Leaky Service
Old 09-04-2007, 06:09 PM   #1
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Leaky Service
Myrtle Beach, South Carolina
Magnettica is offline
Old 09-04-2007, 06:14 PM   #2
mdshunk's Avatar
Re: Leaky Service
Yuk! That looks like grease from the exhaust hood fans on the roof that drizzled down over that meter can. That's a dumb way to do a mast anyhow; right up through the rain gutter. I always offset around the gutter on services like that.
mdshunk is offline
Old 09-04-2007, 06:16 PM   #3
Remodeler Extraordinare
A.W.Davis's Avatar
Re: Leaky Service
what a mess!
A.W. Davis Construction Co.
http://www.awdavisconstruction.com/
Your friendly remodeling contractor
A.W.Davis is offline
Old 09-04-2007, 06:31 PM   #4
mickeyco's Avatar
Trade: Squirrel Handler
Re: Leaky Service
It looks like old abandoned equipment, right?
mickeyco is offline
Old 09-04-2007, 08:51 PM   #5
Fentoozler
Celtic's Avatar
Re: Leaky Service
What is the SE offset to? (Left of that gutter penetration)
Celtic is offline
Old 09-04-2007, 09:24 PM   #6
mdshunk's Avatar
Re: Leaky Service
That's a piece of EMT from that abandoned CT can. It looks like that's all abandoned, and they're running it down that 2-incher to the inside, and probably CT metering it indoors. I see the CT rack in the roof there, but I can't tell where the CT conductors go to. That outdoor CT can's mast doesn't have anything going down it.
EDIT... I just looked again, and see little tails coming out of those CT's and look like they're whipped up to go down that greasy mast. That must have been the original service, and then they added capacity and CT metered things. That old service looks like it might still be in use, so they just jumpered out the old meter and ran them through the CT's. I'm betting that's what we've got there.
mdshunk is offline
Old 09-04-2007, 09:27 PM   #7
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Re: Leaky Service
Like this:
As far as I know this equipment is energized. I didn't actually breakout the tick tracer to find out but all those conductors are attached to the service drop. I just had to get a shot for the board.
Btw, that's not SE.
Old 09-04-2007, 09:32 PM   #8
Service & Repairs
Magnettica's Avatar
Trade: Electrician
Re: Leaky Service
Huh?
What little CT's are you talking about? On the roof?
I believe the two other masts up on the roof go down to their original meters located on this inside. If I had to guess, a small addition was added but the original electrical wasn't updated.
Old 09-04-2007, 09:36 PM   #9
mdshunk's Avatar
Re: Leaky Service
Originally Posted by Magnettica View Post
Huh?
What little CT's are you talking about? On the roof?.
Yeah, there's a CT rack on the roof in your first batch of pictures. It's not really little. It's pretty big.
mdshunk is offline
Old 09-04-2007, 09:38 PM   #10
Fentoozler
Celtic's Avatar
Re: Leaky Service
WTF????
How can you see that sheet?
Celtic is offline
Old 09-04-2007, 09:44 PM   #11
mdshunk's Avatar
Re: Leaky Service
WTF????
You do see three pictures in the first post, right? I'm confused now, since it's pretty clear to me. Maybe I'll draw it out.
mdshunk is offline
Old 09-04-2007, 09:46 PM   #12
Fentoozler
Celtic's Avatar
Re: Leaky Service
I see the 3 pix post...but not the detail you see. The "EMT" looks to be SE to me ~ the 2-hole strap even looks "squared".
Celtic is offline
Old 09-04-2007, 09:51 PM   #13
Patrick's Avatar
Re: Leaky Service
Does the conduit double as a downspout? I woulda spec'd out a larger conduit to allow better water flow
Patrick is offline
Old 09-04-2007, 09:57 PM   #14
mdshunk's Avatar
Re: Leaky Service
I marked up the picture, and annotated it here to what I think's going on.
A-Service mast to indoor panel, which is the "upgrade" that I believe was added to this building.
B-CT rack. I can't tell if it's bolted on a piece of angle iron, or bolted onto a second mast going down to a second indoor panel. Could be either.
C-Building's original service, now going through the CT's for the combined bigger service.
D-CT weatherhead on top of EMT mast. The little weatherhead looks like it's turned away from view, but I can now barely makeout the #12 CT secondary conductors whipped from the CT rack to this weatherhead.
E-Newer paralleled drop, for when all this newer stuff was added.
F-Can for CT meter for this bigger combined service. This is the vandal resistant type.
G- Original meter can, with blank plate installed. Since these conductors now go through the CT's, there's no reason for a meter in here anymore. Jumper links likely installed to refeed original indoor equipment.
mdshunk is offline
Old 09-04-2007, 10:57 PM   #15
Fentoozler
Celtic's Avatar
Re: Leaky Service
B - Your CT rack are insulators (porcelain)
D - It's SE cable
How can you see this detail?
How big is you monitor?
Resolution?
Vid card?
Check out this camera:
13.4 Gigapicel Camera
(yes, it's a typo, their's..not mine)
I see zoomed out...you see zoomed in....those people by the trees - that's what you see.
Celtic is offline
Old 09-04-2007, 11:02 PM   #16
Celtic's #1 Fan
mahlere's Avatar
Trade: electrical
Re: Leaky Service
D - It's SE cable
Resolution?
Vid card?
i'm with MD on both of these...viewing on a 21" monitor..high res...
the D is definitely PVC, with 2 hole straps...put definitely pvc.
the mast, look on the left side of the 3 units, looks like a sticker on a CT to me...
mahlere is offline
Old 09-04-2007, 11:05 PM   #17
Fentoozler
Celtic's Avatar
Re: Leaky Service
Originally Posted by mahlere View Post
.... looks like a sticker on a CT to me...
Get the hell outta here!!
A sticker....my ass.
LOL
WTF???
Celtic is offline
Old 09-04-2007, 11:06 PM   #18
Celtic's #1 Fan
mahlere's Avatar
Trade: electrical
Re: Leaky Service
LOL
WTF???
nameplate...sticker...220...221
seriously, looks like CT's.
if magnetica had just paid f'ing attention, none of this would be occurring...
thanks alot mag...
mahlere is offline
Old 09-04-2007, 11:08 PM   #19
Fentoozler
Celtic's Avatar
Re: Leaky Service
I thinks I may be needed an upgrade over here........
Celtic is offline
Old 09-04-2007, 11:09 PM   #20
Celtic's #1 Fan
mahlere's Avatar
Trade: electrical
Re: Leaky Service
see, if you were a painter, you could go buy a 56" plasma for your monitor....but you're only an EC, so 17" will have to do...
mahlere is offline
Service Magic's new service Grumpy Marketing & Sales 12 08-02-2008 04:31 PM
Setting up service department pcisam General Discussion 0 04-27-2007 09:38 AM
Can anyone make any sense out of this? Teetorbilt Technology 24 04-16-2007 12:21 PM
Service upgrade question ATS Electrical 17 09-05-2006 09:48 PM
May offer a New Service ?? tzzzz216 General Discussion 15 07-16-2006 12:00 PM