plate. Who knows, you could've used a steel I-beam.
Joe Carola |
Youngster
Once I did a cost breakdown for each option, it looks like I can go with 14" I-joists. Overall, it costs me about $200 extra, but saves me a ton of hassle. Admittedly, I didn't price out floor trusses. I don't think that HVAC is going to be an issue. 14" joists @ 16"oc should be plenty of room to run ducts. The main trunk for the main floor and basement will be running through basement closets mostly. HVAC for the second floor will run through the attic.
I'm a Mac
Trade: ICF Construction
Deeper is cheaper
Chris |
Youngster
For anyone who might be interested. I went ahead and got a bid for open web trusses for this same job.
Looks like the two best options are as follows:
Thanks THOM for the heads up on the trusses. |
At the 19+" oc even ¾ T&G is to
springy for my taste, and I think to flexible for tile. Maybe want to throw in a bit for extra thick deck?
#17 | |
Youngster
In any case, most of the floor above it is bedroom, so the carpet won't have any problem. The master baath will have natural stone though, so I might consider 16"oc or less for that space. |
#18 | ||
General Contracting
Trade: Real Estate Broker, Property Manager
![]() Quote:
#19 | |
Youngster
I don't know where you are from, but that statement is only mostly correct. The way you stated it made it sound like the basement has little to no value from an appraisal standpoint. IOW, the basement is considered just a large crawlspace, or at best just a large nonliving space like cold storage.
In some areas that might be the case, but not here. Footings must be >38" deep, so it's only natural that you'd spend the extra few thousand to dig out that dirt between the foundation walls and pour a slab. Sometimes the basements are left unfinished, and sometimes they are finished cheaply as was common back in the 80's. Most times though, they are finished off just as if they were above ground. Especially in nicer areas where the builders pour 9' foundation walls and design for walkout/daylight basements for that above ground feel. From an appraisal standpoint, you are correct in that the appraiser does one calculation for above ground GLA, and a separate calculation for the basement area. But that isn't to say that the basement has little value. The value of basements is very dependent on the area and the finish of the space. This statement can be pulled from almost every appraisal info source. "The local market will dictate the contributory value of the finished basement, which can be influenced by governmental regulations, the degree of modernization, the quality of the finish, and other factors. " In my area, a 1500sf house with a fully finished 1500sf basement is listed and described by sellers and buyers alike as a 3,000sf house. Indeed, appraisers are more careful in clarifying that half of it is basement, but they aren't the ones buying your home. Even an unfinished basement here carries a considerable amount of value. In any case, we designed our house with specific regard to what you are talking about. Most houses here are just as I described above. 1500-2000sf (above ground) ramblers with full finished basements. We opted for a design that would maximize value by have much more GLA above ground and a relatively small footprint. 1,200sf daylight basement... 1,300sf main... 1,300sf second floor. Lumber and other such building materials are very cheap right now, but concrete and steel aren't cheap at all. So, we designed for more lumber and less concrete, which naturally leads to a higher appraisal because of the factors you've cited. In regard to hardwood floors. You are correct. I've had both hardwood and carpet for the MBR. Wood looks much nicer, but carpet is much nicer in function. Most people that I talk to are of that same opinion. It seems to me that the only reason people put wood floors in the MBR is because it is expected in a high-end home and is a distinguishing feature. In reality, it is incredibly impractical to put wood floors in a bedroom. They are cold and uncomfortable in the morning and unforgiving to laziness in terms of cleaning. The result is that everyone ends up covering them with a piece of carpet like an area rug or something. Isn't that just the dumbest thing ever. I'm convinced that 30 years from now people are going to look back on that and wonder what we were thinking. But I have no choice. Just as you say, I probably have to do it as I won't be in this home for more than a couple years. Your suggestion of 16"oc and 12" under the master bath is good. We had actually just talked about doing that, but were still getting opinions from a couple respected professionals. Thanks for the advice. Quote:
#20 |
General Contracting
Cache,
First, I am in New York as it says right under my name to the left. Well I hope you didn't think I was saying not to finish it off. Yes, Finished Basements do add value, but not at the same rate as above ground sq. footage. In my MLS, Basement sq. footage is separated from above ground sq. footage so you are not on the same playing field. Furthermore, if you don't have a c/o for it, it does not count either. Anyway, my main point was that you should be careful just how much money you put into the basement. If it is built better than the upstairs, the upstairs will look like it needs work. If it is done poorly, it will look like it needs to be redone. Ceiling height is the biggest issue. Keep the finished ceiling height at 7-6" to 8' for maximum ROI. Since you stated that all the homes in your area have a finished basement, then you should as well. The RED FLAG I see in your situation is that you indicated you would be selling soon. Soon as in within 10 years. Remember you will not get a 100% ROI. Might get like 80% right now. You should always build or renovate with the idea that you will not to be the Most Expensive House on the block when you are finished. In order to do that, you need to know what the most expensive house on the block is. I have three foreclosures right now where the sellers simply pulled too much equity out of their home or renovated it over market conditions. Now they can't sell and are loosing the houses. Don't do that! |